Pete, When you say; "The NEC allows the three hour fire rated walls to be reduced to one hour for what that is worth." Are you referring to the allowable reduction where transformers are protected with automatic sprinkler, water spray, carbon dioxide, or halon? If so, I would say that the value lies in the sprinkler tradeoff of the reduced fire rating.
Dan Cipriani City of Pittsburgh -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Larrimer, Peter A Sent: Tuesday, May 22, 2007 1:31 PM To: [email protected] Subject: Transformer Vaults to sprinkler or not to sprinkler Looking for input: I have a new vault/building that is to be segregated by three hour fire rated construction into three compartments. (NEC Article 450) The compartments will contain a transformer in two of them with switchgear in the other. The question is would sprinkler protection provided within the structure add any value i.e.business interruption/property protection? The building is essentially remote from other buildings/exposures and is provided with crush stone in pits below the oil filled transformers for containment. The NEC allows the three hour fire rated walls to be reduced to one hour for what that is worth. Thanks in advance. Peter A. Larrimer PE Safety & Fire Protection Engineer VISN 4 Voice 412-365-5466 Cell 412-999-1321 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)