RE: fire pump controller detection requirement

2013-05-07 Thread Failla, Daniel
Tim,

First I am working under the IFC 2012 that requires sprinkler systems to be 
electronically monitored with supervising central station.

Per Section NFPA 72, 2010 10.15  and the definitions of a Fire Alarm Control 
Unit and Dedicated Function Fire Alarm Control Unit, a smoke detector is 
required to be located above the fire pump control panel.

Daniel S. Failla Jr.
Assistant Fire Marshal
Charleston Fire Marshal's Office
75 Calhoun Street
3rd Floor
Charleston, SC 29401
Office - 843 - 724 - 5960
Email: fail...@charleston-sc.gov

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Easter, 
Timothy
Sent: Tuesday, May 07, 2013 11:35 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: fire pump controller detection requirement

I know smoke detectors are required within 5' of FACP/MNS panels, what about 
fire pump controller panels?

Regards,

Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: fire pump controller detection requirement

2013-05-07 Thread Bill Brooks
So, if it does not have a secondary power source it would not be a Dedicated
Function Fire Alarm Control Unit?

I don't believe the committee had a fire pump controller in mind when this
change was made. I never have thought of a fire pump controller as a
component of a fire alarm system, but I'm willing to be educated.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Failla,
Daniel
Sent: Tuesday, May 07, 2013 2:52 PM
To: 'sprinklerforum@lists.firesprinkler.org'
Subject: RE: fire pump controller detection requirement

Tim,

First I am working under the IFC 2012 that requires sprinkler systems to be
electronically monitored with supervising central station.

Per Section NFPA 72, 2010 10.15  and the definitions of a Fire Alarm Control
Unit and Dedicated Function Fire Alarm Control Unit, a smoke detector is
required to be located above the fire pump control panel.

Daniel S. Failla Jr.
Assistant Fire Marshal
Charleston Fire Marshal's Office
75 Calhoun Street
3rd Floor
Charleston, SC 29401
Office - 843 - 724 - 5960
Email: fail...@charleston-sc.gov

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Easter,
Timothy
Sent: Tuesday, May 07, 2013 11:35 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: fire pump controller detection requirement

I know smoke detectors are required within 5' of FACP/MNS panels, what about
fire pump controller panels?

Regards,

Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Fire Pump Controller

2008-12-08 Thread Arthur Tiroly
The fire pump controller can't be used as a junction box for other services.
Not sure where to find it. Ask the controller mfg.

Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
3300 King Ave
Cleveland, OH 44114
216-621-8899
216-570-7030 cell

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Monday, December 08, 2008 11:44 AM
To: sprinklerforum@firesprinkler.org
Subject: Fire Pump Controller

I just had a job site meeting with a electrical contractor. He stated the
engineer wanted to feed the jockey pump controller from the fire pump
controller. Something about a tapping rule or exception. I cautioned against
it, told him to research it first. Can anyone give me a section that
prohibits this arrangement from either NFPA 20 or NEC? 

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [EMAIL PROTECTED]
Web Site: http://www.burtellfire.com
? please don't print this e-mail unless you really need to


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Fire Pump Controller

2008-12-08 Thread Autry, David
NFPA 20 (1999, Edition) 7-3.4.4
A fire pump controller shall not be used as a junction box to supply other 
equipment. Electrical supply conductors for pressure maintenance (jockey or 
make-up) pump(s) shall not be connected to the fire pump controller.

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

** Note new email address: [EMAIL PROTECTED]

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Monday, December 08, 2008 10:44 AM
To: sprinklerforum@firesprinkler.org
Subject: Fire Pump Controller

I just had a job site meeting with a electrical contractor. He stated the 
engineer wanted to feed the jockey pump controller from the fire pump 
controller. Something about a tapping rule or exception. I cautioned against 
it, told him to research it first. Can anyone give me a section that prohibits 
this arrangement from either NFPA 20 or NEC?

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [EMAIL PROTECTED]
Web Site: http://www.burtellfire.com
 please don't print this e-mail unless you really need to


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

RE: Fire Pump Controller

2008-12-08 Thread Jeff Hewitt
Joe,

Try this:

NFPA 70, 2005 edition, 695.6 (F) Junction Points.  

