From: Sprinklerforum
Good morning, forum
Can someone give me chapter & verse of the NFPA 13
statement that you can't use 1/2" heads when the density
is .25 or better?
thanks, Vince
--
11351 Pearl Road / Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876Cell 440
Thoughts?
Approved or not?
Thanks, Vince
--
*Vince Sabolik*
*West Tech Fire Protection, Inc.***
11351 Pearl Road / Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601
___
Sprinklerforum mailing list
One more thing:
HAVE A NICE WEEKEND ALL
On 5/21/2021 2:12 PM, Vince Sabolik via Sprinklerforum wrote:
I spent all morning researching Glen's five gallon thing.
And I came up with my own formula!
Curious though, no prices HERE!
So, if my formula works off forum I'm in good shape
; sprinklerforum@lists.firesprinkler.org
Cc: Glen Buelow, Inc.
Subject: [EXTERNAL] Re: CURIOUS
Vince
I only know of 5 gallon
*Glen Bue**low*
*Glen W. Buelow, Inc.*
*Fire Protection Design and Consulting216-469-7390** <330.665.4439>*
On Fri, May 21, 2021 at 9:31 AM Vince Sabol
Good morning, Forum -
Can I get a per gallon price range for antifreeze premix?
Please, no manufacturer names!
thanks, Vince
--
11351 Pearl Road / Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876Cell 440
My friend Brad Casterline wanted to offer an answer to Tom Duross'
question about how
long it would take to pump up a standpipe.
Please note, I'm not this smart!
P1=75 psi/.433=173 ft.
P2=200 psi/.433=462 ft.
deltaP=289 ft.
V1=5000 gal/7.48=669 ft^3.
P1V1=115,737 ft/ft^3, /289 ft=400 ft^3.
4
Limited Area System 4.12
On 4/8/2021 10:04 AM, Thomas Reinhardt via Sprinklerforum wrote:
Question for the group. I recently did an inspection at a very old McDonalds
restaurant in town. During inspection found 4 sprinkler heads piped off
domestic protecting the rear corridor leading the
CLEVELAND and 'conventional' head that could be installed as a pendent or
upright.
On Mar 18, 2021, Vince Sabolik via Sprinklerforum
wrote:
>"Automatic" Sprinkler used to be IN Clevelar.
>Did you run into one of the old style heads that was installed in the
>upright
"Automatic" Sprinkler used to be IN Clevelar.
Did you run into one of the old style heads that was installed in the upright
or pendent position?
On Mar 18, 2021, jaycs7919--- via Sprinklerforum
wrote:
>Just wondering if anyone is familiar with these sprinklers. I am
>hoping some of the more
Hey forum -
Does anyone here use an independent company to stocklist their jobs?
--
*Vince Sabolik*
*West Tech Fire Protection, Inc.***
11351 Pearl Road / Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601
hat.
Matt
-Original Message-
From: Sprinklerforum On Behalf
Of Vince Sabolik via Sprinklerforum
Sent: Tuesday, February 16, 2021 1:23 PM
To: Travis Mack via Sprinklerforum
Cc: Vince Sabolik
Subject: Re: MORE ACTIVITY WEIGHING IN
Offices.
I'm looking for a table that an
%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0
From: Sprinklerforum On Behalf
Of Vince Sabolik via Sprinklerforum
Sent: Tuesday, February 16, 2021 12:16
Hello forum -
Does anyone have tables of how much weight per square foot a typical
sprinkler system adds
to a building?
thanks, Vince
--
11351 Pearl Road / Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876Cell 440 724-7601
/
Vince Sabolik /
Good evening, Forum -
Can someone email or post a set of instruction on how to transfer
clashes out of Navis Manage to an Autocad drawing? I was familiar in
2019 - has something
changed?
Both programs are 2021 versions out of the box.
Thanks!!
