Thanks Jeff -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jeff Hewitt Sent: Friday, March 30, 2007 11:49 AM To: [email protected] Subject: Re: ESFR sprinklers and moving a single branch line
Dewayne, Yes, you are interpreting correctly. One or the other, but not both. Jeff Hewitt, PE, SET, SFPE (Prof. Member) Corporate Engineer Bi-State Fire Protection Corporation 636-946-0011 636-946-5172 (FAX) This e-mail and any attachments are CONFIDENTIAL and may be protected by one or more legal privileges. It is intended solely for the use of the addressee identified above. If you are not the intended recipient, any use, disclosure, copying or distribution of this e-mail is unauthorized. If you received this e-mail in error, please notify the sender immediately at the above captioned address. ----- Original Message ----- From: "Dewayne Martinez" <[EMAIL PROTECTED]> To: "SprinklerFORUM" <[email protected]> Sent: Friday, March 30, 2007 11:41 AM Subject: ESFR sprinklers and moving a single branch line NFPA 13 (07ed) Sections 8.12.2.2.4 (3) 8.12.3.1 (4c) Am I interpreting these two sections correct to mean that if you have already moved sprinklers along a branch line and have exceeded the maximum allowable spacing then you are not allowed to move the branch line itself. Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)