From: sprinklerforum-boun...@lists.firesprinkler.org on behalf of Brad
Casterline
Sent: Fri 5/17/2013 9:13 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 22 2013 Water storage re-fill time.
Thanks Bruce. It is truly out in the sticks. 35 GPM well pump. The designer
/
From: sprinklerforum-boun...@lists.firesprinkler.org on behalf of Brad
Casterline
Sent: Fri 5/17/2013 9:13 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 22 2013 Water storage re-fill time.
Thanks Bruce. It is truly out
: NFPA 22 2013 Water storage re-fill time.
Owner can have an agreement with one (or more) local tanker company to
respond with x number of trucks to fill in 8. Heckuva lot cheaper than
redundant or double sized tank.
This should qualify as a means to fill in 8.
Sent from my iPhone
On May 17
asking for a co-worker:
1) Why are water storage tanks required to be re-filled in 8 hours?
2) Would the requirement apply to ponds (man-made with liner in this case)?
3) Are there any alternatives to the requirement?
(the pond is large and filled by a well pump with a pumping rate that
to be
able to re-fill the tank within in 8 hours?.
-Original Message-
From: Brad Casterline [mailto:bcasterl...@fsc-inc.com]
Sent: Thursday, May 16, 2013 8:18 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: NFPA 22 2013 Water storage re-fill time.
asking for a co-worker:
1) Why
@lists.firesprinkler.org
Subject: RE: NFPA 22 2013 Water storage re-fill time.
ok good, now then, if you are/were an A.H.J., how would you answer this
question: How much time do we get to be able to re-fill a water storage tank
in 8 hours? for example, 150,000 gallon capacity for demand*duration, say
:43 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 22 2013 Water storage re-fill time.
ok good, now then, if you are/were an A.H.J., how would you answer this
question: How much time do we get to be able to re-fill a water storage
tank in 8 hours? for example, 150,000 gallon capacity
Thank you very much Duane, Craig, and George.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
2013 Water storage re-fill time.
I'm craig went to alien zombie mode as that is a what if I can live with as
it cancels the other what if.
On Thu, May 16, 2013 at 12:57 PM, Brad Casterline
bcasterl...@fsc-inc.comwrote:
Thank you very much Duane, Craig, and George
is not the time for hot work to support new equipment.
bv
From: Brad Casterline bcasterl...@fsc-inc.com
To: sprinklerforum@lists.firesprinkler.org
Sent: Thursday, May 16, 2013 11:42:59 AM
Subject: RE: NFPA 22 2013 Water storage re-fill time.
ok good, now then, if you are/were an A.H.J., how would