Ed,

While there is prescribed height in the standard consider the building code
where clear egress width and or obstructions could become an issue.
Mounting the valve assembly at or above 7'-0" is consistent with the minimum
allowable ceiling height in the building code.

Only one horror story when they decided to paint....everything. 

John Drucker
Fire Protection Subcode Official
New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Thursday, August 02, 2007 5:39 PM
To: [email protected]
Subject: Floor control valves

I'd asked this previously, but got zero responses.  

What's the ideal height within a stairway to install the floor control
valve assembly?  The lower they're installed, the odds of them being
tampered with increases.  The higher they're installed, the more it could
delay shutting down the sprinkler system following a fire or accidental
discharge.  Any horror stories one way or the other?

Ed Kramer
Littleton, CO