Ray, This is a loop around a campus of buildings. The loop is fed from public water in two places. The duplicate run-in is only being considered for one of the four buildings on the campus. The client Rep. that proposed the duplicated run-in is responsible only for that one structure, and this building is not the high rise of the bunch either from a loss/risk perspective.
I agree the concept has a value but in this particular case it is hard to justify based on the factors involved. As far as redundancy because of the facility nature it is hard to justify the duplicate run-in because the client does not want to incur the additional cost of a tank and pump, but rely solely on the public water flow/pressure that is available. What I am leading towards is that the client does not see this site as a highly protected risk or they would want more than they are currently asking for. The duplicate run-in does not have any true benefit since the plan shows them side-by-side. Adam Davis Mechanical Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ray Schmid Sent: Thursday, April 12, 2007 7:43 AM To: [EMAIL PROTECTED] Subject: RE: Duplicate run-in If there are separate feeds from two different municipal service zones that are sufficiently remote and permit concurrent maintainability of the underground supply, there may be a benefit to this. We have been working at a large campus that includes two data centers, each with redundant feeds. Obviously a very high value asset. This is an FM insured facility, but this may not necessarily have been their recommendation when the buildings were constructed (circa 1990). The secondary feed could be from a separate municipal zones, from a campus tank/pump, or from an elevated tank. The intent is to eliminate single points of failure the originate outside the facility. I think you need to know more about what is upstream of the facility before you can draw a conclusion. Ray Schmid -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Davis, Adam Sent: Wednesday, April 11, 2007 3:58 PM To: [EMAIL PROTECTED] Subject: Duplicate run-in I have a client that wants a duplicate run-in. What I mean is two parallel run-ins, each with a PIV going to serve the same sprinkler riser. I have never done this before and I know FM (insured) and NFPA do not advocate this kind of arrangement. Has this ever been done before and if so why? I am trying to respond that I don't think it is a worth while investment to "ensure" continuous water supply. Thank you, Adam Davis Mechanical Engineer ========================================================= NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer. ========================================================= _______________________________________________ Sprinklerforum mailing list [EMAIL PROTECTED] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [EMAIL PROTECTED] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) ========================================================= NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer. ========================================================= _______________________________________________ Sprinklerforum mailing list [EMAIL PROTECTED] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)