Contact your AHJ and see if they will allow NFPA 13, 8.15.10.3
(electrical equipment rooms) to include the telecom room.  There is no
other reference in 13 to telecommunication rooms specifically.  If the
owner insists that you omit sprinklers some AHJ's will allow it if the
room meets the criteria listed in 8.15.10.3.  Otherwise the sprinkler
will be required unless they want to foot the bill for FM200 or Co2 or
some other agent type extinguishing system.  If their concern is someone
smacking the head and it going off, use one of the institutional
(tamper-resistant) type heads.  If they are worried about the proverbial
"leak" then ask them if it's better for their equipment to get a little
water on it or get a lot of water from a hose stream or to burn up
altogether.  You can always dry things out but you can't refashion
little melted blobs of plastic back to their original shape and
function.

Couldn't find any omission clauses in the Building Code for
telecommunication rooms but there is a blurb in the IFC 2006 Section
903.2, EXCEPTION, but it is more related to Telecommunications
BUILDINGS,  913.3.1 says the same thing.  Those are the only references
to Telecommunications that I could find.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Monday, May 21, 2007 2:15 PM
To: [email protected]
Subject: Telecom Rooms

Does anybody know off the top of their head if Telecom Rooms are
referenced in NFPA-13? I know what the code say about Electrical Rooms
with 2 hour walls but does that apply to other types of rooms as well?
 

           Regards,

              Brian Harris
First Defense Fire Protection
        Design Engineer

    <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]