So, if this same tank and pump were at the same elevation and 5 blocks away
in a Water Utility Yard owned by the city water department, what pressure and
flow rate would one use to design a sprinkler system?
Mark at Aero
602 820-7894
-Original Message-
From: Sprinklerforum On Behalf
tion=DwIGaQ=wn3mZQLIuInh2ClcJ0_DIA=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg=bvq41lm2mLFrYYntFs8KbfX4NoqHk7erRa-DeKYiJno=dd4BdD6U3qjPscVViUPaV8u-sawwkYXOA8Ob2TlUbKA=
>
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__www.firesprinkler.org_competition=DwIGaQ=wn3mZQLIuInh2ClcJ0_DIA=dLwiR71i_XhSFqam3ZLeaFLi
I've had at least one Official state (opinion) that the "Fire Flow" @ 20 PSI"
was never intended to be "provided to the site hydrants". It is simply a
recommendation for the benefit of Fire Fighters using their pumpers and hoes to
"preserve" 20 psi in the city water main for all the obvious
Hi Scot,
Long time no argue with !! Correct me if I'm wrong, but isn’t that called the
"Gas Laws" and for good reason, it's different from Hydraulics? If you fill a
standpipe system from the bottom and vent the system at the top to evacuate the
air (gas), you could achieve a hydraulic lock in
In years past, we have actually enlisted the service of the local Fire Station
to bring out a pumper truck, hook an existing hydrant and fill and pressurize
the standpipe. The inspector came back after the requisite 2 hours and signed
it off. It's all about relationships.
Mark at Aero
602
If you were to look up George in my contact list this is what you’d find.
George L. Church
Rowe Sprinkler Systems Inc
Owners Husband
Mark at Aero
602 820-7894
> On Feb 12, 2021, at 3:39 PM, Ron Greenman via Sprinklerforum
> wrote:
>
> Seems like there's been a resurgence in activity in the
https://www.gadsdentimes.com/news/20200415/scottsboro-dock-fire-that-killed-8-ruled-accidental
-Original Message-
From: Sprinklerforum On Behalf
Of Steve Leyton via Sprinklerforum
Sent: Thursday, January 14, 2021 10:57 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton ;
When you say boat storage would be questionable, are you just accommodating
open-top aluminum fishing boats as low risk/hazard? Otherwise boat storage vs
RV storage are the same IMHO.
Mark at Aero
602 820-7894
> On Jan 8, 2021, at 1:38 PM, Travis Mack via Sprinklerforum
> wrote:
>
> RV
Is anyone online this morning willing to discuss the Noted Table in the fire
code.
My question, on behalf of a building owner is...
" What is the application of the three boxes at the right hand side of the
Table labeled
NON-SPRINKLERED
Any Height
NR (Not Required)"
I have to admit, it makes
What Craig said, and don't forget about the organic dust explosion hazard.
Mark at Aero
602 820-7894
-Original Message-
From: Sprinklerforum On Behalf
Of Prahl, Craig/GVL via Sprinklerforum
Sent: Thursday, October 15, 2020 2:52 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Prahl,
Maybe you should have suggested to the ahj that it needed a total flooding
inert gas system with optical detection as the primary protection system with a
6% AR /AFFF deluge system for redundancy. You just never know when someone
might leave a box of Bic pens in their locker (Flammable liquid
San Francisco.
-Original Message-
From: Sprinklerforum On Behalf
Of Kyle.Montgomery via Sprinklerforum
Sent: Thursday, August 13, 2020 8:06 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Kyle.Montgomery
Subject: [EXTERNAL] RE: 13 R in a single family home
Out of curiosity, where
Just out of curiosity, what is driving the need to replace the pump?
Mark at Aero
602 820-7894
-Original Message-
From: Sprinklerforum On Behalf
Of Brian Harris via Sprinklerforum
Sent: Thursday, August 6, 2020 8:24 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Brian Harris
Or actually a 170 year old model. But who’s counting.
Mark at Aero
602 820-7894
On May 30, 2020, at 9:19 AM, Steve Leyton via Sprinklerforum
wrote:
This post could be the narrative explanation for why I went into business as a
design consultant. When I was contracting, I lost countless
This is outside the scope of the NFPA standards. It is in the realm of the
local Building or Fire Code to determine the If required.
Mark at Aero
602 820-7894
From: Sprinklerforum On Behalf
Of John Irwin via Sprinklerforum
Sent: Friday, May 29, 2020 2:55 AM
To:
Another thing to keep in mind is that having combustible material in the attic
space of type IB construction does not change the construction type.
Mark at Aero
602 820-7894
From: Sprinklerforum On Behalf
Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Tuesday, May 19, 2020
I believe you're correct in your assumptions and suppositions. We designed and
build a water supply system very similar to yours a number of years ago but it
has three domestic pumps plus our fire pump. The settings in the individual
controllers are easily arranged to accommodate this. The
Please don't throw rocks at me for this, but if the building isn't normally
occupied (office space of whatever) does it even make sense to put sprinklers
in it? You don't say what the construction type is but these are commonly metal
buildings and if it is, there is even less reason to put in
Do you have to perform the test or do they do it?
Mark at Aero
602 820-7894
Sent from my iPhone
> On Nov 18, 2019, at 8:57 PM, firstin--- via Sprinklerforum
> wrote:
>
> Need advice on the best way to fight a non required requirement.
> Someone at the local water purveyor came up the the
rforum
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
On Behalf Of Mark.Phelps via Sprinklerforum
Sent: Thursday, November 7, 2019 1:24 PM
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Mark.Phelps mailto:mphe...@aerofire.com>&
I am looking for a general idea for the completed cost of a residential
sprinkler system using a wet pipe antifreeze (cold climate location). The
project is a high end two story custom home of around 6,000 square feet of
protected space and has an adequate city water supply. I’m not looking
to activate more than one system with the same fire (say two levels
with a large open communicating space, or open grate flooring? Or even just two
tanks that are close together.
Benjamin Young
On Fri, Oct 18, 2019 at 11:12 AM Mark.Phelps via Sprinklerforum
mailto:sprinklerforum@lists.firesprinkler.org
If you haven't gotten a response on this question, I'll offer a couple of
questions to gather information.
1. Are there exterior walls that enclose the individual floors?
2. Are the floors solid with large openings, or grated with large
openings?
3. What type of equipment is
Silco Fire and Security
2345 Southwest Blvd.
Grove City, OH 43123
P-614-449-2101 Ext. 3367
F-614-449-2007
C-614-348-8206
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Mark.Phelps via Sprinklerforum
Sent: Tuesday, September 24, 2019 3:15 PM
To:
spri
Just curious, but wouldn’t it be about the same to just replace the valve with
a spool?
Sent from my iPhone
On Sep 24, 2019, at 12:08 PM, John Paulsen via Sprinklerforum
mailto:sprinklerforum@lists.firesprinkler.org>>
wrote:
From: John Paulsen
Sent: Tuesday, September 24, 2019 10:06 AM
To: