RE: Drum drip (condensate trap) maintenance in dry system

2007-01-29 Thread Brian Harris
Ed, Any idea where that is in NFPA-13 2007 ? It's always been there in 03 but I don't see it in 07. Regards, Brian Harris First Defense Fire Protection Design Engineer [EMAIL PROTECTED] 704.948.3506 phone 704.948.3507 fax ---

RE: TEST

2008-08-27 Thread Brian Harris
Yep, got it. Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of David M. Canham Sent: Wednesday, August 27, 2008 10:02 AM To: sprinklerforum@firesprinkler.org Subject: TEST Just testing since have not seen any activity in a while

Flow Hydrant vs. Test Hydrant

2008-09-23 Thread Brian Harris
O.K., can someone please help a dummy out (that would be me)? When looking at a Civil Site Utility plan what method do you use to determine which hydrant you want to flow and which one you put the gauge on? I've heard a couple different ways, just wanted to get a popular opinion Regards,

RE: Flow Hydrant vs. Test Hydrant

2008-09-23 Thread Brian Harris
I agree with flowing the hydrant closets to the tap, but how do you tell which way is upstream or downstream? This particular site utility drawing limited at best, it shouldn't make that big of a difference should it? Brian Harris FDFP INC. -Original Message- From: [EMAIL PROT

RE: Flow Hydrant vs. Test Hydrant

2008-09-23 Thread Brian Harris
Vince, I know this is a little off topic but "how bout them Buffalo Bills" !!! :) Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Vince Sabolik Sent: Tuesday, September 23, 2008 10:41 AM To: sprinklerforum@firespr

RE: Flow Hydrant vs. Test Hydrant

2008-09-23 Thread Brian Harris
I think you should keep him, it'll give you something to look forward too.... Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Vince Sabolik Sent: Tuesday, September 23, 2008 11:11 AM To: sprinklerforum@firesprinkle

RE: Flow Hydrant vs. Test Hydrant

2008-09-23 Thread Brian Harris
Trevor, Very nice, thanks. Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Trevor Spain Sent: Tuesday, September 23, 2008 1:53 PM To: sprinklerforum@firesprinkler.org Subject: Re: Flow Hydrant vs. Test Hydrant If anyone needs a

Dry Valve Keeps Tripping

2008-09-24 Thread Brian Harris
The valve originally was tripping within a couple of days, then it held for 3-4 months, then it began to trip again, sometimes within 2 hours after setup, the entire valve assembly was replaced, the system held for 3-4 days and now has tripped again. FYI, Victaulic NXT Dry Pipe Valve pre-piped vers

RE: Dry Valve Keeps Tripping

2008-09-24 Thread Brian Harris
customer service? Thanks guys. Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Wednesday, September 24, 2008 10:40 AM To: sprinklerforum@firesprinkler.org Subject: RE: Dry Valve Keeps Tripping This is going to sound li

RE: Dry Valve Keeps Tripping

2008-09-25 Thread Brian Harris
James, The accelerator was tripping so fast that it didn't allow the compressor to kick on, therefore filling the system. Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, September 24, 2008

N-Shape RPZ's

2008-10-07 Thread Brian Harris
I've used Febco model "N" shape RPZ's in the past, what are some other manufacturer's you guys have used and are happy with? I have a job that is on a fast track schedule and unfortunately Febco is unable to deliver in time. Regards, E-mail messa

RE: N-Shape RPZ's

2008-10-07 Thread Brian Harris
Thanks for the help guys. Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Tuesday, October 07, 2008 2:07 PM To: sprinklerforum@firesprinkler.org Subject: RE: N-Shape RPZ's Try the Wilkins 450/475 s

Water Flow Curve

2008-10-15 Thread Brian Harris
Forum, I must be having a brain cramp or something but a little help would be appreciated. I have a flow test that is Static 54, Residual 47 & Flow is 920, I've plotted that out on N1.85 graph. I just ran my preliminary calc's using HydraCAD and get the following result: Flow Required 458 gpm @ 42

RE: Water Flow Curve

2008-10-15 Thread Brian Harris
Yep I get that part, but why do the results say 458 gpm @ 42 psi ? Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tambini, Ed Sent: Wednesday, October 15, 2008 2:06 PM To: sprinklerforum@firesprinkler.org Subject: RE: Water Flow

