The ENGINEERED fabric ceilings have their own rigging and hangers.  They
shouldn't need to use the sprinklers unless this is an installation by
Larry, Darrell and his other brother Darrell.

You could state that the only way they can legally hang from the
sprinkler assembly is to obtain a letter from the sprinkler mfgr. Giving
them permission.  They would need to include details on the ceiling
material, weights supported, etc.  If they receive a letter giving them
approval (which would appear to be unlikely) then unless the AHJ
disapproves of the installation, you've put the liability back on the
owner and mfgr.  I'd write a letter to the A/E & owner expressing my
concerns including any code references you can find.   Couldn't find
anything specifically in 13 forbidding attachment to the sprinkler
itself probably because for most professionals that's kind of a
no-brainer.  

These fabric ceilings are engineered systems, not just some cloth bought
at Wallymart stapled to the rafters.  You should hopefully have a
reputable contractor doing the install that you can talk to.  Sounds
like the Architect isn't real familiar with the actual product, just the
concept.  He needs some education.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark
Hasenmyer
Sent: Monday, June 25, 2007 9:03 AM
To: [email protected]
Subject: RE: hanging from sprinklers

Todd:

Look at the handbook; it specifically mentions hanging from sprinklers
is prohibited.

Mark Hasenmyer, PE
MEH Fire Protection Engineering LLC
1311 River Oaks Drive
Flower Mound, TX 75028
Office (972) 874-2662
Fax (972) 874-5591


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- work
Sent: Monday, June 25, 2007 7:41 AM
To: [email protected]
Subject: hanging from sprinklers

They are starting early this week........

An Architect wants to support a fabric ceiling from the cup of concealed
sprinklers. Section 9.1.1.7 of The Book warns against this, but their
argument is that it only mentions piping and hangers and not sprinklers.
They are about to take this to the local AHJ. I would think that most
AHJs would send them packing, but I don't know this guy and this is for
a chapel at a well-known regional Catholic university, which could have
some influence. Anybody run into this before? Any ideas besides this
section for my defence? Any ideas on protecting spaces with tensioned
fabric ceilings?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to