Where wire connectors are used in the fire pump circuit, the connectors shall 
be listed.  A fire pump controller or fire pump power transfer switch, where 
provided, shall not be used as a junction box to supply other equipment, 
including a pressure maintenance (jockey) pump.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Monday, December 08, 2008 10:44 AM
To: sprinklerforum@firesprinkler.org
Subject: Fire Pump Controller

I just had a job site meeting with a electrical contractor. He stated the 
engineer wanted to feed the jockey pump controller from the fire pump 
controller. Something about a tapping rule or exception. I cautioned against 
it, told him to research it first. Can anyone give me a section that prohibits 
this arrangement from either NFPA 20 or NEC? 

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [EMAIL PROTECTED]
Web Site: http://www.burtellfire.com
 please don't print this e-mail unless you really need to


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Fire Pump Controller

2008-12-08 Thread Craig.Prahl
It is stated in the NEC, Article 695.6 (F)

(F) Junction Points. Where wire connectors are used in
the fire pump circuit, the connectors shall be listed. A fire
pump controller or fire pump power transfer switch, where
provided, shall not be used as a junction box to supply
other equipment, including a pressure maintenance (jockey)
pump(s). A fire pump controller and fire pump power transfer
switch, where provided, shall not serve any load other
than the fire pump for which it is intended.

Each controller is only for the pump it is designed to control/power.  Can't 
feed one from another, you need separate circuits.  So can't do as the engineer 
wants.

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Monday, December 08, 2008 11:44 AM
To: sprinklerforum@firesprinkler.org
Subject: Fire Pump Controller

I just had a job site meeting with a electrical contractor. He stated the 
engineer wanted to feed the jockey pump controller from the fire pump 
controller. Something about a tapping rule or exception. I cautioned against 
it, told him to research it first. Can anyone give me a section that prohibits 
this arrangement from either NFPA 20 or NEC?

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [EMAIL PROTECTED]
Web Site: http://www.burtellfire.com
P please don't print this e-mail unless you really need to


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Fire Pump Controller

2008-12-08 Thread Steve Leyton
I'm not sure that you can apply the NEC without invoking the debate about 
whether a pressure maintenance pump is a fire pump for purposes of applying 
and enforcing the electrical code.If you accept that it is, then the 
following applies from 70 (I took this from the 2006 Fall Revision Cycle so the 
section numbers might be a bit screwed up):

695.4 Continuity of Power.
Circuits that supply electric motor-driven fire pumps shall be supervised from 
inadvertent disconnection as covered in 695.4(A) or 695.4(B).

(A) Direct Connection. The supply conductors shall directly connect the power 
source to either a listed fire pump controller or listed combination fire pump 
controller and power transfer switch. [NFPA 20:9.3.2.2.2]

(B) Supervised Connection. A single disconnecting means and associated 
overcurrent protective device(s) shall be permitted to be installed between a 
remote power source and one of the following:  

(1) A listed fire pump controller
(2) A listed fire pump power transfer switch
(3) A listed combination fire pump controller and power transfer switch
For systems installed under the provisions of 695.3(B)(2) only, such additional 
disconnecting means and associated overcurrent protective device(s) shall be 
permitted as required to comply with other provisions of this Code. Overcurrent 
protective devices between an on-site standby generator and a fire pump 
controller shall be selected and sized according to 430.62 to provide 
short-circuit protection only. All disconnecting devices and overcurrent 
protective devices that are unique to the fire pump loads shall comply with 
695.4(B)(1) through (B)(5).

(1) Overcurrent Device Selection. The overcurrent protective device(s) shall be 
selected or set to carry indefinitely the sum of the locked-rotor current of 
the fire pump motor(s) and the pressure maintenance pump motor(s) and the 
full-load current of the associated fire pump accessory equipment when 
connected to this power supply. The requirement to carry the locked-rotor 
currents indefinitely shall not apply to conductors or devices other than 
overcurrent devices in the fire pump motor circuit(s).

(2) Disconnecting Means. The disconnecting means shall comply with all of the 
following:  

(1) Be identified as suitable for use as service equipment 
(2) Be lockable in the closed position
(3) Not be located within equipment that feeds loads other than the fire 
pump
(4) Be located sufficiently remote from other building or other fire pump 
source disconnecting means such that inadvertent contemporaneous operation 
would be unlikely


Note in (A) that supply shall be directly connected to the fire pump and that 
under Disconnecting Means, (3) says that the disconnect shall not arranged in 
other equipment.Not sure how/why they would want to do it combined anyway - 
the savings are nil and the complications potentially very expensive and 
intrusive.


