Jeff-
I guess it was just wishful thinking, that's why I was looking for others
opinions. Thanks for the help.

Brian Harris
FDFP Inc.
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jeff Hewitt
Sent: Tuesday, October 05, 2010 5:03 PM
To: [email protected]
Subject: RE: Hose Demand

I don't see where you get relief from the hose allowance.  It's all from a
city source so it has to be accounted for, somewhere.  You can only squeeze
out so much, and if it is not there, it's not there.  Not including it means
not accounting for it, which is not correct in my opinion.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Tuesday, October 05, 2010 3:09 PM
To: [email protected]
Subject: RE: Hose Demand

This is an addition to an existing building so I can tie the inside hose
valves to the existing system side and not have them in the calc's for the
new side. I was hoping that I could eliminate the 250 outside hose.

Brian Harris
FDFP Inc.
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Tuesday, October 05, 2010 4:02 PM
To: [email protected]
Subject: RE: Hose Demand

Is there any place on the system to take a hose demand?


At 03:54 PM 10/5/2010, you wrote:
>Is it actually a private separate water supply, or just a private water
main
>that is ultimately fed from a public utility source?
>
>Jeff Hewitt, PE, SET, SFPE (Professional Member)
>Corporate Engineer
>Bi-State Fire Protection Corporation
>
>241 Hughes Lane
>St. Charles, MO  63301
>636-946-0011
>636-946-5172 (fax)
>314-574-6989 (cell)
>
>Fire Sprinklers Save lives.
>Can You Live Without Them?
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Brian Harris
>Sent: Tuesday, October 05, 2010 2:35 PM
>To: [email protected]
>Subject: Hose Demand
>
>If I have a system with a pump that is fed from a private fire main as
>described in 3.8.1.11 (2007) am I allowed to exclude the hose stream from
>the calculations per 12.8.2?
>
>
>
>Brian Harris
>
>First Defense Fire Protection
>
>11957 Ramah Church Road
>
>Huntersville, NC 28078
>
>Phone: 704.948.3506
>
>Fax: 704.948.3507
>
>Nicet # 128476
>
>
>
>
>
>
>
>=======
>Email scanned by PC Tools - No viruses or spyware found.
>(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16010)
>http://www.pctools.com/
>=======
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16010)
http://www.pctools.com/
=======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16010)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16010)
http://www.pctools.com/
=======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16010)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to