Looking for input:

I have a new vault/building that is to be segregated by three hour fire
rated construction into three compartments.  (NEC Article 450) The
compartments will contain a transformer in two of them with switchgear
in the other.

The question is would sprinkler protection provided within the structure
add any value i.e.business interruption/property protection?  The
building is essentially remote from other buildings/exposures and is
provided with crush stone in pits below the oil filled transformers for
containment.  The NEC allows the three hour fire rated walls to be
reduced to one hour for what that is worth.

Thanks in advance. 