RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Steve Leyton via Sprinklerforum
Thank you Michael, that's music to my ears. We started drawing sprinkler plans 
in Revit six years ago because that's what our clients wanted and what their 
clients were demanding. Since that time, the amount of effort that we expend in 
the construction administration phase of our projects has been reduced by at 
least a third, perhaps by half.  The fact is that BIM -not pretend NavisWorks 
BIM - but real parametric 3D drafting and coordination, does work and sometimes 
it works really well. Nothing's perfect, design and construction will never be 
fully in sync, but it's profoundly better. The fact that the fire sprinkler 
trade has mostly dismissed BIM as being of value is my bread and butter.

Party on Garth...



Steve Leyton

(Sent from my phone; please excuse typos and voice text corruptions.)




 Original message 
From: Michael Goodis via Sprinklerforum 
Date: 1/15/20 10:51 AM (GMT-06:00)
To: sprinklerforum@lists.firesprinkler.org
Cc: Michael Goodis , "'Travis Mack, SET, CFPS, CWBSP, RME-G'" 

Subject: RE: [EXTERNAL] Pipe adjacent to duct

Bim modeling, that’s funny. Never seen it work yet…. Only thing its been god 
for is (your duct is in the way, we see you cant move, the model is wrong, let 
now reroute due to the conflict, oh and wait, its not a CO because this should 
have been caught during the bim modeling.)

Great stuff with the GC’s pushing it off to try and cut the change orders out. 
Gotta love it.


Michael Goodis
Salesman, Project Manager
IL#000635   NICET#135586
Key Fire Protection Enterprises LLC
3200 Mike Padgett HWY
Augusta, GA 30906
Office- (706) 790-3473
Cell- (706) 220-8822
Fax: (706) 738-2119



From: Sprinklerforum  On Behalf 
Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:44 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G 
Subject: RE: [EXTERNAL] Pipe adjacent to duct

Exactly.  It’s all up in the air.  It was a BIM job and not an issue with 
anyone during coordination.  Now it’s all up in the air installed and seems to 
be an issue.  You can’t win some days.  Plus, it shouldn’t be an issue at all, 
but now it is.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
fax: 866-430-6107
tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”


From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Prahl, Craig/GVL via Sprinklerforum
Sent: Wednesday, January 15, 2020 9:41 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Prahl, Craig/GVL mailto:craig.pr...@jacobs.com>>; 
Travis Mack mailto:tm...@mfpdesign.com>>; David Bohannon 
mailto:rdbohan...@aol.com>>; Matthew J Willis 
mailto:ma...@rapidfireinc.com>>; 
jdenha...@stricklandfire.com<mailto:jdenha...@stricklandfire.com>
Subject: RE: [EXTERNAL] Pipe adjacent to duct

Well it’s only a click of the mouse and it’s moved, so what’s your problem?   

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:34 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Travis Mack mailto:tm...@mfpdesign.com>>; 
jdenha...@stricklandfire.com<mailto:jdenha...@stricklandfire.com>; Matthew J 
Willis mailto:ma...@rapidfireinc.com>>; David Bohannon 
mailto:rdbohan...@aol.com>>
Subject: Re: [EXTERNAL] Pipe adjacent to duct

Lol. That’s too funny. Everyone thinks fire sprinkler can just magically move.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail

Re: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Ben Young via Sprinklerforum
Michael it sounds like you need to find some better GCs to work with then

On Wed, Jan 15, 2020 at 11:51 AM Michael Goodis via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> Bim modeling, that’s funny. Never seen it work yet…. Only thing its been
> god for is (your duct is in the way, we see you cant move, the model is
> wrong, let now reroute due to the conflict, oh and wait, its not a CO
> because this should have been caught during the bim modeling.)
>
>
>
> Great stuff with the GC’s pushing it off to try and cut the change orders
> out. Gotta love it.
>
>
>
>
>
> *Michael Goodis *
>
> *Salesman, Project Manager*
>
> *IL#000635   NICET#135586*
>
> *Key Fire Protection Enterprises LLC*
>
> *3200 Mike Padgett HWY
> <https://www.google.com/maps/search/3200+Mike+Padgett+HWY+Augusta,+GA+30906+Office-+(706?entry=gmail=g>*
>
> *Augusta, GA 30906
> <https://www.google.com/maps/search/3200+Mike+Padgett+HWY+Augusta,+GA+30906+Office-+(706?entry=gmail=g>*
>
> *Office- (706
> <https://www.google.com/maps/search/3200+Mike+Padgett+HWY+Augusta,+GA+30906+Office-+(706?entry=gmail=g>)
> 790-3473*
>
> *Cell- (706) 220-8822*
>
> *Fax: (706) 738-2119*
>
>
>
>
>
>
>
> *From:* Sprinklerforum  *On
> Behalf Of *Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
> *Sent:* Wednesday, January 15, 2020 11:44 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Cc:* Travis Mack, SET, CFPS, CWBSP, RME-G 
> *Subject:* RE: [EXTERNAL] Pipe adjacent to duct
>
>
>
> *Exactly.  It’s all up in the air.  It was a BIM job and not an issue with
> anyone during coordination.  Now it’s all up in the air installed and seems
> to be an issue.  You can’t win some days.  Plus, it shouldn’t be an issue
> at all, but now it is.*
>
>
>
> [image: MFP_logo_F] <http://www.mfpdesign.com/>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
>
> MFP Design, LLC
>
> 3356 E Vallejo Ct
> <https://www.google.com/maps/search/3356+E+Vallejo+Ct+Gilbert,+AZ+85298?entry=gmail=g>
>
> Gilbert, AZ 85298
> <https://www.google.com/maps/search/3356+E+Vallejo+Ct+Gilbert,+AZ+85298?entry=gmail=g>
>
> NEW EXTENSION: 480-505-9271 ext. 700
>
> fax: 866-430-6107
>
> tm...@mfpdesign.com
>
> www.mfpdesign.com
>
>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
>
> LinkedIn: https://www.linkedin.com/in/travismack
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>
>
>
>
> *“**The bitterness of poor quality remains long after the sweetness of
> low price is forgotten.”*
>
>
>
>
>
> *From:* Sprinklerforum  *On
> Behalf Of *Prahl, Craig/GVL via Sprinklerforum
> *Sent:* Wednesday, January 15, 2020 9:41 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Cc:* Prahl, Craig/GVL ; Travis Mack <
> tm...@mfpdesign.com>; David Bohannon ; Matthew J
> Willis ; jdenha...@stricklandfire.com
> *Subject:* RE: [EXTERNAL] Pipe adjacent to duct
>
>
>
> Well it’s only a click of the mouse and it’s moved, so what’s your
> problem?   
>
>
>
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |
> craig.pr...@jacobs.com | www.jacobs.com
>
> 1041 East Butler Road
> <https://www.google.com/maps/search/1041+East+Butler+Road+Greenville,+South+Carolina+29606?entry=gmail=g>
> Greenville, South Carolina
> <https://www.google.com/maps/search/1041+East+Butler+Road+Greenville,+South+Carolina+29606?entry=gmail=g>
> 29606
> <https://www.google.com/maps/search/1041+East+Butler+Road+Greenville,+South+Carolina+29606?entry=gmail=g>
>
>
>
> *From:* Sprinklerforum  *On
> Behalf Of *Travis Mack via Sprinklerforum
> *Sent:* Wednesday, January 15, 2020 11:34 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Cc:* Travis Mack ; jdenha...@stricklandfire.com;
> Matthew J Willis ; David Bohannon <
> rdbohan...@aol.com>
> *Subject:* Re: [EXTERNAL] Pipe adjacent to duct
>
>
>
> Lol. That’s too funny. Everyone thinks fire sprinkler can just magically
> move.
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
>
> 480-505-9271 x700
>
> MFP Design, LLC
>
> www.mfpdesign,com
>
> Send large files to MFP D

RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Anthony C via Sprinklerforum
The only reference to clearance is for structural members 

 

NFPA 13 – 2016 edition: 9.3.4.9 The installed horizontal and upward vertical 
clearance between horizontal sprinkler piping and structural members not 
penetrated or used, collectively or independently, to support the piping shall 
be at least 2 in. (50 mm).

If it were a branch-line with sprinklers then per NFPA 13 -2016 edition: 
9.3.4.11* The installed clearance between a sprinkler and structural elements 
not used collectively or independently to support the sprinklers shall be at 
least 3 in. (75 mm).

 

Nothing referencing Mechanical that I know of.

 

Anthony Carrizosa 

Project Manager | Fire Protection 

7855 S 206th St Kent, WA 98032

Cell: 206-679-5283 | Office: 253-872-7222 

 



 <https://archerconstruction.com/> https://archerconstruction.com

 

From: Prahl, Craig/GVL  
Sent: Wednesday, January 15, 2020 8:54 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G 
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Well, when I’ve gotten that “it’s in the code” response from an AHJ and I am 
pretty certain it is not, I respectfully request them to please provide me with 
the code reference so I can present it as part of my Change Notice to the GC 
for design modifications which cannot be made until such code reference is 
received and the change is approved.  

 

This way I’m not challenging them, but seeking their assistance.  When they 
can’t produce any reference, the issue goes away.  I copy key people on the 
project so that they are aware of the issue.  

 

It’s just a more diplomatic way of saying “prove it”.

 

The fact is that most AHJ types or reviewers only review the drawings 
associated with their specific area of responsibility.  They do not care about 
coordination, that’s part of the responsibility of the design professional.  So 
they would most likely never pick up on something like this during permit 
reviews.  

 

Ain’t this fun?  “I need you to move your 8” system main, I’ve got a ½” water 
line that needs to get through.”   

 

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |  
<mailto:craig.pr...@jacobs.com> craig.pr...@jacobs.com |  
<http://www.jacobs.com/> www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

 

From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis 
Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:44 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G mailto:tm...@mfpdesign.com> >
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Exactly.  It’s all up in the air.  It was a BIM job and not an issue with 
anyone during coordination.  Now it’s all up in the air installed and seems to 
be an issue.  You can’t win some days.  Plus, it shouldn’t be an issue at all, 
but now it is.

 

 
<https://urldefense.com/v3/__http:/www.mfpdesign.com/__;!!B5cixuoO7ltTeg!SYGlq52zxPFHvfw4LVunwooDhKL-TrLct9Q-XaSad4uj6L61mxK7neezT8XzAYnzSg$>
 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

fax: 866-430-6107

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

www.mfpdesign.com 
<https://urldefense.com/v3/__http:/www.mfpdesign.com__;!!B5cixuoO7ltTeg!SYGlq52zxPFHvfw4LVunwooDhKL-TrLct9Q-XaSad4uj6L61mxK7neezT8WzVSu4mQ$>
 

 

Send large files to us via:  
<https://urldefense.com/v3/__https:/na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.hightail.com*2Fu*2FMFPDesign=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5*2BAZvlHhABSexWY*3D=0__;JSUlJSUlJSUlJSUlJSU!!B5cixuoO7ltTeg!SYGlq52zxPFHvfw4LVunwooDhKL-TrLct9Q-XaSad4uj6L61mxK7neezT8VaBc3Www$>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://urldefense.com/v3/__https:/na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.linkedin.com*2Fin*2Ftravismack=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN*2BZodi*2FhbeCbHNRijI*3D=0__;JSUlJSUlJSUlJSUlJSUl!!B5cixuoO7ltTeg!SYGlq52zxPFHvfw4LVunwooDhKL-TrLct9Q-XaSad4uj6L61mxK7neezT8XHIcau2Q$>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

 

From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Prahl, 
Craig/GVL via Sprinklerforum
Sent: Wednesday, January 15, 2020 9:41 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Prahl, Craig/GVL mailto:craig.pr...@jacobs.com> >; 
Travis Mack mailto:tm...@mfpdesign.com> >; David Bohannon 

RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Bob Knight via Sprinklerforum
Michael, LOL!  The best thing about BIM modeling is the extra money it 
generates.  Once out in the field the plumbers, HVAC, and sparky’s all act like 
they’ve never heard of such a beast, but that’s only because sprinklers guys 
are all pure as the driven snow.

 

 

Thank you,

 

Bob Knight, CET III

Fire by Knight, LLC

208-318-3057

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Michael Goodis via Sprinklerforum
Sent: Wednesday, January 15, 2020 9:52 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Michael Goodis; 'Travis Mack, SET, CFPS, CWBSP, RME-G'
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Bim modeling, that’s funny. Never seen it work yet…. Only thing its been god 
for is (your duct is in the way, we see you cant move, the model is wrong, let 
now reroute due to the conflict, oh and wait, its not a CO because this should 
have been caught during the bim modeling.) 