Vince
*Vince Sabolik*
*West Tech Fire
.com
From: Vince Sabolik via Sprinklerforum
To: "sprinklerforum@lists.firesprinkler.org"
Cc: Vince Sabolik
Date: 09/29/2020 05:29 PM
Subject: GLOBE 4" DIFF DPV CUT SHEET (OR MAINTENANCE)
Sent
Good afternoon, forum -
Help! Has anyone got a cut sheet of a Globe 4" differential dry pipe valve?
May be Model F or Model D.
Thanks!
--
*Vince Sabolik*
*West Tech Fire Protection, Inc.***
11351 Pearl Road / Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876 Cell 440
No
On 3/3/2020 10:20 AM, BILL MENSTER via Sprinklerforum wrote:
Mornin,
Does FM allow the area reduction for QR sprinklers?
Thanks
Bill Menster
WFM Consulting
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
South Carolina 29606
*From:*Sprinklerforum
*On Behalf Of *Vince Sabolik via Sprinklerforum
*Sent:* Monday, February 17, 2020 11:54 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Cc:* Vince Sabolik
*Subject:* [EXTERNAL] Anybody hit this wall?
Good morning Forum -
This is a new one on me.
A
Scot Deal
On Mon, Feb 17, 2020, 8:53 AM Vince Sabolik via Sprinklerforum
<mailto:sprinklerforum@lists.firesprinkler.org>> wrote:
Good morning Forum -
This is a new one on me.
A building with two Use Groups, H4, S2 is separated by a wall and
is fully sprinklered
per NF
Good morning Forum -
This is a new one on me.
A building with two Use Groups, H4, S2 is separated by a wall and is
fully sprinklered
per NFPA.
Does the separating wall need to be rated?
--
11351 Pearl Road / Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876Cell 440
Aren't there square footage limitations as well?
On 1/29/2020 11:03 AM, Skyler Bilbo via Sprinklerforum wrote:
Take a look at section 16.2.1.2. I believe in your case, the Misc.
Storage criteria does apply. However, for Class IV commodities on
racks 10-12 ft tall, the criteria is EH1, per
Top beam clamps, narrow or wide throat.
On 1/2/2020 8:36 AM, James Litvak via Sprinklerforum wrote:
I'm trying to hang 6" pipe flat beneath a roof with a 4:12 slope, but
having trouble finding an attachment. It's a standard Butler-style
building with Z-purlins, and I'm hanging the pipe flat,
...@lists.firesprinkler.org] *On Behalf Of
*Vince Sabolik via Sprinklerforum
*Sent:* Friday, December 06, 2019 12:53 PM
*To:* sprinklerforum@lists.firesprinkler.org
*Cc:* Vince Sabolik
*Subject:* Hello Forum, me again
Anybody know of a 2" UL listed FM approved water meter?
*Vince Sabolik*
*West Tech
Anybody know of a 2" UL listed FM approved water meter?
*Vince Sabolik*
*West Tech Fire Protection, Inc.***
11351 Pearl Road / Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601
___
Sprinklerforum mailing
Good afternoon, Forum -
Has anyone ever run into a head spacing pattern called "bay & beam"?
and... bonus round
Were heads before 1953 associated with a K-value?
--
11351 Pearl Road / Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876Cell 440 724-7601
/
Vince Sabolik /
On 11/1/2019 4:15 PM, John Irwin via Sprinklerforum wrote:
Where you live does the AHJ have the authority to write his own fire
code? In Florida we would say "that's great that you want that, but no."
Happens frequently enough here in Ohio. And when it does, NFPA cedes
authority to the local.
The area above the ceiling requires protection.
Is the reduced area (use of QR) applicable?
--
*Vince Sabolik*
*West Tech Fire Protection, Inc.***
11351 Pearl Road / Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601
Thanks guys & good night!
On Sep 16, 2019, Vince Sabolik via Sprinklerforum
wrote:
>Hello forum --
>
>Is it acceptable to hook up several dry systems to a single nitrogen
>generator?
Vince Sabolik___
Sprinklerforum mailing lis
Hello forum --
Is it acceptable to hook up several dry systems to a single nitrogen
generator?
--
*Vince Sabolik*
*West Tech Fire Protection, Inc.***
11351 Pearl Road / Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601