Bob, 

Not trying to beat a dead horse, and if you got the answer you wanted to
hear then great.  Just trying to point out that the ruling by the AHJ
you speak of can be from some other issue beyond the confines of one
paragraph of NFPA 13.  

Sorry for the confusion.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob
Knight
Sent: Wednesday, August 22, 2007 3:10 PM
To: [email protected]
Subject: RE: Barrier / Partition Definition

Well Mr. Prahl,
Since I am the originator of this post, I have been trying to stay out
of the discussion.  One I am perfectly ok with being wrong when I am.
It seems as though there are some who cannot accept being wrong no
matter what, but would rather argue the point until they have satisfied
their self that they are right, though that's a different issue for
another day.  Two, the wording in 13 is clear in that it does not
mention "fire" for this partition / barrier.  Searching through NFPA
documents I found NFPA 221, Standard for High Challenge Fire Walls, Fire
Walls, and Fire Barrier Walls, which deals explicitly with fire walls,
partitions and barriers.  If the intent of 13 was to require this
partition / barrier to be a fire partition / barrier it is reasonable to
expect that 13 would have used the proper terminology.
While 13 has made oversights in other areas, this situation is very
clearly spelled out defining what the intent is.  The intent is for heat
not fire as it clearly states in 11.1.2.  It even clearly states that
the 15 foot rule is only to be applied if the partition / barrier do not
exist.  Which brings us right back to Roland's post.  Now as I stated in
an earlier post, it still appears to me that you are over analyzing a
relatively simple situation.  I do it at times as well.  What I was
really seeking was conformation for something that I had been taught in
a seminar years earlier.  As far as I can see from the different
postings for this topic, I received the conformation that I was hoping
for.

Respectfully,

Bob knight

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, August 22, 2007 11:57 AM
To: [email protected]
Subject: RE: Barrier / Partition Definition

Yes adding some clarification to 11.1.2 would help.

Room design method requires the partition to be rated, not just a
physical separation.  Openings are to be protected as well.  

If the originator of this discussion would have gotten just a bit more
info it would have helped quench some of the debate.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Wednesday, August 22, 2007 1:42 PM
To: [email protected]
Subject: RE: Barrier / Partition Definition

2002 NFPA-13 11.1.2 (Design Approaches) was cited in the discussion.
11.1.2 doesn't read "thermal barrier", but barrier or partition. I
believe that was the gist of the debate.  Since Design Approaches is
chapter 11 and 11.1.2 falls in that chapter my thinking was the room
design fire resistance ratings of 11.2.3.3.3 was more closely applicable
to the discussion.

I'll rephrase;  

PS- Add a definition to NFPA-13 for barrier and partition to Chapter 11
and this issue goes away. ;-)

John Drucker


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David
Autry
Sent: Wednesday, August 22, 2007 1:18 PM
To: [email protected]
Subject: RE: Barrier / Partition Definition

Since the definition is in Chapter 3; why wouldn't it apply thoughout?

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Wednesday, August 22, 2007 11:53 AM
To: [email protected]
Subject: RE: Barrier / Partition Definition

David,

Please correct me but my understanding of the definition of thermal
barrier at 3.3.23 applies to 8.14.8.1.1.  This definition was included
specifically to define the required thermal barrier behind a bath/shower
surround.  As an inspector I've observed this many times where a
sprinkler was installed in the bathroom because a thermal barrier was
not installed between the framing and surround excluding use of the
provision to omit the sprinkler.
 
Does the definition at 3.3.23 apply throughout the standard ?.  

Thanks

John Drucker 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David
Autry
Sent: Wednesday, August 22, 2007 12:23 PM
To: [email protected]
Subject: RE: Barrier / Partition Definition

John,
NFPA 13 (2002) does define thermal barrier. 3.3.23

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Wednesday, August 22, 2007 8:57 AM
To: [email protected]
Subject: RE: Barrier / Partition Definition

Craig,

How about applying the "Room Design" criteria ?.  "All rooms shall be
enclosed with walls having a fire resistance rating equal to the water
supply duration".  A thirty minute "wall" (partition in building code
speak) could be 2 X 4 with 1/2" Type X on both side, a one hour the same
except 5/8" Type X.   The annex info (did I really refer to an annex !)
explains that the "wall" "can terminate at a substantial (there we go
again with subjective language) suspended ceiling and need not be
extended to a rated floor slab above for this section to apply" 

