A local AHJ is requiring a sprinkler head under a diesel fuel tank in
fully sprinklered fire pump room. 

>From the AHJ - "IFC 3404.2.7.7 Design of supports requires compliance
with NFPA #30.
NFPA 30-2003, 4.3.1.3: requires that steel support structures for tanks
storing Class I, Class II, or Class III liquids be protected by
materials having a fire resistance rating of not less than 2-hours." The
intent of IFC 3404.2.7.7 is to require protection of the tank supports
regardless of capacity.

NFPA #30, 4.1.1 This chapter shall apply to the following:
4.1.1(2) "The storage of flammable and combustible liquids in portable
tanks and bulk containers whose capacity exceeds 3000 L (793 gal)..."

AHJ contends that 4.1.1 and 4..1.(2) are not applicable because the IFC
is referencing the tank supports and does not specify a minimum size.

Has any one else run into the requirement for a sprinkler under the fuel
tank in a fully sprinklered pump room and what did you fight or comply.
Does anyone know of interpretations or commentary regarding tank
supports.

Ron Fletcher
Aero Automatic
Phoenix, AZ 