Aren't there square footage limitations as well?
On 1/29/2020 11:03 AM, Skyler Bilbo via Sprinklerforum wrote:
Take a look at section 16.2.1.2. I believe in your case, the Misc.
Storage criteria does apply. However, for Class IV commodities on
racks 10-12 ft tall, the criteria is EH1, per the Misc. Storage Table
13.2.1.
I believe where the biggest confusion, and the importance of the
definition comes into play, is with plastic storage over 5 feet, but
under 12 feet. There is not equivalent language to 16.2.1.2 in the
plastic storage chapters...
Skyler Bilbo
1700 S. Raney Street
Effingham, IL 62401
217-819-6404 Direct
217-347-7315 Fax
[email protected] <mailto:[email protected]>
www.wenteplumbing.com <http://www.wenteplumbing.com>
On Wed, Jan 29, 2020 at 9:44 AM Brian Harris via Sprinklerforum
<[email protected]
<mailto:[email protected]>> wrote:
Just want to confirm per the definition of Misc. Storage (3.9.1.18
NFPA 2013) that just because something is stored less than 12’
high doesn’t automatically make it misc. storage. Working on a
project that is 42,000 sq.ft. and the owner is storing Class I-IV
commodities on double row racks. Says he was told as long as he
doesn’t exceed 12’ high he only needs OH-2 protection at the ceiling…
*Brian Harris, CET*
BVS Systems Inc.
Design Manager
bvssystemsinc.com <http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935
_______________________________________________
Sprinklerforum mailing list
[email protected]
<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
11351 Pearl Road / Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876Cell 440 724-7601
/
Vince Sabolik /
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org