If it’s containers more than de minimus curbs are poor practice. Going up an
over a 20” dike with forklift is in the real world a classic cause of spills.
Sumps or a tank are much better. Added benefit is for spills generation of
flammable vapors is related to surface area, not volume. Cover a
In theory shut down in WA State unless response oriented construction.
I’ve seen one pickup at 4 over 2 project across from my pharmacy. Security? One
lone superintendent keeping it rain resistant?
Elsewhere around town? I don’t know. One trip each of last two weeks. Did take
a fifteen mile
Hoping someone's brain is working better than mine.
I cannot seem to find the information on sizing a curb for containment of
flammable liquids and sprinkler water, I seem to remember a time frame for the
sprinkler water plus the largest container, but am having no luck locating is
Any help
There have been several project around my area that are scheduling
different contractors for different days.
On Thu, Apr 9, 2020 at 12:10 Matt Grise via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> I think you will need to look at a local level. Our field operations are
> in
IFC Section 5004.2.2.3 (and also similar language in NFPA #30)
Secondary containment for indoor storage areas shall be designed to contain a
spill from the largest vessel plus the design flow volume of fire protection
water calculated to discharge from the fire-extinguishing system over the
When dealing with secondary containment the 20 minutes is just a number. I’ve
told many clients that there’s no guarantee that sprinklers will be shut down
in 20 minutes and the need to think about where overflow will go. Allowing
hazardous materials to leave your property can lead to a ton
Last time I had to do it, I got the info from NFPA 30. It took a while, but it
is in there somewhere.
Matt
From: Sprinklerforum On Behalf
Of James Crawford via Sprinklerforum
Sent: Thursday, April 09, 2020 12:06 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: James Crawford
Subject: Curbs
What is the rule for having more than 10 people working on a job site?
I've seen projects with more than 100 construction workers, is that legal?
Thanks,
Mike
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
Spill control is single largest vessel. Secondary containment is spill control
plus 20 minutes sprinkler flow.
...plus the design flow volume of fire protection water calculated to discharge
from the fire-extinguishing system over the minimum required system design area
or area of the room or
I was just looking at this issue for a turbine floor FP installation: FM data
sheet 7-83 has some guidance on the spill control and drainage sizing for
flammable liquid areas..
David Toshio Williams, PE, FPE
(218) 279-2436 direct | (218) 310-2446 cell
LHB, Inc. | PERFORMANCE DRIVEN DESIGN
Not sure if this is what you are thinking of, but below is from 2012 IBC Group
H-2 Flammable and combustible liquids section...
[F] 415.8.2.4 Leakage containment. A liquid-tight containment area compatible
with the stored liquid shall be provided. The method of spill control, drainage
control
If secondary containment is required (it's based on occupancy classifications
and quantities) the containment is for 20 minutes of sprinkler discharge and
the volume of the largest vessel.
Not every occupancy classification requires containment and volumes under
certain quantities also would