: George Church g...@rowesprinkler.com
Sent: October 25, 2012 10/25/12
To: sprinklerforum@firesprinkler.org
Subject: RE: trip time per nfpa 25
I'd call it a revenue opportunity. Visors would help trip time, but if a water
delivery calc indicated a higher air pressure decreased transit time as well
the clapper shut.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Wednesday, October 24, 2012 11:06 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: trip time per nfpa 25
I don't
holding the clapper shut.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron
Greenman
Sent: Wednesday, October 24, 2012 11:06 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: trip time per nfpa 25
Subject: Re: trip time per nfpa 25
I would check to make sure that the air supply to the DPV is working as it
should. The time to trip should never be that long. Is the by-pass open?
Sounds like the make-up air is supplying to much air. The make up air needs
to be restricted. The supply line
] On Behalf Of Mike Cabral
Sent: Thursday, October 25, 2012 10:40 AM
To: sprinklerforum@firesprinkler.org
Cc: sprinklerforum@firesprinkler.org
Subject: Re: trip time per nfpa 25
I would check to make sure that the air supply to the DPV is working as it
should. The time to trip should never
Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Gregg Key
Sent: Thursday, October 25, 2012 12:15 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: trip time per nfpa 25
Very good feedback. This system was installed in 2006
, October 25, 2012 12:59 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: trip time per nfpa 25
Was it a Victaulic #756 or #768? Look closely at the differential piston if it
is a #756 some time they stick.
Richard L. Mote ET
NICET Cert. No. 067611
Designer
Rowe Sprinkler Systems, Inc.
7993 Route
570.837.6335
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Gregg Key
Sent: Thursday, October 25, 2012 12:15 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: trip time per nfpa 25
Very good
What was the initial design and acceptance trip time ?
John Drucker - Mobile Email
- Original Message -
From: sprinklerforum-boun...@firesprinkler.org
sprinklerforum-boun...@firesprinkler.org
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Sent: Wed Oct 24 13:27:04
I don't believe their is any reference to how long is too long except in
13 (pre 2010) where a system of between 500 750 gallons is required to
have a QOD if the water delivery time to the inspectors test exceeds 60
seconds. I think there is a presumption that a system of less than 500
gallons
, 2012 11:06 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: trip time per nfpa 25
I don't believe their is any reference to how long is too long except in
13 (pre 2010) where a system of between 500 750 gallons is required to have a
QOD if the water delivery time to the inspectors test
From old time experience there may be obstructions at the dry inspector's
test valve or other that is obstructing the flow of air. From insurance
inspector days anything over 3 minutes needs further investigation. I would
have called 15 minutes a failure in the 60's and 70's.
Arthur Tiroly
ATCO
-
From: Art Tiroly atir...@atcofirepro.com
To: sprinklerforum@firesprinkler.org
Sent: Wed, Oct 24, 2012 18:32:16 GMT+00:00
Subject: RE: trip time per nfpa 25
From old time experience there may be obstructions at the dry inspector's
test valve or other that is obstructing the flow of air. From insurance