RE: Water Flow Curve

2008-10-15 Thread Brian Harris
Yep, the brain cramp has eased a bit, "I can see clearly now".. Thanks for the help guys. Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tambini, Ed Sent: Wednesday, October 15, 2008 2:26 PM To: spri

RE: Fire Sprinkler Pipe through Mechanical Duct

2008-10-24 Thread Brian Harris
Me too please, email would be great. Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gregg Fontes Sent: Thursday, October 23, 2008 7:39 PM To: sprinklerforum@firesprinkler.org Subject: RE: Fire Sprinkler Pipe through Mechanical

Extended Coverage / Quick Response

2008-11-10 Thread Brian Harris
Anybody know of a Extended Coverage (16x16) Quick Response pendent & upright head? Regards, E-mail message checked by Spyware Doctor (6.0.0.386) Database version: 5.11090 http://www.pctools.com/en/spyware-doctor-antivirus/

RE: Extended Coverage / Quick Response

2008-11-10 Thread Brian Harris
That's what I was afraid of... Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack, SET Sent: Monday, November 10, 2008 10:42 AM To: sprinklerforum@firesprinkler.org Subject: RE: Extended Coverage / Quick Res

RE: Extended Coverage / Quick Response

2008-11-10 Thread Brian Harris
I'm looking for one that covers 16x16. Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jimmy Waite Sent: Monday, November 10, 2008 10:48 AM To: sprinklerforum@firesprinkler.org Subject: RE: Extended Coverage / Quick Res

RE: Extended Coverage / Quick Response

2008-11-10 Thread Brian Harris
Unfortunately it's O.H, I guess I left that little tid-bit out of my original request, my bad. Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack, SET Sent: Monday, November 10, 2008 11:10 AM To: sprinkler

RE: Extended Coverage / Quick Response

2008-11-10 Thread Brian Harris
I need one in 16x16, am I missing something? Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of G. Tim Stone Sent: Monday, November 10, 2008 10:24 AM To: sprinklerforum@firesprinkler.org Subject: RE: Extended Coverage / Quick

Piping Layout

2008-12-12 Thread Brian Harris
Peoples Quick question for you. It seems that more and more of the buildings we do are odd shaped, funky angles, blah blah blah. After spotting all the heads what is your thought process when it comes to laying out the piping ? Do you layout the Branch Lines first (perp to the steel) or do you

Electrical Rooms

2008-12-16 Thread Brian Harris
I know it's in the code but I can't put my finger on it, what section talks about not running a sprinkler line through an electrical room? While I'm on it what section prohibits running through a stairwell? Thanks, I'm in a time crunch otherwise I wouldn't bother you Regards,

RE: Electrical Rooms

2008-12-16 Thread Brian Harris
So this doesn't prohibit pipe from passing through an electrical room, right? You just need to stay out of the "dedicated" space? Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.or

Flex Heads / Dissimilar Metals

2009-02-12 Thread Brian Harris
I'm working on a job and the Engineer is rejecting our plans because we are using flex heads, he is using a section in the spec for Dielectric Fittings to justify his point. The only thing I can possibly see him trying to get out of it might be something to do with dissimilar materials? Any thought

RE: Flex Heads / Dissimilar Metals

2009-02-12 Thread Brian Harris
There's one in every crowd!. :) Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: Thursday, February 12, 2009 8:58 AM To: sprinkler

Pipe Labeling

2009-03-05 Thread Brian Harris
Forum, I just wanted to double check myself before I put my foot in my mouth, I'm working on a school and the spec says that pipe is to be labeled per NFPA-13 (2002). I don't remember seeing anything in NFPA that talks about labeling pipe, I just did another quick search and didn't come up with any

RE: Pipe Labeling

2009-03-05 Thread Brian Harris
I read that to mean the identification label put on by the manufacturer & not the flashy little flow stickers & such? Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Kra

RE: Pipe Labeling

2009-03-05 Thread Brian Harris
$ = I likey Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Kramer Sent: Thursday, March 05, 2009 1:54 PM To: sprinklerforum@firesprinkler.org Subject: RE: Pipe Labeling

Big Ass Fans

2010-07-26 Thread Brian Harris
Does anybody have any experience using Big Ass Fans and ESFR heads? I have a Fire Marshall questioning the use of the (2) in the same warehouse. Brian Harris Design Engineer First Defense Fire Protection 11957 Ramah Church Road Huntersville NC 28078 br...@firstdefensefire.com