 

Great stuff with the GC’s pushing it off to try and cut the change orders out. 
Gotta love it.

 

 

Michael Goodis 

Salesman, Project Manager

IL#000635   NICET#135586

Key Fire Protection Enterprises LLC

3200 Mike Padgett HWY

Augusta, GA 30906

Office- (706) 790-3473

Cell- (706) 220-8822

Fax: (706) 738-2119

 

 

 

From: Sprinklerforum  On Behalf 
Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:44 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G 
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Exactly.  It’s all up in the air.  It was a BIM job and not an issue with 
anyone during coordination.  Now it’s all up in the air installed and seems to 
be an issue.  You can’t win some days.  Plus, it shouldn’t be an issue at all, 
but now it is.

 

 <http://www.mfpdesign.com/> MFP_logo_F

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

fax: 866-430-6107

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

www.mfpdesign.com

 

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

 

From: Sprinklerforum  On Behalf 
Of Prahl, Craig/GVL via Sprinklerforum
Sent: Wednesday, January 15, 2020 9:41 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Prahl, Craig/GVL ; Travis Mack 
; David Bohannon ; Matthew J Willis 
; jdenha...@stricklandfire.com
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Well it’s only a click of the mouse and it’s moved, so what’s your problem?    

 

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |  
<mailto:craig.pr...@jacobs.com> craig.pr...@jacobs.com |  
<http://www.jacobs.com/> www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

 

From: Sprinklerforum  On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:34 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack ; jdenha...@stricklandfire.com; Matthew J 
Willis ; David Bohannon 
Subject: Re: [EXTERNAL] Pipe adjacent to duct

 

Lol. That’s too funny. Everyone thinks fire sprinkler can just magically move. 

Travis Mack, CFPS, CWBSP, RME-G, SET

480-505-9271 x700

MFP Design, LLC

www.mfpdesign,com

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign 
<https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona4GLVqxWQ$>
 

 

Sent from my iPhone

 

On Jan 15, 2020, at 9:23 AM, Matthew J Willis via Sprinklerforum 
 wrote:

 

Hahahahaha

 

 

 

 

From: David Bohannon  
Sent: Wednesday, January 15, 2020 9:21 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matthew J Willis ; jdenha...@stricklandfire.com
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Just a question. If the duct is to close to the fire main why wouldn’t the duct 
have to move? Isn’t life safety more important than climate comfort?

Sent from AOL Mobile Mail
Get the new AOL app: mail.mobile.aol.com 
<https://urldefense.com/v3/__http:/mail.mobile.aol.com__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7NH3VpRw$>
 

 

On Wednesday, January 15, 2020, John Denhardt via Sprinklerforum 
 wrote: 

 

I am una

RE: Pipe adjacent to duct

2020-01-15 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Bob:

 

I believe that is in Section 9.3 which is the seismic section.  This job is 
Seismic Design Category B, so 9.3 doesn’t apply.

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

fax: 866-430-6107

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

www.mfpdesign.com

 

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

 

From: Sprinklerforum  On Behalf 
Of Bob Knight via Sprinklerforum
Sent: Wednesday, January 15, 2020 10:02 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Bob Knight 
Subject: RE: Pipe adjacent to duct

 

Travis,

The only thing I can think of is where there is to be a 2” clearance to 
structural that isn’t supporting piping.  The AHJ could be confused as to what 
is structural and what isn’t.

 

 

Thank you,

 

Bob Knight, CET III

Fire by Knight, LLC

208-318-3057

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 6:54 AM
To: mailto:sprinklerforum@lists.firesprinkler.org> >
Cc: Travis Mack
Subject: Pipe adjacent to duct

 

We have a project where the fire inspector is stating that the fire sprinkler 
main is too close to ductwork.  There is a 6” main that is about 1/2” from the 
ductwork. 

 

Of course, the inspectors response is “it’s in the code book” when asking for a 
reference that mandates clearance to hvac ductwork. 

 

Has anyone run into something similar?

 

Note: this is not a high temp duct that would cause for enough heat to convert 
the sprinkler water to steam. This is just your standard, run of the mill, HVAC 
system. 

Travis Mack, CFPS, CWBSP, RME-G, SET

480-505-9271 x700

MFP Design, LLC

www.mfpdesign,com <http://www.mfpdesign,com> 

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

 

Sent from my iPhone

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pipe adjacent to duct

2020-01-15 Thread Bob Knight via Sprinklerforum
Travis,

The only thing I can think of is where there is to be a 2” clearance to 
structural that isn’t supporting piping.  The AHJ could be confused as to what 
is structural and what isn’t.

 

 

Thank you,

 

Bob Knight, CET III

Fire by Knight, LLC

208-318-3057

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 6:54 AM
To: 
Cc: Travis Mack
Subject: Pipe adjacent to duct

 

We have a project where the fire inspector is stating that the fire sprinkler 
main is too close to ductwork.  There is a 6” main that is about 1/2” from the 
ductwork. 

 

Of course, the inspectors response is “it’s in the code book” when asking for a 
reference that mandates clearance to hvac ductwork. 

 

Has anyone run into something similar?

 

Note: this is not a high temp duct that would cause for enough heat to convert 
the sprinkler water to steam. This is just your standard, run of the mill, HVAC 
system. 

Travis Mack, CFPS, CWBSP, RME-G, SET

480-505-9271 x700

MFP Design, LLC

www.mfpdesign,com

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

 

Sent from my iPhone

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Prahl, Craig/GVL via Sprinklerforum
Well, when I’ve gotten that “it’s in the code” response from an AHJ and I am 
pretty certain it is not, I respectfully request them to please provide me with 
the code reference so I can present it as part of my Change Notice to the GC 
for design modifications which cannot be made until such code reference is 
received and the change is approved.

This way I’m not challenging them, but seeking their assistance.  When they 
can’t produce any reference, the issue goes away.  I copy key people on the 
project so that they are aware of the issue.

It’s just a more diplomatic way of saying “prove it”.

The fact is that most AHJ types or reviewers only review the drawings 
associated with their specific area of responsibility.  They do not care about 
coordination, that’s part of the responsibility of the design professional.  So 
they would most likely never pick up on something like this during permit 
reviews.

Ain’t this fun?  “I need you to move your 8” system main, I’ve got a ½” water 
line that needs to get through.”

