RE: calc procedure logic

2013-05-24 Thread Brad Casterline
...epilogue... The next time a similar situation comes up I will weigh Options A B: Option A, step 1- start with a listed head with listed RTI and listed Temp rating. step 2- remove RTI, Temp Rating, chance of accidental fusing, and chance of not fusing when it should. step 3- spend a year and

Re: calc procedure logic

2013-05-24 Thread George Church
Ask them if they flowed it at a specified pressure instead of velocity and you will avoid glazed eyes. Speak their language And no, outside its listing they likely won't stand behind it because there is nothing to stand on. Sent from my iPhone On May 24, 2013, at 8:52 AM, Brad Casterline

Re: calc procedure logic

2013-05-24 Thread MPhelps
and limitations of the deflector. IMHO. Mark at Aero - Original Message - From: Brad Casterline [mailto:bcasterl...@fsc-inc.com] Sent: Friday, May 24, 2013 12:51 PM To: sprinklerforum@lists.firesprinkler.org sprinklerforum@lists.firesprinkler.org Subject: RE: calc procedure logic ...epilogue

RE: calc procedure logic

2013-05-22 Thread Brad Casterline
Thanks Bruce, Ron, Steve, off-Forum dude, everyone else again, and anyone I forgot. Brad -Original Message- From: Ron Greenman [mailto:rongreen...@gmail.com] Sent: Tuesday, May 21, 2013 4:38 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: calc procedure logic It doesn't

Re: calc procedure logic

2013-05-22 Thread John Lewis
@lists.firesprinkler.org; sprinklerforum@lists.firesprinkler.org Sent: Tuesday, May 21, 2013 7:53 PM Subject: RE: calc procedure logic Chris forgot to ask where babies come from.  The answer - as I understand it - to the 52,000 sq. ft. question is ... mildly amusing. SL -Original Message- From

calc procedure logic

2013-05-21 Thread Brad Casterline
Would the 7 psi minimum operating pressure from NFPA 13 Calculation Procedure apply to open head deluge, since the operating parts have already been ejected clear of the frame and deflector by a ball-peen hammer? Brad Casterline, NICET IV Fire Protection Division FSC, Inc. P:

Re: calc procedure logic

2013-05-21 Thread Travis Mack
Doesn't the 7 psi also have to do with minimum pressures to develop spray patterns properly? If so, you would still need the 7 psi minimum. Travis Mack, SET MFP Design, LLC Sent from my iPhone On May 21, 2013, at 6:03 AM, Brad Casterline bcasterl...@fsc-inc.com wrote: Would the 7 psi

RE: calc procedure logic

2013-05-21 Thread Brad Casterline
makes sense, thanks Travis -Original Message- From: Travis Mack [mailto:tm...@mfpdesign.com] Sent: Tuesday, May 21, 2013 8:06 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: calc procedure logic Doesn't the 7 psi also have to do with minimum pressures to develop spray

Re: calc procedure logic

2013-05-21 Thread MPhelps
Subject: calc procedure logic Would the 7 psi minimum operating pressure from NFPA 13 Calculation Procedure apply to open head deluge, since the operating parts have already been ejected clear of the frame and deflector by a ball-peen hammer? Brad Casterline, NICET IV Fire Protection Division

RE: calc procedure logic

2013-05-21 Thread John O'Connor
...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of mphe...@aerofire.com Sent: Tuesday, May 21, 2013 8:31 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: calc procedure logic Wouldn't it depend on the application rate, area of protection and orifice size

RE: calc procedure logic

2013-05-21 Thread Brad Casterline
will not throw 4'-6. Thanks Mark. -Original Message- From: mphe...@aerofire.com [mailto:mphe...@aerofire.com] Sent: Tuesday, May 21, 2013 8:31 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: calc procedure logic Wouldn't it depend on the application rate, area of protection and orifice

Re: calc procedure logic

2013-05-21 Thread George Church
To: sprinklerforum@lists.firesprinkler.org Subject: Re: calc procedure logic Wouldn't it depend on the application rate, area of protection and orifice size? Mark at Aero - Original Message - From: Brad Casterline [mailto:bcasterl...@fsc-inc.com] Sent: Tuesday, May 21, 2013 01:03 PM

