Thanks Matt. That's what I was looking for.
Vince
On 2/16/2021 2:34 PM, Matt Grise via Sprinklerforum wrote:
When I have looked at it (usually for pre-engineered metal buildings)- the
lbs/sf is just the weight of the water-filled pipe divided by the are it
'covers'. Similar to the coverage of a sprinkler head.
Each structural member then has an allowable point-load formula based on how
the connections are spaced and how much load it can handle.
Most of the PEMB designs I come across have a 5 lbs/ft "collateral load"
design. We have never had a sprinkler system exceed that.
Matt
-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf
Of Vince Sabolik via Sprinklerforum
Sent: Tuesday, February 16, 2021 1:23 PM
To: Travis Mack via Sprinklerforum <[email protected]>
Cc: Vince Sabolik <[email protected]>
Subject: Re: MORE ACTIVITY WEIGHING IN
Offices.
I'm looking for a table that an architect or engineer would use to figure roof
loading.
I don't think they're that detailed.
On 2/16/2021 2:17 PM, Travis Mack via Sprinklerforum wrote:
What is a typical system? Protecting flammable liquids will be a lot more than
an office building.
Travis Mack, CFPS, CWBSP, RME-G, COC, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271 ext. 700 C: 480-272-2471
mailto:[email protected]
https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.mfpdesign.com&c=E,1,LWPOkuQfKyi4ROGqKcnbYQjv2Y6W-GC52ALx7gZ_ozT4hvUsEfdfMFU1zDo69tl0F8jhudt85K7GliMneCJSs-0mA2XIq4vv7cNfCaG8A7EfttrZ5KDqiwaXUQ,,&typo=1
Send large files to us via:
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0
From: Sprinklerforum <[email protected]> On Behalf
Of Vince Sabolik via Sprinklerforum
Sent: Tuesday, February 16, 2021 12:16 PM
To: [email protected]
Cc: Vince Sabolik <[email protected]>
Subject: MORE ACTIVITY WEIGHING IN
Hello forum -
Does anyone have tables of how much weight per square foot a typical
sprinkler system adds
to a building?
thanks, Vince
--
11351 Pearl Road / Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876Cell 440 724-7601
/
Vince Sabolik /
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org