PRV's in Calc's

2010-07-28 Thread Brian Harris
alc's. Is the 165psi from the valve considered the new Static or Residual ? Brian Harris Design Engineer First Defense Fire Protection 11957 Ramah Church Road Huntersville NC 28078 br...@firstdefensefire.com www.firstdefensefire.com Ph: 704.9

NFPA-13 & Wood Joist

2010-07-28 Thread Brian Harris
because I'm working on a Rec. Center and one wing of the building has Glu-Lam beams that are exposed except in a few areas where there is a GWB ceiling. The engineer wants pendent heads in the ceilings and upright heads above but only in the exit corridors, does that make any sense? Brian

Galvanized Pipe

2010-08-02 Thread Brian Harris
only for large drop sprinklers. Where did this "extra" tidbit of information in the handbook come from? Brian Harris Design Engineer First Defense Fire Protection 11957 Ramah Church Road Huntersville NC 28078 br...@firstdefensefire.com www.firstdefensefire.com Ph: 70

RE: Galvanized Pipe

2010-08-03 Thread Brian Harris
I'm such a turd! That's what I get for hurrying Thanks for the heads up. Regards, Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis Mack, SET Sent: Monday, August

ESFR Heads

2010-08-03 Thread Brian Harris
ta sheets support it? Also, If it helps the calc's can you go up a level to the 35ft ceiling row and use those heads? Thanks! Brian Harris Design Engineer First Defense Fire Protection 11957 Ramah Church Road Huntersville NC 28078 br...@firstdefensefire.com www.firs

Online courses

2010-08-03 Thread Brian Harris
Does anybody know of a good site that offers an online class for Fire Pumps? Thanks! Brian Harris Design Engineer First Defense Fire Protection 11957 Ramah Church Road Huntersville NC 28078 br...@firstdefensefire.com www.firstdefensefire.com Ph: 704.948.3506 Fax

FW: ESFR Heads

2010-08-03 Thread Brian Harris
Helloo Regards, Brian Harris FDFP INC. _ From: Brian Harris [mailto:br...@firstdefensefire.com] Sent: Tuesday, August 03, 2010 9:20 AM To: 'sprinklerforum@firesprinkler.org' Subject: ESFR Heads Quick question about ESFR heads, In my particular situation I

RE: ESFR Heads

2010-08-03 Thread Brian Harris
The ceiling height is right at 32', I'm hoping to be able to use the k...@20 since it will keep the pipe sizes down. However the K25 are about 3 times as much as the K16.8 Regards, Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firespr

RE: ESFR Heads

2010-08-03 Thread Brian Harris
Gee thanks Regards, Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cliff Whitfield Sent: Tuesday, August 03, 2010 3:27 PM To: sprinklerforum@firesprinkler.org Subject: RE

RE: Online courses

2010-08-03 Thread Brian Harris
Sounds like a winner, Thanks! Regards, Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom Sent: Tuesday, August 03, 2010 3:39 PM To: sprinklerforum@firesprinkler.org Subject: RE

Area Reduction

2010-08-05 Thread Brian Harris
ood reason) with this in mind I don't need to have a 10% cushion "built" into the calc's correct? Thanks! Brian Harris Design Engineer First Defense Fire Protection 11957 Ramah Church Road Huntersville NC 28078 br...@firstdefensefire.com www.firstdefensefire.

RE: Area Reduction

2010-08-05 Thread Brian Harris
could still use AR. Regards, Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of fpech...@embarqmail.com Sent: Thursday, August 05, 2010 11:52 AM To: sprinklerforum@firesprinkler.org Su

RE: Area Reduction

2010-08-05 Thread Brian Harris
Jamie- It's not the actual DOI spec, he has just brought those couple items into his spec to cover his butt. I have no problem playing by his rules, I just wanted to make sure Area Reduction was still a card I could play. Regards, Brian Harris FDFP INC. -Original Message-

4-WAY BRACES

2010-08-10 Thread Brian Harris
Forum- What is the general consensus about putting 4-way braces on "any" vertical pipe that is over 3 feet long? I was under the impression it was for Risers only, is that not the case? Thanks! Brian Harris Design Engineer First Defense Fire Protection 11957 Ramah C

RE: 4-WAY BRACES

2010-08-10 Thread Brian Harris
When it comes to Seismic (and other topics too) Ken is the man. Regards, Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Charles Thurston Sent: Tuesday, August 10, 2010 1:08 PM