The intent is clearly a thermal barrier as it relates to sprinkler
operation and not protection of the building structure or a means of
egress. If the intent was otherwise the building code would have said
that and not depended on the sprinkler standard to do so. As a matter of
fact the building code contains extensive tables that modify (yea that
means reduce) the fire ratings of building elements for complete
automatic fire sprinkler systems.  Guess what a parallam is one hell of
a thermal barrier in the context of sprinklers

Lastly its apples and oranges. Application of codes and standards is
like a recipe, theres a specific order to obtain the end result unlike a
stew where everything gets haphazradly thrown into a pot. Now I realize
this is the sprinkler forum but let me point out one very real example
of this. The Mechanical Code defines the air handling space above a
ceiling as a plenum, The Electrical Code defines it as "Other
Environmental Air Handling Spaces".  From a "permissable" wiring method
standpoint that very definition makes a world of difference. Its
imperative that the context be applied correctly. In the example I cited
the electrical code regulates wiring not the mechanical code.

PS- Add a definition to NFPA-13 for thermal barrier and this issue goes
away.

Hope that helps

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, August 22, 2007 9:08 AM
To: [email protected]
Subject: RE: Barrier / Partition Definition

Roland,

The issue with the code official seems to be more related to the
extension of the higher density into the lower density area due to an
issue with the appropriate separation (or lack thereof) between the two
occupancies.  

We don't have all the information concerning the building in question
and without it , it is hard to render any sort of definitive opinion on
the matter other than code definitions and possible scenarios.



But it becomes confusing when two distinct documents such as the IBC and
NFPA 13 use similar wording but may have different definitions for those
words.  A separation in the IBC means one thing and it sounds like
you're saying that 13 doesn't mean the same.  This ought not be or
should at least be clarified in the appendix to minimize or hopefully
eliminate confusion.

I have dealt with this issue many times.  

Where dissimilar occupancies adjoin and where there is no fire
wall/separation/barrier as required by the building code or an installed
separation does not meet the requirements of the building code for a
fire wall/separation/barrier, the required sprinkler protection for the
more demanding occupancy shall extend 15 ft. beyond it perimeter.


This is a totally separate issue from draft curtains as pertaining to
ESFR sprinklers.


This is one of those issues where the sprinkler contractor is at the
mercy of the EOR and Arch.  If things like fire walls and occupancy
separations are not taken into consideration and indicated on the bid
drawings by the EOR and the contractor isn't aware of the code issues
for an occupancy, it can cost the contractor big time.  The sprinkler
contractor/designer has got to know more than just NFPA 13. 



Craig L. Prahl, CET
Fire Protection Group


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Monday, August 20, 2007 8:34 PM
To: [email protected]
Subject: Re: Barrier / Partition Definition

this is NOT required or desired to be a RATED partition.  It is not
attempting to separate fire areas within the building which is the
purview of the building code.  If the TC wanted a rated partition, it
would have said that.  The TC said a barrier or partition capable of
stopping heat with great intention to avoid those requiring a rated
wall.

Roland

On Aug 20, 2007, at 9:28 AM, <[EMAIL PROTECTED]>
<[EMAIL PROTECTED]> wrote:

> Bob,
> It comes down to the way the AHJ is interpreting this section of NFPA
> 13 and what was type of wall actually constructed versus what may have

> been or is required.  If the wall is 8" block floor to ceiling but 
> there are two openings in it that are unprotected then the wall does 
> not provide for occupancy separation per the building code and is 
> treated as if it doesn't exist.  It sounds like the issue your friend 
> is dealing with is more of an architectural issue dealing with 
> dissimilar occupancies.
>
> The "separation" is very much about the spread of fire from one area 
> to the next.  It is complementary to the sprinkler systems and very 
> integral in large buildings or buildings with adjacent dissimilar 
> occupancies.
>
> While the draft curtain analogy is similar, it's primary function is 
> to limit the unnecessary activation of sprinklers while the fire 
> partition/separation/barrier is more of a distinct, complete, physical

> separation between to spaces.  Two totally different functions from a 
> building code standpoint.
>
> But I would be curious why the AHJ does not believe this wall is a 
> sufficient separation.
>
> Again, what does the code call for between the two areas?  If they did

