Sunny (well actually rainy lately) AZ.  It is using a 13D riser assembly
from one of the major manufacturer's and the AHJ is saying NO WAY!!!!!!!
You got me on this one!  I got this relayed from the field superintendant.
The AHJ states it is in the plumbing code somewhere and he has been trying
to get the manufacturer's to get it out of the those devices for years.

Again, the reasoning is coming through another person so I don't know
exactly what the AHJ said, but basically, the riser is being removed and the
swing check put in.  2 fire inspectors and then the main boss says it has to
come out and only a swing check is acceptable.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Tuesday, July 31, 2007 4:16 PM
To: [email protected]
Subject: Re: Check valve in 13D system

Number one, if you have a backflow device you now have two springloaded
checks in the system. Two, if you use a listed 13D riser assembly from any
of the major manufacturers they come with spring loaded checks. Three, where
are spring loaded checks prohibited?

On 7/31/07, Travis Mack <[EMAIL PROTECTED]> wrote:
> Is there any reason why you couldn't use a spring loaded check valve 
> in a 13D system as the system check valve?  We have an AHJ that is 
> requiring a spring loaded check to be removed and a swing check be 
> installed.  I thought the waterflow valves weren't required to be listed
in a 13D application.
>
> Travis
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 2430 (20070731) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to