Actually there is no gray area that needs discussion.
The Fed. "Safe Drinking Water Act - 1986 Title XIV
Backflow prevention is required for all non-potable water connections to potable water supplies. Yes a wet sprinkler system is a non-potable water connection. (A low hazard one and therefore able to be protected with a double check assembly.) An antifreeze system or any system which has additative's present (Yes that includes MIC treatment) is a high hazard system and requires a reduced pressure zone type backflow preventor.

In addition to the SDWA-1986 OSHA is also in on backflow requirements for any workplace, with the Standards (29 CFR 1910) Subpart J 1910.141 a) and b).

Then there are the additional requirements from individual states, which each of you should become familiar with in those states where you install systems. And finally the purveyor may have additional regulations for discharge of non-potable and waste water, as well as backflow requirements that exceed the fed. or state requirements. Just be aware, that if a purveyor doesn't have a backflow prevention program in place that does not mean you don't need to do it, it just means that you'll share the liability if there is ever a problem.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, April 20, 2007 5:34 PM
Subject: Re: Sprinkler Drainage



This issue was discussed briefly at the recent meeting of the NFSA
Contractors Board.
I have heard about the issue of treating sprinkler water as a contaminant in
Southern California.
I read the article you linked to, and don't think the author has a clear
understanding of the annual tests we perform on sprinkler systems. For example,
he writes that Main Drain Test's are rarely conducted. In reality, they're
probably the most important part of an annual inspection.

One issue to consider: If the system contains additives (ie anti-freeze),
then there may be cause for concern.
What does the local water purveyor say? If he allows sprinkler systems to be connected without backflow devices (ie Detector Check Assembly), then he says
the system is good enough to mix with his Water Supply.

If he requires a Double Check Backflow, then he say's it's a "low Hazard."
(ie, it may smell bad, taste funny , etc)

If he requires an RPZ Backflow, then he considers it high hazard
contaminant. (These areas may be the ones that want sprinkler water discharged into
sewers).

I think the NFSA, AFSA and AWWA should jointly study this issue and write a
paper to guide municipalities on this matter. Perhaps they have?

Forest Wilson
Cherokee Fire Protection Co.
Dayton OH 45434








In a message dated 4/17/2007 6:24:26 P.M. Eastern Daylight Time,
[EMAIL PROTECTED] writes:

---  David Autry <[EMAIL PROTECTED]> wrote:

This article has  come to my attention. I'm just
wondering if anyone else has
 seen this. Anyone have any thoughts?




http://www.plumbingengineer.com/april_07/designers.php







David Autry

Plans Examiner

Nebraska  State Fire Marshal's Office

246 S. 14th Street

Lincoln, NE 68508

402-471-9659

 402-471-3118 fax

www.sfm.ne.gov










************************************** See what's free at http://www.aol.com.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to