RE: unsubscribe

2010-08-11 Thread Brian Harris
I'm getting in on this one mid-stream but what's this designer membership thing? Regards, Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Richard Lindner Sent: Wednesday,

Seismic Question

2010-08-13 Thread Brian Harris
Is a Surge Restraint (tolco #25) considered and End-Of-Line restraint per 9.3.6.3 (2007) ? Thanks! Brian Harris Design Engineer First Defense Fire Protection 11957 Ramah Church Road Huntersville NC 28078 br...@firstdefensefire.com www.firstdefensefire.com Ph

RE: Seismic Question

2010-08-13 Thread Brian Harris
Is there any difference then between a Branch Line Restraint and an End-Of Line restraint? Regards, Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of steve Sent: Friday, August 13

RE: Seismic Question

2010-08-13 Thread Brian Harris
Ron- We are actually in NC... Regards, Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman Sent: Friday, August 13, 2010 11:25 AM To: sprinklerforum@firesprinkler.org

Insulation R Values

2010-08-23 Thread Brian Harris
hanks! Brian Harris FDFP Inc. ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an

Remote Area

2010-08-24 Thread Brian Harris
? Brian Harris Design Engineer First Defense Fire Protection 11957 Ramah Church Road Huntersville NC 28078 br...@firstdefensefire.com www.firstdefensefire.com Ph: 704.948.3506 Fax: 704.948.3507 ___ Sprinklerforum mailing list

RE: Remote Area

2010-08-24 Thread Brian Harris
Matt- Not unless the doors are open on the lower level Regards, Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matthew J. Willis Sent: Tuesday, August 24, 2010 1:21 PM To

FW: 8K Upright

2010-08-27 Thread Brian Harris
Does anybody know if an ECLH 8k Upright exist? Regards, Brian Harris FDFP INC. ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance

Attic's

2010-08-27 Thread Brian Harris
Luckily I don't do allot of attics but every now and then I get stuck with one. Can someone tell me what the difference is between 8.6.4.1.3.1 & 8.6.4.1.4.2? Is it because of the joist being 3ft. or less on center? Thanks Brian Harris FDFP Inc. <http://www.firstdef

RE: 8K Upright

2010-08-27 Thread Brian Harris
Roland- That would be great if we belonged to the national chapter, unfortunately we only belong to the Carolinas chapter. Thanks anyway Regards, Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun

Job Tracking Software

2010-08-31 Thread Brian Harris
I'm looking to get some type of software that I can track/schedule active jobs, any input? Brian Harris Design Manager First Defense Fire Protection, Inc. 11957 Ramah Church Rd. Huntersville, NC 28078 Phone - 704.948.3506 Fax - 704.948.3507 NICET #128476 br...@firstdefensefir

RE: Job Tracking Software

2010-08-31 Thread Brian Harris
I've seen some programs that create a type of graph, and say for example a job is running late it automatically updates the other projects completion dates to reflect it. Regards, Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkle

ESFR Heads & Skylights

2010-09-08 Thread Brian Harris
n the heads. Any help would be greatly appreciated. Thanks! Brian Harris FDFP Inc. ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assi

Commodity Question

2010-09-09 Thread Brian Harris
I have an ESFR Warehouse that has a 1600 sq.ft. room that is used for charging the forklift batteries, what should this room be designed to? Thanks, Brian Harris First Defense Fire Protection === Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus

RE: Commodity Question

2010-09-09 Thread Brian Harris
Craig- I'm leaning towards Group A Plastics because of the batteries but don't want to overkill it either. Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2

RE: Commodity Question

2010-09-09 Thread Brian Harris
Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris Sent: Thursday, September 09, 2010 9:08 AM To: sprinklerforum@firesprinkler.org Subject: RE: Commodity Question Craig- I'm leaning towards Group

RE: Commodity Question

2010-09-09 Thread Brian Harris
n feeble little mind Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matthew J. Willis Sent: Thursday, September 09, 2010 10:03 AM To: sprinklerforum@firesprinkler.org Subject: RE: Commod

RE: Commodity Question

2010-09-09 Thread Brian Harris
Chris- It's not an issue of getting the system to work; I just wanted to make sure that my line of thinking wasn't way out of wack.... Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On

Obstruction to upright heads

2010-09-13 Thread Brian Harris
a 1" arm-over on a 1" sprig, does it still need to be 16" above the 4" pipe? Brian Harris Design Manager First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 Nicet # 128476 === Email scanned b

