Where does it say 40dF? My copy of 13 says that were piping is subject to
freezing it shall be heated to 40dF.
Eric J. Shelton, PE
Senior Fire Protection Engineer
Associate
Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
v: (804) 521.7105 f: (804)
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Eric Shelton
Sent: Thursday, November 12, 2009 3:19 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Gulf Coast
Where does it say 40dF? My copy of 13 says that were piping is subject to
freezing it shall be heated to 40dF
Bobby,
Check the Georgia code amendments. Years ago, when I lived in Atlanta, they
allowed re-using heads in some circumstances.
Eric J. Shelton, PE
Senior Fire Protection Engineer
Associate
Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
v: (804)
This report, ESR-2397 appears to be an update to NER-516, dated January 1,
2004. While I haven't done a detailed comparison, one difference that pops out
at me is the following.
(Old text from NER-516):
7.8 All combustible materials shall be kept 2 inches (51 mm) from the face of
the glass.
Actually, the IBC section on limited area sprinkler systems goes up to 19 heads
(fewer than 20). It also requires a hydraulic calc with a simultaneous
plumbing demand.
Eric J. Shelton, PE
Senior Fire Protection Engineer
Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Chime joists are shown in a figure at
http://www.abwoodtech.com/instructions_assembly.html
Croze is defined at http://www.thefreedictionary.com/crozes
Eric J. Shelton, PE
Senior Fire Protection Engineer
Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
Thank you, Rich. This is exactly the kind of information I was looking for.
Eric Shelton
From: [EMAIL PROTECTED] on behalf of Rich Pehrson
Sent: Mon 7/30/2007 9:26 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: High Density Art Storage
Eric
5:45 PM
To: Eric Shelton
Subject: Re: High Density Art Storage
Hello Eric,
I just happened to see 21.36.1.2 but it does not mention a specific
density. Looks like NFPA 909 might give some guidance.
Friday, July 27, 2007, 4:53:07 PM, you wrote:
I have a museum with a system of high density
I went down his road once, thinking that if an area wasn't subject to freezing
then a dry system can't be used. After all, that's just the reverse of the
requirement that if an area IS subject to freezing then a dry system MUST be
used.
There are some who specify this, but after doing much
I have a museum with a system of high density storage units used for
storing small paintings and sculptures, some of which is crated. It is
similar to the units used for records storage, being about 8'6 high
with 24 deep shelves, with two back-to-back shelves per unit. The
units are manual;
I am evaluating an existing pipe schedule system that was installed in
1961 in an old house. It is now used as a business-type occupancy and
the AHJ has asked that the system be evaluated to the current (1999)
edition of NFPA 13.
In addition to evaluating the available flow and pressure against
it even if you're not a customer.
Eric Shelton
Hankins and Anderson, Inc.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, April 17, 2007 3:43 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 3D cad capabilities ??
What we
If a floor is less than 48 wide but is adjacent to a wall, does it need
sprinklers under it?
/Eric Shelton
Hankins and Anderson, Inc.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, April 05, 2007 1:27 PM
A similar event happened in Richmond a few years ago. An electrician
stuck a tool in a live bus duct in a 19th floor electrical room and set
off fireworks that activated the two sprinklers in the room. Water
totally flooded several floors below and traveled down the elevator
shaft until it
I haven't seen a 2006 version of ASME A17.1 nor is one listed for sale
on their web site, so perhaps he's referring to a proposed change that
is yet to be published. I do recall several months ago (on this forum,
I think) someone posting about a proposed change that would require
pre-action in