Re: Non-Combustible Concealed Space (NFPA 13 2013)

2018-05-10 Thread Jay Stough
; > *From:* Sprinklerforum [mailto: > sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Jay Stough > *Sent:* Wednesday, May 09, 2018 8:25 AM > *To:* Sprinkler Forum > *Subject:* Re: Non-Combustible Concealed Space (NFPA 13 2013) > > > > It is accessible thru the s

Re: Non-Combustible Concealed Space (NFPA 13 2013)

2018-05-09 Thread bcasterline
just wouldn’t be the same!! ;-) Mark at Aero 602 820-7894 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve Leyton Sent: Wednesday, May 09, 2018 2:16 PM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] RE: Non-Combustible Con

RE: Non-Combustible Concealed Space (NFPA 13 2013)

2018-05-09 Thread John Drucker
Of Steve Leyton Sent: Wednesday, May 09, 2018 2:16 PM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] RE: Non-Combustible Concealed Space (NFPA 13 2013) Absolutely. What could be a better gig than GETTING PAID to fight with fire officials?? Steve PS: No guarantee of result.

Re: Non-Combustible Concealed Space (NFPA 13 2013)

2018-05-09 Thread Roland Huggins
No restrictions due to the presence of gas fired heater except for 8.15.1.4 - composite wood joists channels and then its ALL heart-producing equipment. There is that goofy requirement in 13D for requiring a single sprinkler over gas-fired furnaces in attics. Think of it this way. THere’s

RE: Non-Combustible Concealed Space (NFPA 13 2013)

2018-05-09 Thread Mark.Phelps
...@lists.firesprinkler.org] On Behalf Of Steve Leyton Sent: Wednesday, May 09, 2018 2:16 PM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] RE: Non-Combustible Concealed Space (NFPA 13 2013) Absolutely. What could be a better gig than GETTING PAID to fight with fire officials?? Steve PS

RE: Non-Combustible Concealed Space (NFPA 13 2013)

2018-05-09 Thread Steve Leyton
, May 09, 2018 1:13 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Non-Combustible Concealed Space (NFPA 13 2013) Steve can I hire you to fight with AHJ’s when I have issues? Rocci Cetani III, CET Senior Designer Water-Based Fire Protections Systems Layout, Nicet Level III Northern

RE: Non-Combustible Concealed Space (NFPA 13 2013)

2018-05-09 Thread Rocci 3 Cetani
To: sprinklerforum@lists.firesprinkler.org Subject: RE: Non-Combustible Concealed Space (NFPA 13 2013) N Let’s stop using the word “accessible” in conjunction with T-Bar ceilings. As described in the standard for purposes of determining whether a non-combustible space might

RE: Non-Combustible Concealed Space (NFPA 13 2013)

2018-05-09 Thread Steve Leyton
exhausting … SML From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Jay Stough Sent: Wednesday, May 09, 2018 8:25 AM To: Sprinkler Forum Subject: Re: Non-Combustible Concealed Space (NFPA 13 2013) It is accessible thru the suspended ceiling with ladders. Jay

Re: Non-Combustible Concealed Space (NFPA 13 2013)

2018-05-09 Thread Jay Stough
It is accessible thru the suspended ceiling with ladders. *Jay Stough* NICET IV LAYOUT NICET III ITM On Wed, May 9, 2018 at 11:04 AM Casey Yardley wrote: > Jay, > > > > Are the non combustible concealed spaces readily accessible or no? > > > > > > > > *From: *Jay

RE: Non-Combustible Concealed Space (NFPA 13 2013)

2018-05-09 Thread Casey Yardley
Jay, Are the non combustible concealed spaces readily accessible or no? From: Jay Stough Sent: Wednesday, May 9, 2018 8:00 AM To: Sprinkler Forum Subject: Non-Combustible Concealed Space (NFPA 13 2013) We are bidding a school gym/locker rooms project that has non-combustible concealed