Dewayne,

So do you have a foam system or not? If you do then curbs without drainage is OK If you have a water only system then u will need drainage with the curbs.

Review figure 6.8.5 on page 57 of NFPA 30, 2003 edition, it will indicate IF you need to provide spill containment OR liquid spread control. Curbs are used if you have a closed head foam system to control the spread of the product mixed with the water (section 6.4.2.5). If you have a water only sprinkler system and you have a Class I-IIIA liquid then, you need to provide liquid spread control as per 6.8.5.1.


Take a look at FM data sheet 7-29 it has more up to date sprinkler protection requirements then NFPA 30/ 2003 edition.

Regards

Tom

Chubb Insurance

From: "Dewayne Martinez" <[EMAIL PROTECTED]>
Reply-To: [email protected]
To: "SprinklerFORUM" <[email protected]>
Subject: NFPA 30 (03ed) - curbs
Date: Mon, 15 Jan 2007 10:51:03 -0600

Section 6.4.2.5 deals with curbs, scuppers, special drains, ect....and
states that "If a drainage system is used, it shall have sufficient
capacity to carry the expected discharge of water from the fire
protection systems and hose streams."
If there is only curbs does this apply since there is technically no
drains?  If so, what is the proper way to determine the expected
discharge?
Thanks,
Dewayne

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_________________________________________________________________
Type your favorite song.  Get a customized station.  Try MSN Radio powered by Pandora. http://radio.msn.com/?icid=T002MSN03A07001

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to