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum  On Behalf 
Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:44 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G 
Subject: RE: [EXTERNAL] Pipe adjacent to duct

Exactly.  It’s all up in the air.  It was a BIM job and not an issue with 
anyone during coordination.  Now it’s all up in the air installed and seems to 
be an issue.  You can’t win some days.  Plus, it shouldn’t be an issue at all, 
but now it is.

[MFP_logo_F]<https://urldefense.com/v3/__http:/www.mfpdesign.com/__;!!B5cixuoO7ltTeg!SYGlq52zxPFHvfw4LVunwooDhKL-TrLct9Q-XaSad4uj6L61mxK7neezT8XzAYnzSg$>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
fax: 866-430-6107
tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>
www.mfpdesign.com<https://urldefense.com/v3/__http:/www.mfpdesign.com__;!!B5cixuoO7ltTeg!SYGlq52zxPFHvfw4LVunwooDhKL-TrLct9Q-XaSad4uj6L61mxK7neezT8WzVSu4mQ$>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://urldefense.com/v3/__https:/na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.hightail.com*2Fu*2FMFPDesign=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5*2BAZvlHhABSexWY*3D=0__;JSUlJSUlJSUlJSUlJSU!!B5cixuoO7ltTeg!SYGlq52zxPFHvfw4LVunwooDhKL-TrLct9Q-XaSad4uj6L61mxK7neezT8VaBc3Www$>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://urldefense.com/v3/__https:/na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.linkedin.com*2Fin*2Ftravismack=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN*2BZodi*2FhbeCbHNRijI*3D=0__;JSUlJSUlJSUlJSUlJSUl!!B5cixuoO7ltTeg!SYGlq52zxPFHvfw4LVunwooDhKL-TrLct9Q-XaSad4uj6L61mxK7neezT8XHIcau2Q$>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”


From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Prahl, Craig/GVL via Sprinklerforum
Sent: Wednesday, January 15, 2020 9:41 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Prahl, Craig/GVL mailto:craig.pr...@jacobs.com>>; 
Travis Mack mailto:tm...@mfpdesign.com>>; David Bohannon 
mailto:rdbohan...@aol.com>>; Matthew J Willis 
mailto:ma...@rapidfireinc.com>>; 
jdenha...@stricklandfire.com<mailto:jdenha...@stricklandfire.com>
Subject: RE: [EXTERNAL] Pipe adjacent to duct

Well it’s only a click of the mouse and it’s moved, so what’s your problem?   

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:34 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Travis Mack mailto:tm...@mfpdesign.com>>; 
jdenha...@stricklandfire.com<mailto:jdenha...@stricklandfire.com>; Matthew J 
Willis mailto:ma...@rapidfireinc.com>>; David Bohannon 
mailto:rdbohan...@aol.com>>
Subject: Re: [EXTERNAL] Pipe adjacent to duct

Lol. That’s too funny. Everyone thinks fire sprinkler can just magically move.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com<https://u

RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Michael Goodis via Sprinklerforum
Bim modeling, that’s funny. Never seen it work yet…. Only thing its been god 
for is (your duct is in the way, we see you cant move, the model is wrong, let 
now reroute due to the conflict, oh and wait, its not a CO because this should 
have been caught during the bim modeling.) 

 

Great stuff with the GC’s pushing it off to try and cut the change orders out. 
Gotta love it.

 

 

Michael Goodis 

Salesman, Project Manager

IL#000635   NICET#135586

Key Fire Protection Enterprises LLC

3200 Mike Padgett HWY

Augusta, GA 30906

Office- (706) 790-3473

Cell- (706) 220-8822

Fax: (706) 738-2119

 

 

 

From: Sprinklerforum  On Behalf 
Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:44 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G 
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Exactly.  It’s all up in the air.  It was a BIM job and not an issue with 
anyone during coordination.  Now it’s all up in the air installed and seems to 
be an issue.  You can’t win some days.  Plus, it shouldn’t be an issue at all, 
but now it is.

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

fax: 866-430-6107

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

www.mfpdesign.com <http://www.mfpdesign.com> 

 

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

 

From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Prahl, 
Craig/GVL via Sprinklerforum
Sent: Wednesday, January 15, 2020 9:41 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Prahl, Craig/GVL mailto:craig.pr...@jacobs.com> >; 
Travis Mack mailto:tm...@mfpdesign.com> >; David Bohannon 
mailto:rdbohan...@aol.com> >; Matthew J Willis 
mailto:ma...@rapidfireinc.com> >; 
jdenha...@stricklandfire.com <mailto:jdenha...@stricklandfire.com> 
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Well it’s only a click of the mouse and it’s moved, so what’s your problem?    

 

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |  
<mailto:craig.pr...@jacobs.com> craig.pr...@jacobs.com |  
<http://www.jacobs.com/> www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

 

From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis 
Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:34 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Travis Mack mailto:tm...@mfpdesign.com> >; 
jdenha...@stricklandfire.com <mailto:jdenha...@stricklandfire.com> ; Matthew J 
Willis mailto:ma...@rapidfireinc.com> >; David 
Bohannon mailto:rdbohan...@aol.com> >
Subject: Re: [EXTERNAL] Pipe adjacent to duct

 

Lol. That’s too funny. Everyone thinks fire sprinkler can just magically move. 

Travis Mack, CFPS, CWBSP, RME-G, SET

480-505-9271 x700

MFP Design, LLC

www.mfpdesign,com <http://www.mfpdesign,com> 

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign 
<https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona4GLVqxWQ$>
 

 

Sent from my iPhone

 

On Jan 15, 2020, at 9:23 AM, Matthew J Willis via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org> > wrote:

 

Hahahahaha

 

 

 

 

From: David Bohannon mailto:rdbohan...@aol.com> > 
Sent: Wednesday, January 15, 2020 9:21 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Matthew J Willis mailto:ma...@rapidfireinc.com> >; 
jdenha...@stricklandfire.com <mailto:jdenha...@stricklandfire.com> 
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Just a question. If the duct is to close to the fire main why wouldn’t the duct 
have to move? Isn’t life safety more important than climate comfort?

Sent from AOL Mobile Mail
Get the new AOL app: mail.mobile.aol.com 
<https://urldefense.com/v3/__http

RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Exactly.  It’s all up in the air.  It was a BIM job and not an issue with 
anyone during coordination.  Now it’s all up in the air installed and seems to 
be an issue.  You can’t win some days.  Plus, it shouldn’t be an issue at all, 
but now it is.