Steve Leyton
Protection Design  Consulting
San Diego, CA

Please note:  Our offices will be closed 
from 12/29/08 to 1/02/09, returning 1/05/09.  
PDC wishes you a happy holiday season!



-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Monday, December 08, 2008 8:44 AM
To: sprinklerforum@firesprinkler.org
Subject: Fire Pump Controller

I just had a job site meeting with a electrical contractor. He stated the 
engineer wanted to feed the jockey pump controller from the fire pump 
controller. Something about a tapping rule or exception. I cautioned against 
it, told him to research it first. Can anyone give me a section that prohibits 
this arrangement from either NFPA 20 or NEC? 

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [EMAIL PROTECTED]
Web Site: http://www.burtellfire.com
 please don't print this e-mail unless you really need to


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
 

__ Information from ESET NOD32 Antivirus, version of virus signature 
database 3672 (20081208) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__ Information from ESET NOD32 Antivirus, version of virus signature 
database 3672 (20081208) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

RE: Fire Pump Controller

2008-12-08 Thread John Drucker
Joe,

Although NEC 695 does not cover (695.1(B)) jockey pumps they are permitted
to be connected to the fire pump feeder. There are however requirements for
tapping the fire pump feeder. The tap however cannot be taken within the
fire pump controller. The primary overcurrent and feeders shall consider the
sum of the locked rotor currents of the fire pump, jockey pump and and full
load currents of the associated controllers. 

695.3(A)
695.5(B)
695.6(C)(1)

If you have the 2005 NEC handbook close by take a look at page 1047, Exhibit
695.5.

John Drucker
Fire Protection Subcode Official
Electrical Inspector
Red Bank, NJ

  

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Monday, December 08, 2008 11:44 AM
To: sprinklerforum@firesprinkler.org
Subject: Fire Pump Controller

I just had a job site meeting with a electrical contractor. He stated the
engineer wanted to feed the jockey pump controller from the fire pump
controller. Something about a tapping rule or exception. I cautioned against
it, told him to research it first. Can anyone give me a section that
prohibits this arrangement from either NFPA 20 or NEC? 

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [EMAIL PROTECTED]
Web Site: http://www.burtellfire.com
P please don't print this e-mail unless you really need to


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Fire Pump Controller Mounting Requirements

2007-02-26 Thread Thom McMahon
If you have a concrete wall why wouldn't you just mount uni-strut to the 
wall, and the controller to the strut?


Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message - 
From: Mark Gouveia [EMAIL PROTECTED]

To: Sprinklerforum@firesprinkler.org
Sent: Monday, February 26, 2007 7:46 AM
Subject: Fire Pump Controller Mounting Requirements



I have a project where the electrician has pointed out an NEC code section
that requires the controller to be mounted on a non-combustible 
supporting

structure.  I can not remember a location where I have seen a controller
mounted on a OSB/Plywood sheathed wall.  I was thinking that this in 
general
should be a non-issue since the fire pump is to be located in a 1-hour 
rated

room.  However suppose you had a concrete room and mounted a 4x8 sheet of
plywood to the wall to support the controllers.  Is this wrong?  I have
calls into the electrical engineer and the pump supplier, however I am
curious what the forum has seen.

 NFPA 70 - National Electrical Code (2005 Edition)
 ARTICLE 695 Fire Pumps
 695.12 Equipment Location.
 ...
(F) Mounting. All fire pump control equipment shall be mounted in 
a

substantial manner on *noncombustible* supporting structures.


Thanks,
Mark Gouveia
Sprinkler Technology Design
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum





___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: Fire Pump Controller Mounting Requirements

2007-02-26 Thread Mark Gouveia

They are furing our the concrete walls with studs, insulation, and
sheathing.  We are making them install a non-combustible sheathing at this
time to keep the project going.

Based on Mr. Kaczor's input from the NEC Handbook, the intent is to *
prohibit* a plywood backboard behind the controllers.

Thanks for your help.



On 2/26/07, Thom McMahon [EMAIL PROTECTED] wrote:


If you have a concrete wall why wouldn't you just mount uni-strut to the
wall, and the controller to the strut?

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: Mark Gouveia  [EMAIL PROTECTED]
To: Sprinklerforum@firesprinkler.org
Sent: Monday, February 26, 2007 7:46 AM
Subject: Fire Pump Controller Mounting Requirements



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum