Sunny (well actually rainy lately) AZ. It is using a 13D riser assembly from one of the major manufacturer's and the AHJ is saying NO WAY!!!!!!! You got me on this one! I got this relayed from the field superintendant. The AHJ states it is in the plumbing code somewhere and he has been trying to get the manufacturer's to get it out of the those devices for years.
Again, the reasoning is coming through another person so I don't know exactly what the AHJ said, but basically, the riser is being removed and the swing check put in. 2 fire inspectors and then the main boss says it has to come out and only a swing check is acceptable. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman Sent: Tuesday, July 31, 2007 4:16 PM To: [email protected] Subject: Re: Check valve in 13D system Number one, if you have a backflow device you now have two springloaded checks in the system. Two, if you use a listed 13D riser assembly from any of the major manufacturers they come with spring loaded checks. Three, where are spring loaded checks prohibited? On 7/31/07, Travis Mack <[EMAIL PROTECTED]> wrote: > Is there any reason why you couldn't use a spring loaded check valve > in a 13D system as the system check valve? We have an AHJ that is > requiring a spring loaded check to be removed and a swing check be > installed. I thought the waterflow valves weren't required to be listed in a 13D application. > > Travis > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) __________ NOD32 2430 (20070731) Information __________ This message was checked by NOD32 antivirus system. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)