Number one, if you have a backflow device you now have two
springloaded checks in the system. Two, if you use a listed 13D riser
assembly from any of the major manufacturers they come with spring
loaded checks. Three, where are spring loaded checks prohibited?

On 7/31/07, Travis Mack <[EMAIL PROTECTED]> wrote:
> Is there any reason why you couldn't use a spring loaded check valve in a
> 13D system as the system check valve?  We have an AHJ that is requiring a
> spring loaded check to be removed and a swing check be installed.  I thought
> the waterflow valves weren't required to be listed in a 13D application.
>
> Travis
>