RE: calc procedure logic

2013-05-21 Thread Brad Casterline
...@nfspk.com] Sent: Tuesday, May 21, 2013 8:37 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: calc procedure logic The 7.0 PSI end head minimum pressure was never intended to kick out the links, seat etc, but to develop the minimum spray pattern required to deliver the specified density

Re: calc procedure logic

2013-05-21 Thread George Church
To: sprinklerforum@lists.firesprinkler.org Subject: RE: calc procedure logic The 7.0 PSI end head minimum pressure was never intended to kick out the links, seat etc, but to develop the minimum spray pattern required to deliver the specified density. John O'Connor National Fire Sprinklers, Inc

RE: calc procedure logic

2013-05-21 Thread Mark A. Sornsin, P.E.
...@lists.firesprinkler.org] On Behalf Of Brad Casterline Sent: Tuesday, May 21, 2013 8:04 AM To: sprinklerforum@lists.firesprinkler.org Subject: calc procedure logic Would the 7 psi minimum operating pressure from NFPA 13 Calculation Procedure apply to open head deluge, since the operating parts have already been

RE: calc procedure logic

2013-05-21 Thread RFletcher
, May 21, 2013 11:19 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: calc procedure logic My understanding of sprinkler design is that the cap is supposed to be ejected away from the sprinkler regardless of the pressure available. As soon as the element fuses, the cap springs free

RE: calc procedure logic

2013-05-21 Thread Brad Casterline
deluge systems like aircraft hangers. What do you think? Thanks for feedback. -Original Message- From: rfletc...@aerofire.com [mailto:rfletc...@aerofire.com] Sent: Tuesday, May 21, 2013 1:36 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: calc procedure logic During Phoenix summers

Re: calc procedure logic

2013-05-21 Thread bverhei
- From: George Church g...@rowesprinkler.com To: sprinklerforum@lists.firesprinkler.org Sent: Tuesday, May 21, 2013 7:13:22 AM Subject: Re: calc procedure logic Except that you are designing outside the standard. Can't recall ever even thinking of approaching an AHJ with 6 psi instead of 7

RE: calc procedure logic

2013-05-21 Thread RFletcher
...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad Casterline Sent: Tuesday, May 21, 2013 11:43 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: calc procedure logic lol Ron! Mark, I think there are 2 schools of thought about this, but in the case

RE: calc procedure logic

2013-05-21 Thread Cahill, Christopher
Subject: RE: calc procedure logic Thanks John. Assuming that is true, we could say a 1/2 head at 7 psi throws 7'-6 each way. At 7 psi the water hits the deflector going 32.26 ft/sec. v=SQRT(2gh). At 6 psi it would be going 29.87 ft/sec, and would throw 6'-11 each way. -Original Message

Re: calc procedure logic

2013-05-21 Thread George Church
Sent: Tuesday, May 21, 2013 8:54 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: calc procedure logic Thanks John. Assuming that is true, we could say a 1/2 head at 7 psi throws 7'-6 each way. At 7 psi the water hits the deflector going 32.26 ft/sec. v=SQRT(2gh). At 6 psi

RE: calc procedure logic

2013-05-21 Thread Brad Casterline
@lists.firesprinkler.org Subject: RE: calc procedure logic You are confusing velocity with vector. Same head at 50 psi doesn't go much farther. Go grab a head and take a match to it. The link surely clears. The cap if upright stays. If pendant gravity takes care of it. Then you can see how little

Re: calc procedure logic

2013-05-21 Thread Ron Greenman
: Cahill, Christopher [mailto:ccah...@burnsmcd.com] Sent: Tuesday, May 21, 2013 3:28 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: calc procedure logic You are confusing velocity with vector. Same head at 50 psi doesn't go much farther. Go grab a head and take a match

RE: calc procedure logic

2013-05-21 Thread Steve Leyton
@lists.firesprinkler.org Subject: Re: calc procedure logic Add some dried sludge and age 20 years. Mark, did u see the clogged drops on a DIPreAction sys up your way? I realize we need to maintain and cure bad ones with testing, but reality testing should include aging and normal degradation