What will be the savings if sprinklers are installed?
Limit damage to transformer? From fire--explosion
Limit damage to structure? From fire--explosion
Limit damage to exposures?
Limit business interruption?
Protect against external fire?
I think 3-hour walls with enough ventilation to relieve explosion pressure
could limit transformer damage to only one transformer. A lot would depend on
transformer size, and the effect of BI.
Often enough, a damaged transformer will have to be factory rebuilt, or
replaced. This is with or without sprinklers.
If the switchgear section is large enough to store ANYTHING
I would want it sprinklered.
[EMAIL PROTECTED]
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
----- Original Message ----
From: Mark Sornsin <[EMAIL PROTECTED]>
To: [email protected]
Sent: Tuesday, May 22, 2007 10:46:54 AM
Subject: RE: Transformer Vaults to sprinkler or not to sprinkler
Peter:
I would throw the same question back at you - or to the owner: Does
protection provide a benefit from a business interruption standpoint?
What is their loss potential if one or all of these things burn? How
long would it take to replace or to at least mitigate its lack of
operation?
What are these transformers worth in a physical sense?
If the combined loss potential is $25,000, then maybe it's not worth the
up-front or maintenance expense for protection; if the loss potential is
$250,000,000, then maybe you could argue that protection is worthwhile.
Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
701.280.8591
[EMAIL PROTECTED]
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Larrimer,
Peter A
Sent: Tuesday, May 22, 2007 12:31 PM
To: [email protected]
Subject: Transformer Vaults to sprinkler or not to sprinkler
Looking for input:
I have a new vault/building that is to be segregated by three hour fire
rated construction into three compartments. (NEC Article 450) The
compartments will contain a transformer in two of them with switchgear
in the other.
The question is would sprinkler protection provided within the structure
add any value i.e.business interruption/property protection? The
building is essentially remote from other buildings/exposures and is
provided with crush stone in pits below the oil filled transformers for
containment. The NEC allows the three hour fire rated walls to be
reduced to one hour for what that is worth.
Thanks in advance.
Peter A. Larrimer PE
Safety & Fire Protection Engineer
VISN 4
Voice 412-365-5466
Cell 412-999-1321
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)