Maybe I am missing something..??? Anyone consider 8.5.5?

R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of [EMAIL PROTECTED]
----- >Sent: Thursday, August 16, 2007 7:48 AM
----- >To: [email protected]
----- >Subject: RE: Ceiling Clouds throughout Band / Choir Room
----- >
----- >I stand corrected and should have said CONTAIN instead 
----- >of suppress. But in any case, the situation illustrated 
----- >here wouldn't even contain a fire.  Water running in 
----- >streams off the panels (if the sprinkler even operated) 
----- >isn't going to accomplish much, maybe it would drown the 
----- >fire eventually if you let it flow long enough.  (ah 
----- >there you go, now that would be suppression by drowning)  ;)
----- >
----- >
----- >The whole concept of when does an obstruction become an 
----- >obstruction can not always be defined by the black and 
----- >white rules written down.  There's no magic in the 48" 
----- >number.  To say that at 48" it's not an obstruction but 
----- >at 48.5" it is, only defines the item as an obstruction 
----- >per the code but not always in actual application.  When 
----- >there are obstructions such as these they can almost 
----- >create a ceiling level below the roof deck sprinklers.  
----- >This is one area where the FP designer can help the 
----- >architect by letting them know these kind of items can 
----- >create a problem.  Maybe going to a smaller panel and 
----- >adjusting the spacing between differently can eliminate 
----- >any question whatsoever about the need of sub-level 
----- >sprinklers and the effectiveness and unhindered 
----- >activation of the roof deck sprinklers.  
----- >
----- >But in typical fashion if we meet the written definition 
----- >of the Code, we're covered.  No extra costs to the 
----- >owner.  We've met the requirements based on the minimum. 
----- > I guess this is my soapbox issue.  Owners want cheap, 
----- >cheap, cheap when it comes to fire protection systems, 
----- >save every dollar they can there, "just give me the bare 
----- >minimum", but I don't ever remember hearing someone say 
----- >to buy the cheapest carpet they can find.  Sounds like 
----- >the priorities are a bit askew.
----- >
----- >
----- >Craig L. Prahl, CET
----- >Fire Protection Group
----- >Mechanical Department
----- >CH2MHILL
----- >Lockwood Greene
----- >1500 International Drive
----- >PO Box 491, Spartanburg, SC  29304-0491
----- >Direct - 864.599.4102
----- >Fax - 864.599.8439
----- >[EMAIL PROTECTED]
----- >http://www.lg.com
----- >
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Bob Knight
----- >Sent: Wednesday, August 15, 2007 5:47 PM
----- >To: [email protected]
----- >Subject: RE: Ceiling Clouds throughout Band / Choir Room
----- >
----- >Craig,
----- >I agreed with you on the quantity and closeness of the 
----- >panels, I was merely pointing out the fact that an 
----- >object is not an obstruction just because it is 48" 
----- >wide.  It's not an obstruction until it exceeds the 48" 
----- >threshold.
----- >As far as are sprinklers required; it will depend on the 
----- >actual layout of the panels.  It may be that there are 
----- >areas were it would be advisable to place pendants in 
----- >the panels, while there may be other areas where this 
----- >can be avoided.  This is why I'm not sold either way.  
----- >The layout will dictate where sprinklers will be 
----- >required.  As Garth mentioned, I think it was Garth, the 
----- >fire sprinklers are designed to contain not suppress the fire.
----- >While we all want to see every fire suppressed, this is 
----- >not the intent.  It is an excellent bonus though that 
----- >most fires are suppressed by sprinklers, and I agree 
----- >that we need to be diligent in our designs so as not to 
----- >create systems that will be destined to fail.
----- >
----- >Bob K
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of [EMAIL PROTECTED]
----- >Sent: Wednesday, August 15, 2007 3:27 PM
----- >To: [email protected]
----- >Subject: RE: Ceiling Clouds throughout Band / Choir Room
----- >
----- >It will discharge down upon the panels and then just run 
----- >down to the floor in streams.  Doubt there will be much 
----- >swirling below the panels. If the discharge pattern of a 
----- >sprinkler is crucial to its effective nature at 
----- >suppressing fire, then it's unlikely that they will have 
----- >much more effect than someone laying a garden hose on 
----- >top of the panels and letting it run.
----- >Hopefully the panels are designed and installed in such 
----- >a way that they won't retain or collect water, then fall 
----- >to the floor under the weight.  
----- >
----- >This is one of those issues where we need to feel 
----- >confident that due diligence has been practiced when "we 
----- >just meet the code".  Don't forget, that's the mantra 
----- >the owner of Sofa World used.
