The branch lines are 10' apart and the head spacing on each line is 8.5'.



From: "Ed Kramer" <[EMAIL PROTECTED]>
Reply-To: [email protected]
To: <[email protected]>
Subject: RE: ESFR On Line Spacing Less Then 8' Options??
Date: Sat, 13 Jan 2007 11:18:44 -0700

Tom - you didn't indicate the ESFR spacing along the branchline or the
spacing of the branchlines.  If the spacing along the branchlines are
greater than 8', maybe an additional row or 2 of sprinklers can be moved
and maintain the 8' minimum.

Ed Kramer
Littleton, CO


>I have a client with ESFR system obstructions and I am looking for
>options.
>
>Here is what I have, the heads are K17 pendent with 23 lines running East
>to
>West. One head on each line is obstructed in the same location by being
>too
>close to bar joist. If we move the head so it is 12" from the obstruction
>it will be 7'6" away from the adjacent sprinkler, less then the 8'
>required
>by NFPA and FM 2-2. I can not use an upright K 17 because I have exposed
>non-expanded plastics.
>
>Only option I can think of is to install a baffle on the 23 heads to
>prevent
>the water from one ESFR hitting the other. Any idea how large this baffle
>should be? I am thinking 2' wide by 2' deep with the ESFR head centered.
>The
>heads are 10-14" below the desk.
>
>Suggestions comments?
>
>Thanks
>
>Tom LaCorte
>Chubb Insurance Co


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_________________________________________________________________
Get FREE Web site and company branded e-mail from Microsoft Office Live http://clk.atdmt.com/MRT/go/mcrssaub0050001411mrt/direct/01/

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to