RE: Obstruction to upright heads

2010-09-13 Thread Brian Harris
I'm referencing 8.8.5.2.1.6 (2007) Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Sent: Monday, September 13, 2010 11:23 AM To: sprinklerforum@firesprinkler.org Subjec

Antifreeze

2010-09-13 Thread Brian Harris
I've searched through NFPA-13 & the archives and can't find a definitive answer.. Do antifreeze loops require an RPZ on the supply into the building or is this dependant on the AHJ? Brian Harris Design Manager First Defense Fire Protection 11957 Ramah Church Road Huntersv

Pumps & RPZ's

2010-09-13 Thread Brian Harris
Thanks for all the info regarding RPZ's and antifreeze systems. One more question, the requirement of RPZ's on systems with fire pumps, is this from the water authority as well? Brian Harris Design Manager First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28

RE: Pumps & RPZ's

2010-09-14 Thread Brian Harris
Excellent, Thanks! I was able to track down a couple good reports that pointed me to AWWA M14 manual. Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman Sent: Monday

Obstruction to ESFR Heads

2010-09-14 Thread Brian Harris
heads with regard to columns? Thanks! Brian Harris Design Manager First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 Nicet # 128476 === Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0

FW: Obstruction to ESFR Heads

2010-09-14 Thread Brian Harris
Cmon' guys help a brutha out.. Brian Harris FDFP Inc. _ From: Brian Harris [mailto:br...@firstdefensefire.com] Sent: Tuesday, September 14, 2010 9:10 AM To: 'sprinklerforum@firesprinkler.org' Subject: Obstruction to ESFR Heads Looking through the code book

Pipe Schedule Systems

2010-09-16 Thread Brian Harris
I swear I read somewhere that for a pipe schedule system you do not need to add hose allowance, Am I nuts? Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 Nicet # 128476 === Email scanned by PC

RE: Pipe Schedule Systems

2010-09-16 Thread Brian Harris
David- We are doing some minor work to an existing warehouse that was done with the pipe schedule method. Now the AHJ wants us to provide hydraulic calc's to show him if the existing system will work. Brian Harris FDFP Inc. -Original Message- From: sprinklerforum

RE: Pipe Schedule Systems

2010-09-16 Thread Brian Harris
I guess that makes sense.. Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matthew J. Willis Sent: Thursday, September 16, 2010 10:00 AM To: sprinklerforum@firesprinkler.org

Pump Rooms

2010-09-16 Thread Brian Harris
What's the consensus on ventilating pump rooms? 5.12.5 (NFPA 20) Says that provisions for ventilation need to be made, is this for all pump rooms or diesel only? I'm getting conflicting stories from the AHJ & the pump rep. Brian Harris First Defense Fire Protection 11957 Ram

RE: Pump Rooms

2010-09-16 Thread Brian Harris
Matt- The pump room is in the basement of the warehouse. Electric motor driven. Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise Sent: Thursday, September 16, 2010 11:41 AM

RE: Pump Rooms

2010-09-16 Thread Brian Harris
John- You busted yourself before I had the chance. :) Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker Sent: Thursday, September 16, 2010 11:55 AM To: sprinklerforum

Pump Churn

2010-09-17 Thread Brian Harris
NFPA 20 says that pump shutoff (churn) can range from 101% - 140% of the rated head. I use Hydracalc for our hydraulics and I see by default it sets it to 110%, where does 110% come from? Is that pretty much the industry standard for safety or is there more to it? Brian Harris First Defense

Pump Test Question

2010-09-22 Thread Brian Harris
the "gpm column" or is this the amount of psi left on the suction side (city side)? Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 Nicet # 128476 === Email scanned by PC Tools - No

RE: Pump Test Question

2010-09-22 Thread Brian Harris
I agree, the confusion started when the manufacturer's tech rep said that the value was what was required at the suction side, not what was left on the city side. Just got a phone call from a fellow forumite and got it straightened out. Thanks! Brian Harris FDFP Inc. -Original Me

Control Mode vs. ESFR

2010-09-23 Thread Brian Harris
product data sheets and right away you can see the end head pressure is quite a bit lower than the ESFR. Are the obstruction rules the same? Etc... Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.