----- >
----- >
----- >Craig L. Prahl, CET
----- >Fire Protection Group
----- >Mechanical Department
----- >CH2MHILL
----- >Lockwood Greene
----- >1500 International Drive
----- >PO Box 491, Spartanburg, SC  29304-0491
----- >Direct - 864.599.4102
----- >Fax - 864.599.8439
----- >[EMAIL PROTECTED]
----- >http://www.lg.com
----- >
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Bob Knight
----- >Sent: Wednesday, August 15, 2007 5:20 PM
----- >To: [email protected]
----- >Subject: RE: Ceiling Clouds throughout Band / Choir Room
----- >
----- >Splitting hairs may be true, but none the less 48" and 
----- >less qualifies per code.  As long as the panels are 
----- >consistent in size, they are acceptable per code.  So, 
----- >the sprinklers don't have to be precise, they just need 
----- >to discharge.  One of the reasons that obstructions of 
----- >this size are allowed per code is because water is 
----- >distributed and acts in a laminar fashion.
----- >Simply meaning that water can and will swirl around in 
----- >the air allowing it to cover areas that are otherwise 
----- >obstructed from direct discharge. 
----- >
----- >Bob
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of [EMAIL PROTECTED]
----- >Sent: Wednesday, August 15, 2007 3:03 PM
----- >To: [email protected]
----- >Subject: RE: Ceiling Clouds throughout Band / Choir Room
----- >
----- >This is splitting hairs but at 48" they are not an 
----- >obstruction based on NFPA 13, but if they were 48-1/8" 
----- >they are now an obstruction.  Those are some excessively 
----- >precise sprinklers.
----- >
----- >
----- >
----- >
----- >
----- >
----- >Craig L. Prahl, CET
----- >Fire Protection Group
----- >Mechanical Department
----- >CH2MHILL
----- >Lockwood Greene
----- >1500 International Drive
----- >PO Box 491, Spartanburg, SC  29304-0491
----- >Direct - 864.599.4102
----- >Fax - 864.599.8439
----- >[EMAIL PROTECTED]
----- >http://www.lg.com
----- >
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Bob Knight
----- >Sent: Wednesday, August 15, 2007 4:57 PM
----- >To: [email protected]
----- >Subject: RE: Ceiling Clouds throughout Band / Choir Room
----- >
----- >Chuck,
----- >I'm not disagreeing or agreeing with the positions being 
----- >taken on this because I haven't made up my mind.  I'm a 
----- >little uncomfortable with the quantity of panels as 
----- >someone Craig mentioned.  However, if the panels measure 
----- >exactly 48" they still can be considered a non 
----- >obstruction based on width alone.  They become an 
----- >obstruction only when they exceed 48".
----- >
----- >Bob Knight
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Rapid Fire - Bismarck
----- >Sent: Wednesday, August 15, 2007 2:46 PM
----- >To: [email protected]
----- >Subject: RE: Ceiling Clouds throughout Band / Choir Room
----- >
----- >Sorry, I know that Life Safety is everybody's primary 
----- >concern - and that's the business we're in.  (The 
----- >comment about "cost" and "feel good" was meant to be 
----- >tongue-in-cheek.) Information on the panels just arrived 
----- >- yep non-covered actual dimensions = 3'-10¾ square (now 
----- >- add some sort of fabric
----- >- and we're at 4'-0").  I'm still awaiting a return from 
----- >the A.H.J.
----- >
----- >**I apologize for the doubling of the messages - I don't 
----- >know why they're coming across 2x**
----- >
----- >Chuck
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Terri Leyton
----- >Sent: Wednesday, August 15, 2007 3:46 PM
----- >To: [email protected]
----- >Subject: RE: Ceiling Clouds throughout Band / Choir Room
----- >
----- >In this heat, even the dirty water "feels good".
----- >:-)
----- >
----- >Terri Simmons Leyton
----- >PROTECTION DESIGN & CONSULTING
----- >Ph:      858-751-2930
----- >Fax:    858-751-2933
----- >Cell:  619-871-8450
----- >
----- >PLEASE NOTE: 
----- >New address effective 8-27-07!
----- >8849-B Complex Drive, San Diego, CA  92123 Phone and fax 
----- >remain the same
----- >
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Rapid Fire - Bismarck
----- >Sent: Wednesday, August 15, 2007 1:35 PM
----- >To: [email protected]
----- >Subject: RE: Ceiling Clouds throughout Band / Choir Room
----- >
----- >But at what expense?  Surely you won't see an architect 
----- >/ owner openly offer money to "feel good".
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Fletcher, Ron
----- >Sent: Wednesday, August 15, 2007 3:23 PM
----- >To: [email protected]
----- >Subject: RE: Ceiling Clouds throughout Band / Choir Room
----- >
----- >Granted the clouds may not allow a sprinkler to 
----- >"effectively extinguish a fire below such an assembly" 
----- >but when did extinguishment become a requirement and how 
----- >will a sprinkler installed in a 4x4 panel prevent 
----- >diversion of combustion gasses?
----- >
----- >We call them feel good sprinklers, they won't go off 
----- >because there is no heat collection but they make the 
----- >AHJ's and engineers happy.
