Greg, I have calc'd numerous test headers at distances from 16ft to more than 100' from the fire pump discharge. I have never had an instance where the calc's did not work with.
I am sure there must be a situation that has concerned the NFPA committees enough to include the requirement, but I do not know what it is. Thanks, Ray Vance Chief Engineering Tech Wayne Automatic Fire Sprinklers, Inc. www.waynefire.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Friday, March 02, 2007 2:54 PM To: [email protected] Subject: fire pump test header size Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 This is from the 2007 edition of NFPA #20. 5.19.3.4 Pipe Size. The pipe size shall be in accordance with one of the following two methods: (1) Where the pipe between the hose valve header and connection to the pump discharge pipe is over 15 ft (4.5 m) in length, the next larger pipe size than required by 5.19.3.1.3 shall be used. (2)* This pipe is permitted to be sized by hydraulic calculations based on a total flow of 150 percent of rated pump capacity, including the following: (a) This calculation shall include friction loss for the total length of pipe plus equivalent lengths of fittings, control valve, and hose valves, plus elevation loss, from the pump discharge flange to the hose valve outlets. (b) The installation shall be proven by a test flowing the maximum water available. I just calculated a test header located approx. 65' from a 750 gpm pump and it seems to work easily with 6" pipe flowing 1,125 gpm in lieu of increasing the pipe to 8". Has anyone got experience using this method? Space is the issue and 6" works much better then 8" in this situation. Thanks, Greg McGahan _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum