Yes the HADs are for the Automatic Sprinkler Deluge valves that use HADs in series, a bank of mercury check valves and a diaphragm for the initiation of the deluge valve. The 'alarm' interpretation is a bellows on the air circuit which sends an alarm signal to the fire detection system. I am interpreting the HADs as initiation devices however some here disagree.
Kevin -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ford, Charles Sent: Thursday, March 29, 2007 4:26 PM To: [email protected] Subject: RE: heat activated devices for a deluge system. Pneumatic rate-of-rise detection has been in use as fire alarm since long before there was electric detection. HAD is a spot type of pneumatic rate-of-rise detection (versus linear type). It was the primary method of releasing early CO2 systems, I have seen it in water curtain applications in older shopping malls . They are surprisingly sensitive to temperature change. Rugged, reliable with no power requirements but NOT SUPERVISED. I would follow NFPA 72 testing schedules. They can be successfully proof tested with hot water, but a manometer is required to accurately test sensitivity. Automatic Sprinkler CO of America is the last manufacturer of manometers for this purpose that I'm aware of. Burton Ford SET, CFPS Member AFAA [EMAIL PROTECTED] 267-487-1000 Fax 267-487-1010 This e-mail transmission contains information that is intended to be confidential and privileged. If you receive this e-mail and you are not a named addressee you are hereby notified that you are not authorized to read, print, retain, copy or disseminate this communication without the consent of the sender and that doing so is prohibited and may be unlawful. Please reply to the message immediately by informing the sender that the message was misdirected. After replying, please delete and otherwise erase it and any attachments from your computer system. Your assistance in correcting this error is appreciated. Thank you. Cintas Corporation -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of MOWLE Kevin(K) - BRUCE POWER Sent: Thursday, March 29, 2007 2:29 PM To: [email protected] Subject: heat activated devices for a deluge system. Are heat actuated devices (HADS) used to initiate a deluge system via a pneumatic signal considered: 1- a heat detector and so the required testing is per NFPA 72 ? 2- or are the HADS considered part of the deluge system so testing requirements as per NFPA 25 ? Thanks Kevin Mowle Bruce Power Tiverton, ON guess ************************************************************************ ************************** *** The contents of this email and any attachments *** are confidential and may be privileged. *** They are intended for the named recipient(s) only. *** If this message has been delivered to you in error, please reply to the *** sender to that effect, don't forward the message to anyone *** and delete the message from your computer. *** Thanks for your help, and sorry for the inconvenience. ************************************************************************ ************************** _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) This e-mail transmission contains information that is intended to be confidential and privileged. If you receive this e-mail and you are not a named addressee you are hereby notified that you are not authorized to read, print, retain, copy or disseminate this communication without the consent of the sender and that doing so is prohibited and may be unlawful. Please reply to the message immediately by informing the sender that the message was misdirected. After replying, please delete and otherwise erase it and any attachments from your computer system. Your assistance in correcting this error is appreciated. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) ************************************************************************************************** *** The contents of this email and any attachments *** are confidential and may be privileged. *** They are intended for the named recipient(s) only. *** If this message has been delivered to you in error, please reply to the *** sender to that effect, dont forward the message to anyone *** and delete the message from your computer. *** Thanks for your help, and sorry for the inconvenience. ************************************************************************************************** _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)