----- >
----- >Ron Fletcher
----- >Aero Automatic
----- >Phoenix, AZ
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of [EMAIL PROTECTED]
----- >Sent: Wednesday, August 15, 2007 1:07 PM
----- >To: [email protected]
----- >Subject: RE: Ceiling Clouds throughout Band / Choir Room
----- >
----- >Even though the clouds are 3'-11 and technically under 
----- >the 4'-0 rule
----- >(8.6.5.3.3) with only 1'-0 up to 4'-0 between the panels 
----- >what will the effective spray pattern be from heads 
----- >installed at the underside of the roof deck? If you had 
----- >4 panels with only 12" between the panels you've 
----- >essentially got a 16x16 ft obstruction and would you 
----- >really expect sprinklers to effectively extinguish a 
----- >fire below such an assembly?  Also while we're 
----- >discussing obstruction to water spray, what about 
----- >diversion of combustion gasses to sprinklers not near 
----- >the actual fire source?  Is this considered?  
----- >
----- >I don't know if the 3'-11 measurement is off the actual 
----- >cloud/ a shop drawing or off of an architectural 
----- >drawing.  If you're scaling something off a cad drawing 
----- >I wouldn't try to call it that close, chances are it'll 
----- >be 48"+.  What did Dirty Harry say,  "do ya feel lucky?" 
..................
----- >
----- >
----- >Craig L. Prahl, CET
----- >Fire Protection Group
----- >Mechanical Department
----- >CH2MHILL
----- >Lockwood Greene
----- >1500 International Drive
----- >PO Box 491, Spartanburg, SC  29304-0491
----- >Direct - 864.599.4102
----- >Fax - 864.599.8439
----- >[EMAIL PROTECTED]
----- >http://www.lg.com
----- >
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Rapid Fire - Bismarck
----- >Sent: Wednesday, August 15, 2007 3:18 PM
----- >To: [email protected]
----- >Subject: RE: Ceiling Clouds throughout Band / Choir Room
----- >
----- >I appreciate all's input on the matter.  (Taking 8.6.5.2.1.4 into
----- >consideration) Though I'm 'nickel and dime'ing the 
----- >situation - measurement of the panels are 3'-11" square. 
----- > Whew!  Under 4'!!  Seriously though - in a room 
----- >measuring 48'-9" square, there's 56 of these panels!  ½" 
----- >have a convex contour... the others - concave.  
----- >I'll be making a call to the respective A.H.J. and get 
----- >his take on it.
----- >
----- >Thanks again! 
----- >
----- >No virus found in this outgoing message.
----- >Checked by AVG Free Edition. 
----- >Version: 7.5.476 / Virus Database: 269.11.19/953 - 
----- >Release Date: 8/14/2007
----- >5:19 PM
----- > 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field) 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field) 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >
----- >No virus found in this incoming message.
----- >Checked by AVG Free Edition. 
----- >Version: 7.5.476 / Virus Database: 269.11.19/953 - 
----- >Release Date: 8/14/2007
----- >5:19 PM
----- > 
----- >
----- >No virus found in this outgoing message.
----- >Checked by AVG Free Edition. 
----- >Version: 7.5.476 / Virus Database: 269.11.19/953 - 
----- >Release Date: 8/14/2007
----- >5:19 PM
----- > 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field) 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >
----- >No virus found in this incoming message.
----- >Checked by AVG Free Edition. 
----- >Version: 7.5.476 / Virus Database: 269.11.19/953 - 
----- >Release Date: 8/14/2007
----- >5:19 PM
----- > 
----- >
----- >No virus found in this outgoing message.
----- >Checked by AVG Free Edition. 
----- >Version: 7.5.476 / Virus Database: 269.11.19/953 - 
----- >Release Date: 8/14/2007
----- >5:19 PM
----- > 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >
----- >No virus found in this incoming message.
----- >Checked by AVG Free Edition. 
----- >Version: 7.5.476 / Virus Database: 269.11.17/951 - 
----- >Release Date: 8/13/2007
----- >10:15 AM
----- > 
----- >
----- >No virus found in this outgoing message.
----- >Checked by AVG Free Edition. 
----- >Version: 7.5.476 / Virus Database: 269.11.17/951 - 
----- >Release Date: 8/13/2007
----- >10:15 AM
----- > 
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field) 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >
----- >No virus found in this incoming message.
----- >Checked by AVG Free Edition. 
----- >Version: 7.5.476 / Virus Database: 269.11.17/951 - 
----- >Release Date: 8/13/2007
----- >10:15 AM
----- > 
----- >
----- >No virus found in this outgoing message.
----- >Checked by AVG Free Edition. 
----- >Version: 7.5.476 / Virus Database: 269.11.17/951 - 
----- >Release Date: 8/13/2007
----- >10:15 AM
----- > 
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field) 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >
----- >No virus found in this incoming message.
----- >Checked by AVG Free Edition. 
----- >Version: 7.5.476 / Virus Database: 269.11.17/951 - 
----- >Release Date: 8/13/2007
----- >10:15 AM
----- > 
----- >
----- >No virus found in this outgoing message.
----- >Checked by AVG Free Edition. 
----- >Version: 7.5.476 / Virus Database: 269.11.17/951 - 
----- >Release Date: 8/13/2007
----- >10:15 AM
----- > 
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field) 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)