In years past, we have actually enlisted the service of the local Fire Station 
to bring out a pumper truck, hook an existing hydrant and fill and pressurize 
the standpipe.  The inspector came back after the requisite 2 hours and signed 
it off. It's all about relationships. 

Mark at Aero
602 820-7894

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Tom Duross via Sprinklerforum
Sent: Thursday, April 15, 2021 3:59 PM
To: [email protected]
Cc: Tom Duross <[email protected]>
Subject: [EXTERNAL] Standpipe Testing

I'm wondering if anyone here on the list can help me with some estimates.

 

I have 3 elevated roadway standpipes to pressure test and flow test.  All set 
with the flow testing part.

My question is pressure testing.  Never did this part before.  I can use the 
public hydrants to fill to street pressure.  No problem.  Static on grade is 
about 75# as I have a couple of pumps in the area I test annually.
Standpipes are about 50' above.  I need to figure out if I need to rent a pump 
capable of reaching 200+ psi or how long will these 2 little ½ and ¾ hp hydro 
pumps I have will take.  This is all witnessed and the plan is hydro for 2 
hours, walk and check everything, drain completely, hook up the pumper and pull 
the trigger.  Can't make the fire guy stand there for 2 hours while the little 
pump hits 200 plus 50 feet.

 

If I took each of the standpipes, calculated their volume (close to a mile in 
total), figured in all the expansion joints, pipe to the double wye's, air 
vents, low point drains, dual FDC's, etc., and came up volume.  Use fire
hose to reach static.    I take my little pumps at 4 or 6 gpm, decreases as
pressure grows obviously, I need to figure how long these will take to reach 
200-225#.  Thinking hours.  So maybe I need to look into rentals but I need to 
know what size I need.

 

Ideas?

 

TD

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIFAw&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=cicIkTxPTDGmY6Z2ABtrc37sNC4Fz5auvLmpPxfRXWM&s=WufeO6alS7HhoyKVAjj7QIHxIFzsw-grgIKY_ERsmY4&e=
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to