2012-09-03 Thread George Church
in: MN -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Gregory Lindholm Sent: Friday, August 31, 2012 1:41 PM To: SprinklerFORUM Subject: RE: Attic Remote Area Yes, I was thinking about using

Re: Attic Remote Area

2012-08-31 Thread Roland Huggins
concur, we ignore even rated walls unless using room design method. There is new guidance on how to address small subsystems (such as dry- pipe on loading docks or preaction in computer room) in the 2013 edition of NFPA 13. This use to be a particularly tricky issue when applying logic for

RE: Attic Remote Area

2012-08-31 Thread Gregory Lindholm
...@firesprinkler.org To: sprinklerforum@firesprinkler.org Subject: Re: Attic Remote Area Date: Fri, 31 Aug 2012 11:26:16 -0700 concur, we ignore even rated walls unless using room design method. There is new guidance on how to address small subsystems (such as dry- pipe on loading docks