We have run into the problem of ESFR's in production areas many times but mostly due to the obstruction rules. I haven't had an AHJ try to apply area/density criteria to ESFR's.
Offer to calc a full RA at "X" density to prove the system exceeds that prescribed for the hazard. There is no precedence for treating ESFR's as area/density but if the AHJ wants a full size remote "area" then they should be willing to allow a "density" calc in lieu of the ESFR discharge criteria. (In for a penny in for a pound.) The Tyco guys once asked me if I had any ideas for new products. I suggested they cross list ESFR's for area/density. They looked at me like I had two heads so I wouldn't look for any changes from the OEM. Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Powell Sent: Monday, December 18, 2006 3:25 PM To: [email protected] Subject: ESFR in production areas We have an issue with ESFR in a rack storage area interspersed with componant assembly. The assembly process does not involve flamable liquids or hydraulic equipment. There are no shielded hazards and the storage complies with the ESFR listing. Our AHJ requires that the limited assembly/process hazard be listed for QR sprinklers, which it is, and the number of ESFR sprinklers calculated for the usual OH area of operation discharging at the listed pressure for the storage and building height involved. Seems excessive to me. Have the forum members had any similar ruling? John Powell - New Zealand _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
