Nope.  These are not bushings for sprinklers connected directly to
branch lines for future accommodation of a suspended ceiling, and
standard fittings of the required size were available, so neither of the
exceptions applies. 

These are bushings that were installed by the contractor for simplicity
in construction, not because they met any of the design criteria.    

Paul J. Pinigis, P.E.
Chief Life Safety Engineer


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Posey,
Mike
Sent: Monday, March 12, 2007 2:24 PM
To: [email protected]
Subject: RE: Equivalent length of bushings

NFPA 13, 2002 edition......
6.4.6.2 Hexagonal or face bushings shall be permitted....
6.4.6.3. Hexagonal bushings as permitted.......
USE OF BUSHINGS IS ALLOWED


  Mike Posey
    Direct:   972-587-5232
    [EMAIL PROTECTED]

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Monday, March 12, 2007 1:03 PM
To: [email protected]
Subject: Equivalent length of bushings

Does anyone out there know where I can find the equivalent length of
various bushings that were installed in a system.  I know that NFPA 13
does not permit the use of bushings, and that they do not require
additional equivalent length to be added to the calculations for the
bushings, but I would like to include them in our calculation for
peace-of-mind.  

 

Paul Pinigis

Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
v: (804) 285.4171 f: (804) 217.8520
http://www.haengineers.com 

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to