WHOA-
I don't think there's a prohibition on them, but 
"readily obtainable" 
"manufactured with long lead time"
"not on the truck at the site when we needed it" 
Are examples of how different people interpret "available" without getting
in to semantics.

While I'm not an engineer (or even a designer or a Mote) I'd think that the
loss thru a bushing would vary with the configuration in which it was
installed. Doubt you'll find any empirical data to support anything, why not
just use the loss for a reducing fitting and use the loss thru the smallest
diameter ? If its for peace of mind, the level of accuracy should be
sufficient that it either does or doesn't work within a relevant range.
Hopefully they left a 40 PSI cushion that only reduces to 39.9 psi ad you
can sleep well.  How's that for optimistic?

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis
Sent: Monday, March 12, 2007 2:03 PM
To: [email protected]
Subject: Equivalent length of bushings

Does anyone out there know where I can find the equivalent length of
various bushings that were installed in a system.  I know that NFPA 13
does not permit the use of bushings, and that they do not require
additional equivalent length to be added to the calculations for the
bushings, but I would like to include them in our calculation for
peace-of-mind.  

 

Paul Pinigis

Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
v: (804) 285.4171 f: (804) 217.8520 
http://www.haengineers.com 

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to