As Mark said the main drain on an auxiiiiary dry pipe can be argued to
be an auxilliary drain. On a 6 head system I'd think draining into a
bucket would be sufficient. Without taking a lot of time to calculate
cubic feet in a tube and converting that to gallons I'll just guess
that there'll be less than five gallons in the piping after a trip
test.

On 8/16/07, Joe Hankins <[EMAIL PROTECTED]> wrote:
> The 2-in drain was put on sprinkler systems to drain the system when
> needed. Drain tests were instituted (by HPR Insurance Companies) at a
> time where full flow water tests (including loop tests) were done at
> least once a year.  Drain tests were an additional test to verify that
> the valve on the lead-in to the system had not dropped it's gate and
> that there was no blockage in the lead-in.  A drain test on the wet
> system will tell you everything you need to know.
>
> BTW, using drain tests to do anything other than find major problems is
> risky business. There is no way that a drain test can substitute for a
> water test for the purpose of  accurately measuring the available water
> supply.
>
> Joe
>
>
>
>
> John T. Johnson, CFPS wrote:
> > Hello Members,
> >
> > We are installing a new wet system. Off of the wet system is a small dry 
> > system with 6 sprinklers to protect a porch area. For us to pipe the main 
> > drain of the dry system we need to core 2 walls to get to the outside of 
> > the building, go up about 15'-0" to the roof of the porch, and for the most 
> > part follow the dry system piping to the end of the porch.
> >
> > My question is:
> > If the control valves between the wet system and dry system are tampered & 
> > monitored by the building fire alarm to ensure that they remain open, can 
> > we use the main drain on the wet system to fulfill the main drain test 
> > requirements, and just pipe the drain of the dry system to a floor drain?
> >
> > Thank you in advance,
> >
> >
> >
> >
> >
> > ---------------------------------
> > Sick sense of humor? Visit Yahoo! TV's Comedy with an Edge to see what's 
> > on, when.
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> >
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to