Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
bcasterl...@fsc-inc.com
Sent: Sunday, September 30, 2012 11:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler head Temperature requirement
all i got is some
: RE: Sprinkler head Temperature requirement
At home this morning and don't have the 2002 NFPA 13 laying around, but it may
be that if the older standard doesn't include the conditional application
granted in 8.3.2.3 (2010 ed.) then he or she is holding you to the letter of
the 2002. You might
- One Sprinkler at a Time
-Original Message-
From: Cahill, Christopher [mailto:ccah...@burnsmcd.com]
Sent: Monday, October 01, 2012 8:13 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
And so Response time difference is only one factor
, October 01, 2012 07:56 AM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
My name wasn't listed so I am not sure I am able to respond (actually I was out
of office on Fri).
In the 2002 edition, 8.3.2.1 states ordinary
: Johnson, Duane (NIH/OD/ORS) [C] [mailto:johnson...@mail.nih.gov]
Sent: Monday, October 01, 2012 8:28 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
Yes, keep the overall picture in mind. RTI is only one aspect. As others
have said, as more sprinklers
all i got is some numbers:
27' ceiling height, 9 deflector distance, couch on fire in the middle
of a large, open furniture showroom---
286F, standard response- activation time = 188 seconds
286F, quick response- activation time = 172 seconds
212F, standard response- activation time = 97
SoHigh release vertical heat plume hitting ceiling and starting to
spread out, immediate ring opens starts to cool fire but intermediate heads
in second ring open, dropping flow to first ring, but doing nothing to cool
fire, the third ring with even worse results. My understanding of QR
!EXACTLY! Ron :)
I never try to predict anything, per se, I try to find the DIFFERENCE
between scenarios, in this case the same Ceiling Height and Heat
Release Rate versus sprinkler Temp and RTI. For a benchmark, I found
the steady state HRR that would activate a 286 SR in ~180 seconds,
Verhei [mailto:bver...@comcast.net]
Sent: Saturday, September 29, 2012 12:47 AM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler head Temperature requirement
Mark
My understanding of this is to ensure that ordinary temp heads are replaced
with at least
: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Friday, September 28, 2012 2:39 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler head Temperature requirement
From a heat release aspect, and having had a somewhat recent
: sprinklerforum-boun...@firesprinkler.org on behalf of mphe...@aerofire.com
Sent: Sat 9/29/2012 5:56 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler head Temperature requirement
What we have is High temp heads installed in an ordinary hazard occupancy. I
believe 8.3.2.3 does explicitly
@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
At home this morning and don't have the 2002 NFPA 13 laying around, but it may
be that if the older standard doesn't include the conditional application
granted in 8.3.2.3 (2010 ed.) then he or she
: Re: Sprinkler head Temperature requirement
The 2002 version of 8.3.2.3 differs from 2010 only by the inclusion of
intermediate temp in the text. The store will be display in room style
settings, no storage. The roof is at 27 feet and is a panelized wood
structure with open web wood joist on 8
@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
All said and done, I think it's pretty clear that the intent is to allow the
use of those sprinklers.
SL
From: sprinklerforum-boun...@firesprinkler.org on behalf of mphe...@aerofire.com
Sent: Sat
- Original Message -
From: George Church [mailto:g...@rowesprinkler.com]
Sent: Saturday, September 29, 2012 04:14 PM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
You can lead an AHJ to water but you can't make him think. Or see
, September 29, 2012 04:14 PM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
You can lead an AHJ to water but you can't make him think. Or see what
you think is obvious.
Might want to print out responses from the Forum and show
on behalf of Ron Greenman
Sent: Sat 9/29/2012 7:04 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler head Temperature requirement
Wouldn't it be nice if the reviewers and inspectors were held to the same
standards of education, continuing education, and experience that they hold
...@rowesprinkler.com]
Sent: Saturday, September 29, 2012 04:14 PM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
You can lead an AHJ to water but you can't make him think. Or see what
you think is obvious.
Might want to print out
of uninsured that the rest of
us are subsidizing, methinks.
SML
From: sprinklerforum-boun...@firesprinkler.org on behalf of Ron Greenman
Sent: Sat 9/29/2012 7:04 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler head Temperature requirement
]
Sent: Saturday, September 29, 2012 09:51 PM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler head Temperature requirement
Actually many jurisdictions require CEUs etc. it's whether or not we learn
anything. Having been a code official in NJ for many years
I have a Friday question for the forum, and maybe Roland is able to respond
with some intent perspective. In a 27' high industrial spec building, we
installed sprinkler heads rated at 286 degree. This was permitted, installed,
inspected and approved. The owner now has a tenant lease which will
: Friday, September 28, 2012 10:00 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
I have a Friday question for the forum, and maybe Roland is able to
respond with some intent perspective. In a 27' high industrial spec
building, we installed sprinkler
: Friday, September 28, 2012 10:30 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
Just to clarify - are you lumping me into the set of professionals, or hoping
that I know of one who can speak to this issue?
SL
-Original Message-
From
...@aerofire.com
Sent: Fri 9/28/2012 1:00 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
I have a Friday question for the forum, and maybe Roland is able to respond
with some intent perspective. In a 27' high industrial spec building, we
installed
Leyton
Sent: Friday, September 28, 2012 10:30 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
Just to clarify - are you lumping me into the set of professionals, or
hoping that I know of one who can speak to this issue?
SL
-Original Message
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
mphe...@aerofire.com
Sent: Friday, September 28, 2012 10:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
Let's just say that I value the very broad base of experience you have
amassed in working
He is working from 2002.
- Original Message -
From: Steve Leyton [mailto:st...@protectiondesign.com]
Sent: Friday, September 28, 2012 12:47 PM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement
Snake oil sales talk
Methinks he is picking nits.
On what basis is he requiring intermediate temperature heads? Does he have
evidence that the maximum ceiling temperature exceeds 100 degF? How does he
know it is 150 degF and not 225 degF? (Table 6.2.5.1) It sounds to me like he
is making something up just because
as Todd already said, it is explicitly allowed by 8.3.2.3 unless the
AHJ is trying to call it a light hazard occupancy.
Roland
On Sep 28, 2012, at 10:00 AM, mphe...@aerofire.com mphe...@aerofire.com
wrote:
I have a Friday question for the forum, and maybe Roland is able to
respond with
To: sprinklerforum@firesprinkler.org
Sent: Fri, Sep 28, 2012 22:40:08 GMT+00:00
Subject: Re: Sprinkler head Temperature requirement
as Todd already said, it is explicitly allowed by 8.3.2.3 unless the AHJ is
trying to call it a light hazard occupancy.
Roland
On Sep 28, 2012, at 10:00 AM, mphe