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

fax: 866-430-6107

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

www.mfpdesign.com

 

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

 

From: Sprinklerforum  On Behalf 
Of Prahl, Craig/GVL via Sprinklerforum
Sent: Wednesday, January 15, 2020 9:41 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Prahl, Craig/GVL ; Travis Mack 
; David Bohannon ; Matthew J Willis 
; jdenha...@stricklandfire.com
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Well it’s only a click of the mouse and it’s moved, so what’s your problem?    

 

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |  
<mailto:craig.pr...@jacobs.com> craig.pr...@jacobs.com |  
<http://www.jacobs.com/> www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

 

From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis 
Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:34 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Travis Mack mailto:tm...@mfpdesign.com> >; 
jdenha...@stricklandfire.com <mailto:jdenha...@stricklandfire.com> ; Matthew J 
Willis mailto:ma...@rapidfireinc.com> >; David 
Bohannon mailto:rdbohan...@aol.com> >
Subject: Re: [EXTERNAL] Pipe adjacent to duct

 

Lol. That’s too funny. Everyone thinks fire sprinkler can just magically move. 

Travis Mack, CFPS, CWBSP, RME-G, SET

480-505-9271 x700

MFP Design, LLC

www.mfpdesign,com <http://www.mfpdesign,com> 

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign 
<https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona4GLVqxWQ$>
 

 

Sent from my iPhone





On Jan 15, 2020, at 9:23 AM, Matthew J Willis via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org> > wrote:

 

Hahahahaha

 

 

 

 

From: David Bohannon mailto:rdbohan...@aol.com> > 
Sent: Wednesday, January 15, 2020 9:21 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Matthew J Willis mailto:ma...@rapidfireinc.com> >; 
jdenha...@stricklandfire.com <mailto:jdenha...@stricklandfire.com> 
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Just a question. If the duct is to close to the fire main why wouldn’t the duct 
have to move? Isn’t life safety more important than climate comfort?

Sent from AOL Mobile Mail
Get the new AOL app: mail.mobile.aol.com 
<https://urldefense.com/v3/__http:/mail.mobile.aol.com__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7NH3VpRw$>
 

 

On Wednesday, January 15, 2020, John Denhardt via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org> > wrote: 

 

I am unaware of any language that would support the fire inspector’s position.

 

Thanks,

John

 

John August Denhardt, P.E.

Vice President Engineering and Technical Services

American Fire Sprinkler Association

301.343.1457 - Mobile

 

From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Matthew 
J Willis via Sprinklerforum
Sent: Wednesday, January 15, 2020 10:00 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Matthew J Willis mailto:ma...@rapidfireinc.com> >
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Educate him.

 

Use your charm.

 

R/

Matt

 

From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis 
Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 7:16 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Travis Mack mailto:tm...@mfpdesign

RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Prahl, Craig/GVL via Sprinklerforum
Well it’s only a click of the mouse and it’s moved, so what’s your problem?   

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum  On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:34 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack ; jdenha...@stricklandfire.com; Matthew J 
Willis ; David Bohannon 
Subject: Re: [EXTERNAL] Pipe adjacent to duct

Lol. That’s too funny. Everyone thinks fire sprinkler can just magically move.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign<https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona4GLVqxWQ$>

Sent from my iPhone


On Jan 15, 2020, at 9:23 AM, Matthew J Willis via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:

Hahahahaha




From: David Bohannon mailto:rdbohan...@aol.com>>
Sent: Wednesday, January 15, 2020 9:21 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Matthew J Willis mailto:ma...@rapidfireinc.com>>; 
jdenha...@stricklandfire.com<mailto:jdenha...@stricklandfire.com>
Subject: RE: [EXTERNAL] Pipe adjacent to duct

Just a question. If the duct is to close to the fire main why wouldn’t the duct 
have to move? Isn’t life safety more important than climate comfort?
Sent from AOL Mobile Mail
Get the new AOL app: 
mail.mobile.aol.com<https://urldefense.com/v3/__http:/mail.mobile.aol.com__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7NH3VpRw$>

On Wednesday, January 15, 2020, John Denhardt via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:


I am unaware of any language that would support the fire inspector’s position.



Thanks,

John



John August Denhardt, P.E.

Vice President Engineering and Technical Services

American Fire Sprinkler Association

301.343.1457 - Mobile



From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Matthew J Willis via Sprinklerforum
Sent: Wednesday, January 15, 2020 10:00 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Matthew J Willis mailto:ma...@rapidfireinc.com>>
Subject: RE: [EXTERNAL] Pipe adjacent to duct



Educate him.



Use your charm.



R/

Matt



From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 7:16 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Travis Mack mailto:tm...@mfpdesign.com>>; Prahl, 
Craig/GVL mailto:craig.pr...@jacobs.com>>
Subject: Re: [EXTERNAL] Pipe adjacent to duct



No seismic. No insulation.

Travis Mack, CFPS, CWBSP, RME-G, SET

480-505-9271 x700

MFP Design, LLC

www.mfpdesign,com<https://urldefense.com/v3/__http:/www.mfpdesign,com__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7aUKCG7Q$>

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign<https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona4GLVqxWQ$>



Sent from my iPhone



On Jan 15, 2020, at 7:12 AM, Prahl, Craig/GVL via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:



Could it be related to seismic movement of unrestrained ductwork against the FP 
pipe?



When you say ductwork, is that ½” between pipe and insulation or actual sheet 
metal?



Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>

1041 East Butler Road   Greenville, South Carolina  29606



From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 8:54 AM
To: 
mailto:sprinklerforum@lists.firesprinkler.org>>
 
mailto:sprinklerforum@lists.firesprinkler.org>>
Cc: Travis Mack mailto:tm...@mfpdesign.com>>
Subject: [EXTERNAL] Pipe adjacent to duct



We have a project where the fire inspector is stating that the fire sprinkler 
main is too close to ductwork.  There is a 6” main that is about 1/2” from the 
ductwork.



Of course, the inspectors response is “it’s in the code book” when asking for a 
reference that mandates clearance to hvac ductwork.



Has anyone run into something similar?



Note: this is 

Re: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Travis Mack via Sprinklerforum
Lol. That’s too funny. Everyone thinks fire sprinkler can just magically move. 

Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Jan 15, 2020, at 9:23 AM, Matthew J Willis via Sprinklerforum 
>  wrote:
> 
> 
> Hahahahaha
>  
>  
>  
>  
> From: David Bohannon  
> Sent: Wednesday, January 15, 2020 9:21 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Matthew J Willis ; jdenha...@stricklandfire.com
> Subject: RE: [EXTERNAL] Pipe adjacent to duct
>  
> Just a question. If the duct is to close to the fire main why wouldn’t the 
> duct have to move? Isn’t life safety more important than climate comfort?
> 
> Sent from AOL Mobile Mail
> Get the new AOL app: mail.mobile.aol.com
>  
> On Wednesday, January 15, 2020, John Denhardt via Sprinklerforum 
>  wrote:
>  
> I am unaware of any language that would support the fire inspector’s position.
> 
>  
> 
> Thanks,
> 
> John
> 
>  
> 
> John August Denhardt, P.E.
> 
> Vice President Engineering and Technical Services
> 
> American Fire Sprinkler Association
> 
> 301.343.1457 - Mobile
> 
>  
> 
> From: Sprinklerforum  On 
> Behalf Of Matthew J Willis via Sprinklerforum
> Sent: Wednesday, January 15, 2020 10:00 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Matthew J Willis 
> Subject: RE: [EXTERNAL] Pipe adjacent to duct
> 
>  
> 
> Educate him.
> 
>  
> 
> Use your charm.
> 
>  
> 
> R/
> 
> Matt
> 
>  
> 
> From: Sprinklerforum  On 
> Behalf Of Travis Mack via Sprinklerforum
> Sent: Wednesday, January 15, 2020 7:16 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Travis Mack ; Prahl, Craig/GVL 
> 
> Subject: Re: [EXTERNAL] Pipe adjacent to duct
> 
>  
> 
> No seismic. No insulation. 
> 
> Travis Mack, CFPS, CWBSP, RME-G, SET
> 
> 480-505-9271 x700
> 
> MFP Design, LLC
> 
> www.mfpdesign,com
> 
> Send large files to MFP Design via:
> 
> https://www.hightail.com/u/MFPDesign
> 
>  
> 
> Sent from my iPhone
> 
>  
> 
> On Jan 15, 2020, at 7:12 AM, Prahl, Craig/GVL via Sprinklerforum 
>  wrote:
> 
> 
> 
> Could it be related to seismic movement of unrestrained ductwork against the 
> FP pipe?
> 
>  
> 
> When you say ductwork, is that ½” between pipe and insulation or actual sheet 
> metal?  
> 
>  
> 
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
> craig.pr...@jacobs.com | www.jacobs.com
> 
> 1041 East Butler Road   Greenville, South Carolina  29606
> 
>  
> 
> From: Sprinklerforum  On 
> Behalf Of Travis Mack via Sprinklerforum
> Sent: Wednesday, January 15, 2020 8:54 AM
> To:  
> 
> Cc: Travis Mack 
> Subject: [EXTERNAL] Pipe adjacent to duct
> 
>  
> 
> We have a project where the fire inspector is stating that the fire sprinkler 
> main is too close to ductwork.  There is a 6” main that is about 1/2” from 
> the ductwork. 
> 
>  
> 
> Of course, the inspectors response is “it’s in the code book” when asking for 
> a reference that mandates clearance to hvac ductwork. 
> 
>  
> 
> Has anyone run into something similar?
> 
>  
> 
> Note: this is not a high temp duct that would cause for enough heat to 
> convert the sprinkler water to steam. This is just your standard, run of the 
> mill, HVAC system. 
> 
> Travis Mack, CFPS, CWBSP, RME-G, SET
> 
> 480-505-9271 x700
> 
> MFP Design, LLC
> 
> www.mfpdesign,com
> 
> Send large files to MFP Design via:
> 
> https://www.hightail.com/u/MFPDesign
> 
>  
> 
> Sent from my iPhone
> 
>  
> 
> 
> NOTICE - This communication may contain confidential and privileged 
> information that is for the sole use of the intended recipient. Any viewing, 
> copying or distribution of, or reliance on this message by unintended 
> recipients is strictly prohibited. If you have received this message in 
> error, please notify us immediately by replying to the message and deleting 
> it from your computer.
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Matthew J Willis via Sprinklerforum
Hahahahaha




From: David Bohannon 
Sent: Wednesday, January 15, 2020 9:21 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matthew J Willis ; jdenha...@stricklandfire.com
Subject: RE: [EXTERNAL] Pipe adjacent to duct

Just a question. If the duct is to close to the fire main why wouldn’t the duct 
have to move? Isn’t life safety more important than climate comfort?
Sent from AOL Mobile Mail
Get the new AOL app: mail.mobile.aol.com<http://mail.mobile.aol.com>

On Wednesday, January 15, 2020, John Denhardt via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:


I am unaware of any language that would support the fire inspector’s position.



Thanks,

John



John August Denhardt, P.E.

Vice President Engineering and Technical Services

American Fire Sprinkler Association

301.343.1457 - Mobile



From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Matthew J Willis via Sprinklerforum
Sent: Wednesday, January 15, 2020 10:00 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Matthew J Willis mailto:ma...@rapidfireinc.com>>
Subject: RE: [EXTERNAL] Pipe adjacent to duct



Educate him.



Use your charm.



R/

Matt



From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 7:16 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Travis Mack mailto:tm...@mfpdesign.com>>; Prahl, 
Craig/GVL mailto:craig.pr...@jacobs.com>>
Subject: Re: [EXTERNAL] Pipe adjacent to duct



No seismic. No insulation.

Travis Mack, CFPS, CWBSP, RME-G, SET

480-505-9271 x700

MFP Design, LLC

www.mfpdesign,com<http://www.mfpdesign,com>

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign



Sent from my iPhone



On Jan 15, 2020, at 7:12 AM, Prahl, Craig/GVL via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:



Could it be related to seismic movement of unrestrained ductwork against the FP 
pipe?



When you say ductwork, is that ½” between pipe and insulation or actual sheet 
metal?



Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>

1041 East Butler Road   Greenville, South Carolina  29606



From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 8:54 AM
To: 
mailto:sprinklerforum@lists.firesprinkler.org>>
 
mailto:sprinklerforum@lists.firesprinkler.org>>
Cc: Travis Mack mailto:tm...@mfpdesign.com>>
Subject: [EXTERNAL] Pipe adjacent to duct



We have a project where the fire inspector is stating that the fire sprinkler 
main is too close to ductwork.  There is a 6” main that is about 1/2” from the 
ductwork.



Of course, the inspectors response is “it’s in the code book” when asking for a 
reference that mandates clearance to hvac ductwork.



Has anyone run into something similar?



Note: this is not a high temp duct that would cause for enough heat to convert 
the sprinkler water to steam. This is just your standard, run of the mill, HVAC 
system.

Travis Mack, CFPS, CWBSP, RME-G, SET

480-505-9271 x700

MFP Design, LLC

www.mfpdesign,com<http://www.mfpdesign,com>

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign<https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!VcjF30iEaFuEx1cvHWPEx0GwlCXjsi62_q06GNj_cf6hxAEmmhx_JZyYbSEuPjBOcw$>



Sent from my iPhone





NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread David Bohannon via Sprinklerforum
Just a question. If the duct is to close to the fire main why wouldn’t the duct 
have to move? Isn’t life safety more important than climate comfort?

Sent from AOL Mobile Mail
Get the new AOL app: mail.mobile.aol.com
 On Wednesday, January 15, 2020, John Denhardt via Sprinklerforum 
 wrote:

#yiv7418936655 #yiv7418936655 -- _filtered {} _filtered {} _filtered 
{}#yiv7418936655 #yiv7418936655 p.yiv7418936655MsoNormal, #yiv7418936655 
li.yiv7418936655MsoNormal, #yiv7418936655 div.yiv7418936655MsoNormal 
{margin:0in;margin-bottom:.0001pt;font-size:11.0pt;font-family:sans-serif;}#yiv7418936655
 a:link, #yiv7418936655 span.yiv7418936655MsoHyperlink 
{color:blue;text-decoration:underline;}#yiv7418936655 
span.yiv7418936655EmailStyle21 
{font-family:sans-serif;color:blue;font-weight:normal;font-style:normal;}#yiv7418936655
 .yiv7418936655MsoChpDefault {font-size:10.0pt;} _filtered {}#yiv7418936655 
div.yiv7418936655WordSection1 {}#yiv7418936655 
I am unaware of any language that would support the fire inspector’s position.
 
  
 
Thanks,
 
John
 
  
 
John August Denhardt, P.E.
 
Vice President Engineering and Technical Services
 
American Fire Sprinkler Association
 
301.343.1457 - Mobile
 
  
 
From: Sprinklerforum On Behalf 
Of Matthew J Willis via Sprinklerforum
Sent: Wednesday, January 15, 2020 10:00 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matthew J Willis 
Subject: RE: [EXTERNAL] Pipe adjacent to duct
 
  
 
Educate him.
 
  
 
Use your charm.
 
  
 
R/
 
Matt
 
  
 
From: Sprinklerforum On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 7:16 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack ; Prahl, Craig/GVL 
Subject: Re: [EXTERNAL] Pipe adjacent to duct
 
  
 
No seismic. No insulation. 
 
Travis Mack, CFPS, CWBSP, RME-G, SET
 
480-505-9271 x700
 
MFP Design, LLC
 
www.mfpdesign,com
 
Send large files to MFP Design via:
 
https://www.hightail.com/u/MFPDesign
 
  
 
Sent from my iPhone
 
  
 

On Jan 15, 2020, at 7:12 AM, Prahl, Craig/GVL via Sprinklerforum 
 wrote:
 


 
 
Could it be related to seismic movement of unrestrained ductwork against the FP 
pipe?
 
 
 
When you say ductwork, is that ½” between pipe and insulation or actual sheet 
metal?  
 
 
 
Craig Prahl|Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com|www.jacobs.com
 
1041 East Butler Road   Greenville, South Carolina  29606
 
 
 
From: Sprinklerforum On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 8:54 AM
To:  

Cc: Travis Mack 
Subject: [EXTERNAL] Pipe adjacent to duct
 
 
 
We have a project where the fire inspector is stating that the fire sprinkler 
main is too close to ductwork.  There is a 6” main that is about 1/2” from the 
ductwork. 
 
 
 
Of course, the inspectors response is “it’s in the code book” when asking for a 
reference that mandates clearance to hvac ductwork. 
 
 
 
Has anyone run into something similar?
 
 
 
Note: this is not a high temp duct that would cause for enough heat to convert 
the sprinkler water to steam. This is just your standard, run of the mill, HVAC 
system. 
 
Travis Mack, CFPS, CWBSP, RME-G, SET
 
480-505-9271 x700
 
MFP Design, LLC
 
www.mfpdesign,com
 
Send large files to MFP Design via:
 
https://www.hightail.com/u/MFPDesign
 
 
 
Sent from my iPhone
 
  
 

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread John Denhardt via Sprinklerforum
I am unaware of any language that would support the fire inspector’s position.

Thanks,
John

John August Denhardt, P.E.
Vice President Engineering and Technical Services
American Fire Sprinkler Association
301.343.1457 - Mobile

From: Sprinklerforum  On Behalf 
Of Matthew J Willis via Sprinklerforum
Sent: Wednesday, January 15, 2020 10:00 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matthew J Willis 
Subject: RE: [EXTERNAL] Pipe adjacent to duct

Educate him.

Use your charm.

R/
Matt

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 7:16 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Travis Mack mailto:tm...@mfpdesign.com>>; Prahl, 
Craig/GVL mailto:craig.pr...@jacobs.com>>
Subject: Re: [EXTERNAL] Pipe adjacent to duct

No seismic. No insulation.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Jan 15, 2020, at 7:12 AM, Prahl, Craig/GVL via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:

Could it be related to seismic movement of unrestrained ductwork against the FP 
pipe?

When you say ductwork, is that ½” between pipe and insulation or actual sheet 
metal?

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 8:54 AM
To: 
mailto:sprinklerforum@lists.firesprinkler.org>>
 
mailto:sprinklerforum@lists.firesprinkler.org>>
Cc: Travis Mack mailto:tm...@mfpdesign.com>>
Subject: [EXTERNAL] Pipe adjacent to duct

We have a project where the fire inspector is stating that the fire sprinkler 
main is too close to ductwork.  There is a 6” main that is about 1/2” from the 
ductwork.

Of course, the inspectors response is “it’s in the code book” when asking for a 
reference that mandates clearance to hvac ductwork.

Has anyone run into something similar?

Note: this is not a high temp duct that would cause for enough heat to convert 
the sprinkler water to steam. This is just your standard, run of the mill, HVAC 
system.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign<https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!VcjF30iEaFuEx1cvHWPEx0GwlCXjsi62_q06GNj_cf6hxAEmmhx_JZyYbSEuPjBOcw$>

Sent from my iPhone



NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Matthew J Willis via Sprinklerforum
Educate him.

Use your charm.

R/
Matt

From: Sprinklerforum  On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 7:16 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack ; Prahl, Craig/GVL 
Subject: Re: [EXTERNAL] Pipe adjacent to duct

No seismic. No insulation.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone


On Jan 15, 2020, at 7:12 AM, Prahl, Craig/GVL via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:

Could it be related to seismic movement of unrestrained ductwork against the FP 
pipe?

When you say ductwork, is that ½” between pipe and insulation or actual sheet 
metal?

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 8:54 AM
To: 
mailto:sprinklerforum@lists.firesprinkler.org>>
 
mailto:sprinklerforum@lists.firesprinkler.org>>
Cc: Travis Mack mailto:tm...@mfpdesign.com>>
Subject: [EXTERNAL] Pipe adjacent to duct

We have a project where the fire inspector is stating that the fire sprinkler 
main is too close to ductwork.  There is a 6” main that is about 1/2” from the 
ductwork.

Of course, the inspectors response is “it’s in the code book” when asking for a 
reference that mandates clearance to hvac ductwork.

Has anyone run into something similar?

Note: this is not a high temp duct that would cause for enough heat to convert 
the sprinkler water to steam. This is just your standard, run of the mill, HVAC 
system.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign<https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!VcjF30iEaFuEx1cvHWPEx0GwlCXjsi62_q06GNj_cf6hxAEmmhx_JZyYbSEuPjBOcw$>

Sent from my iPhone



NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Travis Mack via Sprinklerforum
No seismic. No insulation. 

Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Jan 15, 2020, at 7:12 AM, Prahl, Craig/GVL via Sprinklerforum 
>  wrote:
> 
> 
> Could it be related to seismic movement of unrestrained ductwork against the 
> FP pipe?
>  
> When you say ductwork, is that ½” between pipe and insulation or actual sheet 
> metal? 
>  
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
> craig.pr...@jacobs.com | www.jacobs.com
> 1041 East Butler Road   Greenville, South Carolina  29606
>  
> From: Sprinklerforum  On 
> Behalf Of Travis Mack via Sprinklerforum
> Sent: Wednesday, January 15, 2020 8:54 AM
> To:  
> 
> Cc: Travis Mack 
> Subject: [EXTERNAL] Pipe adjacent to duct
>  
> We have a project where the fire inspector is stating that the fire sprinkler 
> main is too close to ductwork.  There is a 6” main that is about 1/2” from 
> the ductwork. 
>  
> Of course, the inspectors response is “it’s in the code book” when asking for 
> a reference that mandates clearance to hvac ductwork. 
>  
> Has anyone run into something similar?
>  
> Note: this is not a high temp duct that would cause for enough heat to 
> convert the sprinkler water to steam. This is just your standard, run of the 
> mill, HVAC system. 
> 
> Travis Mack, CFPS, CWBSP, RME-G, SET
> 480-505-9271 x700
> MFP Design, LLC
> www.mfpdesign,com
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>  
> Sent from my iPhone
> 
> 
> NOTICE - This communication may contain confidential and privileged 
> information that is for the sole use of the intended recipient. Any viewing, 
> copying or distribution of, or reliance on this message by unintended 
> recipients is strictly prohibited. If you have received this message in 
> error, please notify us immediately by replying to the message and deleting 
> it from your computer.
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Prahl, Craig/GVL via Sprinklerforum
Could it be related to seismic movement of unrestrained ductwork against the FP 
pipe?

When you say ductwork, is that ½” between pipe and insulation or actual sheet 
metal?

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 8:54 AM
To: 
mailto:sprinklerforum@lists.firesprinkler.org>>
 
mailto:sprinklerforum@lists.firesprinkler.org>>
Cc: Travis Mack mailto:tm...@mfpdesign.com>>
Subject: [EXTERNAL] Pipe adjacent to duct

We have a project where the fire inspector is stating that the fire sprinkler 
main is too close to ductwork.  There is a 6” main that is about 1/2” from the 
ductwork.

Of course, the inspectors response is “it’s in the code book” when asking for a 
reference that mandates clearance to hvac ductwork.

Has anyone run into something similar?

Note: this is not a high temp duct that would cause for enough heat to convert 
the sprinkler water to steam. This is just your standard, run of the mill, HVAC 
system.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign<https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!VcjF30iEaFuEx1cvHWPEx0GwlCXjsi62_q06GNj_cf6hxAEmmhx_JZyYbSEuPjBOcw$>

Sent from my iPhone



NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pipe adjacent to duct

2020-01-15 Thread Greg McGahan via Sprinklerforum
I’ve never seen anything but we have had inspector’s misinterpret the 
prohibition for supporting anything from sprinkler pipe to mean touching…never 
seen this one though.

 

Greg McGahan

Genesis Fire Services, LLC

o-850-637-8535

 

From: Sprinklerforum  On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 7:54 AM
To:  

Cc: Travis Mack 
Subject: Pipe adjacent to duct

 

We have a project where the fire inspector is stating that the fire sprinkler 
main is too close to ductwork.  There is a 6” main that is about 1/2” from the 
ductwork. 

 

Of course, the inspectors response is “it’s in the code book” when asking for a 
reference that mandates clearance to hvac ductwork. 

 

Has anyone run into something similar?

 

Note: this is not a high temp duct that would cause for enough heat to convert 
the sprinkler water to steam. This is just your standard, run of the mill, HVAC 
system. 

Travis Mack, CFPS, CWBSP, RME-G, SET

480-505-9271 x700

MFP Design, LLC

www.mfpdesign,com <http://www.mfpdesign,com> 

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

 

Sent from my iPhone

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Pipe adjacent to duct

2020-01-15 Thread Travis Mack via Sprinklerforum
We have a project where the fire inspector is stating that the fire sprinkler 
main is too close to ductwork.  There is a 6” main that is about 1/2” from the 
ductwork. 

Of course, the inspectors response is “it’s in the code book” when asking for a 
reference that mandates clearance to hvac ductwork. 

Has anyone run into something similar?

Note: this is not a high temp duct that would cause for enough heat to convert 
the sprinkler water to steam. This is just your standard, run of the mill, HVAC 
system. 

Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone___