We did a couple of rehab houses where the piping was in the unheated
attic.  In one case we had a wet system serving the occupied space with
6" of batt insulation laid over the piping, stapled to the bottom chord
of the trusses with roofing felt laid over the insulation to protect it
and prevent it from being disturbed.  That is one problem.  While you
can lay insulation over the pipe, you can't guarantee it won't stay put
if people are moving around in the attic at some point in time.  Once
exposed you have a potential problem.  

The other scenario was dry system for the attic and the occupied space
based on the fact that both systems were located in the unheated attic.
Insulation over the pipes was not considered a reliable means of
protecting against freezing by the AHJ.  

NFPA 13, 8.16.4.1 (2007) gives some options for protection of piping
against freezing.

There is no restriction in using the dry system in an occupied area per
NFPA 13 that I can find but not saying that some other code or
applicable standard might be more restrictive than NFPA. (one of our
jobs was with the State Dept. of Health, which had some additional
restrictions)  

As far as the time delay,  there are specific time parameters we must
meet as listed in NFPA 13, (2007)Table 7.23.6.1.  Note it lists from
Residential to Extra Hazard occupancies, leading one to believe that a
dry system is acceptable for any of these occupancies.  

Not to be argumentative but I would definitely ask the AHJ where the
restriction for use of dry systems is located in NFPA 13.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Monday, July 30, 2007 10:08 AM
To: [email protected]
Subject: RE: Dry System with Pendents

The only thing I have ever been able to find is in the handbook 9-125
18th edition. "Dry-pipe systems should only be used in areas subject to
freezing temperatures." I have had an AHJ use this as justification for
a slightly different application.

Isn't there something about insulation not being a suitable separation
between hazards? I would hate to rely on the insulation being
undisturbed throughout the life of the system to prevent freezing.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Friday, July 27, 2007 2:59 PM
To: [email protected]
Subject: Dry System with Pendents


We have an AHJ telling us that we can not use a dry system to feed an
unheated attic and the heated space below the ceiling. He is insisting
that we use a wet system for the lower area with insulation on top of
the piping.
We have done this many times in the past but on this project it is very
difficult to accomplish this due to the construction. 

I am having a hard time refuting him with concrete proof that there is
nothing wrong with using the dry system with dry pendents. 

Thanks for any input from the forum.
Greg
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to