NFPA 101 requires quick-response or residential sprinklers in health care facilities and residential occupancies due to life safety concerns. The intent appear to be to deliver water quickly.
A dry pipe system has a built-in time delay, and using quick-response dry pendent sprinklers doesn't eliminate the delay in getting water to the fire area...so a dry system with QR dry pendent sprinklers might not meet the life safety intent in a nursing home. Ask the sprinkler manufacturer if his QR dry pendent sprinkler can be used to satisfy the NFPA 101 requirement. Maybe the NFPA 101 requirment should be changed to require QR sprinklers with a wet pipe system since there are no residential sprinklers listed for dry pipe use. rick matsuda, city of dallas -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Monday, July 30, 2007 9:09 AM To: [email protected] Subject: RE: Dry System with Pendents Yes it is residential below the attic. Greg Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- At 05:58 PM 7/27/2007, you wrote: >We have an AHJ telling us that we can not use a dry system to feed an >unheated attic and the heated space below the ceiling. He is insisting that >we use a wet system for the lower area with insulation on top of the piping. >We have done this many times in the past but on this project it is very >difficult to accomplish this due to the construction. > >I am having a hard time refuting him with concrete proof that there is >nothing wrong with using the dry system with dry pendents. > >Thanks for any input from the forum. >Greg >Living Water Fire Protection, LLC >1160 McKenzie Road >Cantonment, FL 32533 >850-937-1850 >Fax: 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)