RE: Control Mode vs. ESFR

2010-09-23 Thread Brian Harris
o think those of us with less years under our belt could rely on the forum to help a brother out. Please forgive me if I've taken your post out of context, maybe the deadlines are starting to get to me.. Brian Harris FDFP Inc. -Original Message- From: sprinklerforu

RE: Control Mode vs. ESFR

2010-09-24 Thread Brian Harris
George- No apology necessary, I appreciate all the help from the forum. Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church Sent: Thursday, September 23, 2010 6:02 PM To

Sprinklers under a pitched roof

2010-09-30 Thread Brian Harris
more than 3ft. on center? Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 Nicet # 128476 === Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spywar

Pump & Calc's

2010-10-04 Thread Brian Harris
et through to him, any help would be greatly appreciated. Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 Nicet # 128476 === Email scanned by PC Tools - No viruses or spyware found. (Email Guard

Hose Demand

2010-10-05 Thread Brian Harris
If I have a system with a pump that is fed from a private fire main as described in 3.8.1.11 (2007) am I allowed to exclude the hose stream from the calculations per 12.8.2? Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax

RE: Hose Demand

2010-10-05 Thread Brian Harris
Matt- On this particular project the calculations will not work with the existing pump if hose stream is figured in, without the hose stream the system will work. Can 12.8.2 be applied? Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Hose Demand

2010-10-05 Thread Brian Harris
It's a private water main that is ultimately fed from a public utility source. If I'm reading 3.8.1.11 correctly 12.8.2 should apply? Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On

RE: Hose Demand

2010-10-05 Thread Brian Harris
Matt- I don't understand why you would not have to take hose demand into consideration when sizing a pump but that exclusion would not apply to an existing one. Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum

RE: Hose Demand

2010-10-05 Thread Brian Harris
This is an addition to an existing building so I can tie the inside hose valves to the existing system side and not have them in the calc's for the new side. I was hoping that I could eliminate the 250 outside hose. Brian Harris FDFP Inc. -Original Message- From: sprinklerforum

RE: Hose Demand

2010-10-05 Thread Brian Harris
Jeff- I guess it was just wishful thinking, that's why I was looking for others opinions. Thanks for the help. Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jeff Hewitt

HydraCalc

2010-10-06 Thread Brian Harris
Quick Hydracalc question: Any idea why I'm getting 52 gpm required for an 8k head? (130 sq.ft. @ .20) Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 Nicet # 128476 === Email scanned by PC

RE: HydraCalc

2010-10-06 Thread Brian Harris
The calc's say that's the "Actual Flow" Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis Mack, SET Sent: Wednesday, October 06, 2010 3:15 P

RE: HydraCalc

2010-10-06 Thread Brian Harris
K = 13.411 Qt = 52.00Pt = 15.04 Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On

RE: HydraCalc

2010-10-06 Thread Brian Harris
Dinga Dinga Dinga... We have a winner folks! Brad you are the man! Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Sent: Wednesday, October 06, 2010 3:39 PM To: sprinklerforum

ESFR & Hose Allowance

2010-10-06 Thread Brian Harris
Any thoughts as to why ESFR heads seem to be the only one that doesn't say "combined inside and outside hose allowance"? Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 Nicet # 128476

RE: ESFR & Hose Allowance

2010-10-06 Thread Brian Harris
lc's (assuming inside hose stations are added) since theoretically the fire should be out before the fire department shows up? Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of

RE: ESFR & Hose Allowance

2010-10-07 Thread Brian Harris
Roland- My point about the ESFR heads having more hose allowance was because with ESFR heads it's 250 outside + inside where most other heads it's a combined inside/outside. Brian Harris FDFP Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:spri

Dry Sidewall

2010-10-12 Thread Brian Harris
Does anyone know of an ECOH Dry Sidewall that can be installed 12"-18" below deck? Thanks! Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 Nicet # 128476 === Email scanned by PC

1-1/2" & 2-1/2" Hose Connections

2010-10-19 Thread Brian Harris
Can someone confirm for me that the hose connections talked about in 8.17.5.1.3 are the Small (1-1/2") type only? If so what are acceptable supply points for 2-1/2" hose connections? Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28

Remote Area

2010-10-22 Thread Brian Harris
obby, the Lobby itself is 1200 sq.ft. Can I do a calc on just the Lobby or do I need to pick up an additional 300 sq.ft. from the first floor? I was always taught you could just calc that entire area but now I'm starting to wonder. Brian Harris First Defense Fire Protection 119