If there are separate feeds from two different municipal service zones that are sufficiently remote and permit concurrent maintainability of the underground supply, there may be a benefit to this. We have been working at a large campus that includes two data centers, each with redundant feeds. Obviously a very high value asset. This is an FM insured facility, but this may not necessarily have been their recommendation when the buildings were constructed (circa 1990).
The secondary feed could be from a separate municipal zones, from a campus tank/pump, or from an elevated tank. The intent is to eliminate single points of failure the originate outside the facility. I think you need to know more about what is upstream of the facility before you can draw a conclusion. Ray Schmid -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Davis, Adam Sent: Wednesday, April 11, 2007 3:58 PM To: [EMAIL PROTECTED] Subject: Duplicate run-in I have a client that wants a duplicate run-in. What I mean is two parallel run-ins, each with a PIV going to serve the same sprinkler riser. I have never done this before and I know FM (insured) and NFPA do not advocate this kind of arrangement. Has this ever been done before and if so why? I am trying to respond that I don't think it is a worth while investment to "ensure" continuous water supply. Thank you, Adam Davis Mechanical Engineer ========================================================= NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer. ========================================================= _______________________________________________ Sprinklerforum mailing list [EMAIL PROTECTED] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [EMAIL PROTECTED] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)