Well yes, in the Dallas area
Mike Posey
Direct: 972-587-5232
[EMAIL PROTECTED]
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Monday, March 12, 2007 1:39 PM
To: sprinklerforum
Subject: Re: Equivalent length of bushings
I used to know a Mike Posey in the Ft Worth area. Same one?
Rahe loftin
Rahe Loftin
----- Original Message -----
From: "Posey, Mike" [EMAIL PROTECTED]
Sent: 03/12/2007 01:23 PM
To: [email protected]
Subject: RE: Equivalent length of bushings
NFPA 13, 2002 edition......
6.4.6.2 Hexagonal or face bushings shall be permitted....
6.4.6.3. Hexagonal bushings as permitted.......
USE OF BUSHINGS IS ALLOWED
Mike Posey
Direct: 972-587-5232
[EMAIL PROTECTED]
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Monday, March 12, 2007 1:03 PM
To: [email protected]
Subject: Equivalent length of bushings
Does anyone out there know where I can find the equivalent length of
various bushings that were installed in a system. I know that NFPA 13
does not permit the use of bushings, and that they do not require
additional equivalent length to be added to the calculations for the
bushings, but I would like to include them in our calculation for
peace-of-mind.
Paul Pinigis
Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
v: (804) 285.4171 f: (804) 217.8520
http://www.haengineers.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum