RE: [EXTERNAL] RE: Sprinklers next to Diffusers

2018-11-09 Thread Kyle . Montgomery
:51 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: [EXTERNAL] RE: Sprinklers next to Diffusers I have had an architect and ahjs ask for intermediate temp head throughout so there wouldn’t be two different color bulbs On Fri, Nov 9, 2018 at 08:43 Kyle.Montgomery mailto:kmontgom

RE: [EXTERNAL] RE: Sprinklers next to Diffusers

2018-11-09 Thread Matt Grise
. Matt From: Sprinklerforum On Behalf Of Shawn Foor Sent: Friday, November 09, 2018 8:51 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: [EXTERNAL] RE: Sprinklers next to Diffusers I have had an architect and ahjs ask for intermediate temp head throughout so there wouldn’t be two

Re: [EXTERNAL] RE: Sprinklers next to Diffusers

2018-11-09 Thread Shawn Foor
um [mailto: > sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *BJ Newlin > *Sent:* Friday, November 9, 2018 6:44 AM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* [EXTERNAL] RE: Sprinklers next to Diffusers > > > > Are you allowed to use i

RE: [EXTERNAL] RE: Sprinklers next to Diffusers

2018-11-09 Thread Kyle . Montgomery
] On Behalf Of BJ Newlin Sent: Friday, November 9, 2018 6:44 AM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] RE: Sprinklers next to Diffusers Are you allowed to use intermediate sprinklers everywhere? In 13 Section 8.3.2.1 seems to interchange the use of intermediate and ordinary

RE: Sprinklers next to Diffusers

2018-11-09 Thread BJ Newlin
. “--Benjamin Franklin From: Sprinklerforum On Behalf Of ron fletcher Sent: Thursday, November 8, 2018 2:56 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Sprinklers next to Diffusers Why not use intermediate temp heads everywhere? Then diffuser proximity won't matter. Ron F

Re: Sprinklers next to Diffusers

2018-11-08 Thread Steve Leyton
corruptions.) Original message From: "Kyle.Montgomery" Date: 11/8/18 10:57 PM (GMT+03:00) To: sprinklerforum@lists.firesprinkler.org Subject: RE: Sprinklers next to Diffusers What Steve said. Generally, my experience has been that if they have a heat pump, max outlet t

RE: Sprinklers next to Diffusers

2018-11-08 Thread Jerry Van Kolken
Of ron fletcher Sent: Thursday, November 08, 2018 1:56 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Sprinklers next to Diffusers Why not use intermediate temp heads everywhere? Then diffuser proximity won't matter. Ron F On Thu, Nov 8, 2018, 1:57 PM Kyle.Montgomery wrote

Re: Sprinklers next to Diffusers

2018-11-08 Thread ron fletcher
g] *On Behalf Of *Steve > Leyton > *Sent:* Thursday, November 8, 2018 12:20 PM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* [EXTERNAL] Re: Sprinklers next to Diffusers > > > > Higher than the ambient temp rating of the subject sprinkler. > > > &g

RE: Sprinklers next to Diffusers

2018-11-08 Thread Kyle . Montgomery
: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve Leyton Sent: Thursday, November 8, 2018 12:20 PM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] Re: Sprinklers next to Diffusers Higher than the ambient temp rating of the subject sprinkler

Re: Sprinklers next to Diffusers

2018-11-08 Thread Steve Leyton
Higher than the ambient temp rating of the subject sprinkler. Steve Leyton (Sent from my phone; please excuse typos and voice text corruptions.) Original message From: Jerry Van Kolken Date: 11/8/18 8:47 PM (GMT+03:00) To: sprinklerforum@lists.firesprinkler.org Subject:

RE: Sprinklers next to Diffusers

2018-11-08 Thread MFP Design, LLC
Ask the mechanical engineer that did the HVAC plans. 8.3.2.5(9) may eliminate the issue. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com