To restate John's comment a little more bluntly, the requirement to adjust the
K-factor for antifreeze solutions was deleted the following edition because it
created an insignificant difference considering the approximate nature of our
overall methodology and especially the assigned average
@lists.firesprinkler.org
Subject: Re: adjusting the K-Factor with our bare hands
To restate John's comment a little more bluntly, the requirement to adjust the
K-factor for antifreeze solutions was deleted the following edition because it
created an insignificant difference considering the approximate nature of our
: sprinklerforum-boun...@lists.firesprinkler.org [mailto:
sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Wednesday, June 12, 2013 11:03 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: adjusting the K-Factor with our bare hands
To restate John's comment
editions, would be shame.
Thanks to everyone again.
Brad
-Original Message-
From: Ron Greenman [mailto:rongreen...@gmail.com]
Sent: Wednesday, June 12, 2013 12:39 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: adjusting the K-Factor with our bare hands
And the anti-freeze is out
,
A.22.4.4.5.1,
which, if deleted in later editions, would be shame.
Thanks to everyone again.
Brad
-Original Message-
From: Ron Greenman [mailto:rongreen...@gmail.com]
Sent: Wednesday, June 12, 2013 12:39 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: adjusting the K-Factor
a more direct link to it?
-Original Message-
From: IPA [mailto:nsfdc...@gmail.com]
Sent: Wednesday, June 12, 2013 1:32 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: adjusting the K-Factor with our bare hands
Aren't Darcy calcs a bit counterintuitive? We want to make sure
-Original Message-
From: Brad Casterline [mailto:bcasterl...@fsc-inc.com]
Never mind Roland, dumb question, of course you did.
The main reason I wanted to check it out was to see how you adjusted the
K-Factor. Then I saw in 13-2010 the formula for doing this. In my original
post I got
From NFPA 13-2007, 22.4.4.5.1, we are required to, among other things,
adjust the K-Factor.
Using the Hazen-Williams friction formula, 62.4 lb/ft3 / 144 in2 = .433
lb/in2/ft(h).
If we have an AF solution at 65.5 lb/ft3, / 144 = .455 lb/in2/ft(h).
If K=5.6, and we assume P=7 PSI.:
I'd be concerned that you have completely muddled up kfactors for someone who
no longer looks at it as the standard and industry practices do.
But why listen to us warning about sending novices out with the wrong
viewpoint?
Sent from my iPhone
On Jun 11, 2013, at 7:52 AM, Brad Casterline
...@rowesprinkler.com]
Sent: Tuesday, June 11, 2013 12:05 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: adjusting the K-Factor with our bare hands
I'd be concerned that you have completely muddled up kfactors for someone
who no longer looks at it as the standard and industry practices
I would strongly caution against using this method for estimate calculations.
(Without doing extensive testing to verify that it is accurate)
The D-W and H-W calculation methods are simply approximations of how fluids
interact with themselves and the pipe they are in. The H-W equation and the
can I say strongly enough how much I agree with what Matt said? can I say
it again? And third time being the charm, I agree with what Matt said--a
lot--and with George's earlier comments.
On Tue, Jun 11, 2013 at 11:40 AM, Matt Grise m...@afpsprink.com wrote:
I would strongly caution against
[mailto:rongreen...@gmail.com]
Sent: Tuesday, June 11, 2013 2:03 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: adjusting the K-Factor with our bare hands
can I say strongly enough how much I agree with what Matt said? can I say
it again? And third time being the charm, I agree with what Matt
without them?
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad
Casterline
Sent: Tuesday, June 11, 2013 7:52 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: adjusting the K-Factor with our
: Tuesday, June 11, 2013 4:42 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: adjusting the K-Factor with our bare hands
Keep in mind that you started with a nominal K factor of 5.6. Per Table
6.2.3.1 (NFPA 13 - 2007), the range for the K factor under laboratory
testing conditions was 5.3
, June 11, 2013 2:03 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: adjusting the K-Factor with our bare hands
can I say strongly enough how much I agree with what Matt said? can I say
it again? And third time being the charm, I agree with what Matt said--a
lot--and with George's
- adjusting
K-Factors
I mean, from NFPA 13 referenced earlier?
-Original Message-
From: Ron Greenman [mailto:rongreen...@gmail.com]
Sent: Tuesday, June 11, 2013 2:03 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: adjusting the K-Factor with our bare hands
can I say
...@lists.firesprinkler.org on behalf of Ron Greenman
Sent: Tue 6/11/2013 5:53 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: adjusting the K-Factor with our bare hands
I love the 1. Typo. or 2. Auto Correct. or 3. Freudian ? or 4. Slotism.
...and I'm licking myself
You just keep
@lists.firesprinkler.org
Subject: Re: adjusting the K-Factor with our bare hands
I love the 1. Typo. or 2. Auto Correct. or 3. Freudian ? or 4. Slotism.
...and I'm licking myself
You just keep hanging out with the woman and licking yourself. It's not a
pretty picture, but it will be now
19 matches
Mail list logo