A.10.10.2.2.1  Compressed air or compressed gas should never be used to test
systems with rigid thermoplastic pipe. (13, 2007)


A.6.4.2  Testing of a system can be accomplished by pressurizing the system
with water and checking visually for leakage at each joint or coupling
unless specifically allowed by the manufacturer(s) of both the pipe and the
fittings in their installation instructions.
Where pressure testing systems have rigid thermoplastic piping, such as
listed CPVC, or flexible piping, such as listed polybutylene, the sprinkler
system should be filled with water. The air should be bled from the highest
and farthest sprinklers before the test pressure is applied. Compressed air
or compressed gas never should be used for pressure testing CPVC piping.
Testing with air pressure is permitted for polybutylene piping where
conducted in accordance with the testing procedures of 16.2.2.1 of NFPA 13,
Standard for the Installation of Sprinkler Systems.(13R, 2007)

nothing has changed.

Garth
a fitter

----- Original Message ----- 
From: "Jim Kettler" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, May 03, 2007 2:05 PM
Subject: Air Testing of CPVC Piping


> We've recently heard from quite a few contractors regarding air testing of
> CPVC piping on our residential systems. All of the information I have
> indicates that air testing of CPVC is not permitted. We've never required
> testing beyond the parameters of 13D.
>
> My question: what has prompted the sudden interest? Has something changed
or
> is there new information on the CPVC piping?
>
> Jim Kettler
> Fire Marshal
> Buckingham, PA
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)