Subject: RE: Dual Purpose Fire Pump - Hydrants and Sprinklers
Hi Craig, I thought I would chime in ring, a helpful tool is the commentary
section of the IFC (appendix), which describes this very scenario. You are
right though because of SOG of many Fire Departments being
To: sprinklerforum@firesprinkler.org
Subject: RE: Dual Purpose Fire Pump - Hydrants and Sprinklers
So why would we rely on a written and adopted code or standard! Oh that's
right, because when we end up in court we have a written adopted document to
support or position. That usually works out better than, Well
: RE: Dual Purpose Fire Pump - Hydrants and Sprinklers
Hi Craig, I thought I would chime in ring, a helpful tool is the commentary
section of the IFC (appendix), which describes this very scenario. You are
right though because of SOG of many Fire Departments being different, it is
always best
Ralphy,
In my experience,please note the following:
Question #1 : The size of the tank should be based on the larger of the
two,estimated fire flow (which should include an estimated sprinkler demand) or
the actual sprinkler demand including required hose demand,for the required
duration.
Fire flow is from IFC Appendix B not NFPA. As far as I know 1500 gpm is the
minimum fire flow for any property. The inside/outside hose flow added to
sprinkler flow has nothing to do with fire flow from hydrants, they are two
completely separate issues. A reduction in fire flow is allowed for
Oh boy, where to begin...
1. Fire Flow: There are several methods of determining fire flow; (1) IBC
Appendix B, (2) NFPA 1, (3) NFPA Handbook, (4) ISO, (5) Local FD/Water
Dept./Ins. Which can be methods based on any of the above or something totally
different.)
It's up to whatever EOR
If your IFC, the following from appendix B, may apply to your project.
B105.2 Buildings other than one- and two-family dwellings.
The minimum fire-flow and flow duration for buildings other
than one- and two-family dwellings shall be as specified in
Table B105.1.
Exception: A reduction in
...@firesprinkler.org] On Behalf Of Thom
Sent: Wednesday, September 08, 2010 5:17 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dual Purpose Fire Pump - Hydrants and Sprinklers
If your IFC, the following from appendix B, may apply to your project.
B105.2 Buildings other than one- and two-family dwellings
Of
craig.pr...@ch2m.com
Sent: Wednesday, September 08, 2010 3:19 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dual Purpose Fire Pump - Hydrants and Sprinklers
Don't make that assumption. Fire flow is one thing that has no universal
rules and has no regard for the applicable building code
@firesprinkler.org
Subject: RE: Dual Purpose Fire Pump - Hydrants and Sprinklers
So why would we rely on a written and adopted code or standard! Oh that's
right, because when we end up in court we have a written adopted document to
support or position. That usually works out better than, Well I polled the
AHJ