Greg,

Has he given you any code or standard reference for such a decision on his part? Has he developed some information on a problem that results in doing what you're after?? 7.2.2 (2) ('02 ed) seems to suggest to me that if you're using dry-pendent sprinklers it's irrelevant what the temperature of the space below the ceiling is for a dry-pipe system, particularly in light of the criteria in (3) for using return bends only in areas maintained above 40 deg. Right off the top of my head I can't think of any reason you couldn't, particularly if you're using dry pendents, or even standard pendents on return bends.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website



Greg McGahan wrote:
We have an AHJ telling us that we can not use a dry system to feed an
unheated attic and the heated space below the ceiling. He is insisting that
we use a wet system for the lower area with insulation on top of the piping.
We have done this many times in the past but on this project it is very
difficult to accomplish this due to the construction.
I am having a hard time refuting him with concrete proof that there is
nothing wrong with using the dry system with dry pendents.
Thanks for any input from the forum.
Greg
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to