We did this for a project in Mexico based on the owner's Fire and Safety Rep. Directive. He was afraid that if one run-in was damaged they would have no FP for that zone. That was his only reasoning.
If someone hits one with a backhoe and they're side by side, chances are they'll hit both. So no real value there. Sometimes a secondary feed to a manifold serving several areas has been recommended by an Underwriter but the secondary feed was from another direction to minimize potential disruption due to an impairment and the manifold served up to 5 systems. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Davis, Adam Sent: Wednesday, April 11, 2007 3:58 PM To: [email protected] Subject: Duplicate run-in I have a client that wants a duplicate run-in. What I mean is two parallel run-ins, each with a PIV going to serve the same sprinkler riser. I have never done this before and I know FM (insured) and NFPA do not advocate this kind of arrangement. Has this ever been done before and if so why? I am trying to respond that I don't think it is a worth while investment to "ensure" continuous water supply. Thank you, Adam Davis Mechanical Engineer ========================================================= NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer. ========================================================= _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)