> not meet that requirement then NFPA 13 says to extend the higher 
> density 15ft into the less demanding adjacent occupancy, end of story.
>
> Like I said, limitation of sprinkler activation is not the main 
> purpose for fire barriers.  It's to prevent the spread of fire from 
> one area to another.
>
>
>
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
> 864.599.8439 [EMAIL PROTECTED] http://www.lg.com
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Bob 
> Knight
> Sent: Monday, August 20, 2007 12:01 PM
> To: [email protected]
> Subject: RE: Barrier / Partition Definition
>
> Craig,
> I think that you are over analyzing this situation.  There is no 
> mention in
> 13 for this to be a "fire" rated anything.  This barrier / partition 
> is merely for heat containment for the purpose of sprinkler activation

> or lack thereof, not the spread of fire.
>
> Thank you,
>
> Bob Knight
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of 
> [EMAIL PROTECTED]
> Sent: Monday, August 20, 2007 7:20 AM
> To: [email protected]
> Subject: RE: Barrier / Partition Definition
>
> The definition of fire wall, fire partition, fire barrier comes from 
> the
> building code.  If using the IBC see Chapter 7.   Depending on the
> occupancies and the level of sprinkler protection you may or may not 
> be required to provide one of the three.  Each one has slightly 
> different characteristics as defined.  The Fire Wall being the most 
> stringent where the assembly extends from the slab to or even through 
> the roof and is capable of maintaining its structural integrity even 
> if the building on either or both sides would collapse.  A fire 
> partition  is a physical separation designed with fire resistant 
> materials whose purpose is to prevent the spread of fire from one area

> to the next.  A fire partition
> is not "rated".   The fire barrier is a rated assembly but not to the
> extent of the Fire Wall.  All have protected openings as well.
>
> The wall, barrier and partition are designed to protect one occupancy 
> from fire spread from an adjacent occupancy.  They have a different 
> purpose than a draft curtain.
>
> As far as the scenario described, if the openings are not protected 
> with either fire doors or shutters or an accepted (by the AHJ) water 
> spray curtain, then by definition it does not qualify as a Code 
> defined separation. It would provide no real separation and his 
> assessment of requiring the extension of the higher density into the 
> lesser density protected area would be correct.
>
> So the question is, do the openings have any kind of automatic 
> closures, is the wall rated, is the wall required to be rated or just 
> one of the lesser assemblies?  Still a few outstanding questions 
> needing to be answered in order to make a definitive determination.
>
>
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
> 864.599.8439 [EMAIL PROTECTED] http://www.lg.com
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Bob 
> Knight
> Sent: Friday, August 17, 2007 5:22 PM
> To: [email protected]
> Subject: Barrier / Partition Definition
>
> Does anyone have a good definition for what 11.1.2 means by "Barrier" 
> or "Partition" (NFPA 13 2002 ed).  I have a friend who has an AHJ 
> telling him that an 8" concrete full height wall with two door 
> openings in it does not qualify. My understanding of this is that this

> is a perfectly acceptable barrier since the purpose of the barrier is 
> to prevent fusing of the sprinklers from one area to another.  The 
> reason the question arises is that this AHJ wants to extend a new .55 
> / 2500 sf area through the concrete wall and into an existing .2 / 
> 1500 sf system. Without being too obvious, the original system has no 
> possibility of providing this density, let alone the proper spacing of

> sprinklers. Anyway, any help will be appreciated.
>
> Thank you,
>
> Bob Knight, CET
> (208) 495-2057
> [EMAIL PROTECTED]
> www.firebyknight.com
>
>
> No virus found in this outgoing message.
> Checked by AVG Free Edition.
> Version: 7.5.484 / Virus Database: 269.12.0/957 - Release Date:
> 8/16/2007
> 1:46 PM
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> No virus found in this incoming message.
> Checked by AVG Free Edition.
> Version: 7.5.484 / Virus Database: 269.12.1/962 - Release Date:
> 8/20/2007
> 1:08 PM
>
>
> No virus found in this outgoing message.
> Checked by AVG Free Edition.
> Version: 7.5.484 / Virus Database: 269.12.1/962 - Release Date:
> 8/20/2007
> 1:08 PM
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED] (Put the word unsubscribe in the subject
> field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.484 / Virus Database: 269.12.1/963 - Release Date:
8/20/2007
5:44 PM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.484 / Virus Database: 269.12.1/963 - Release Date:
8/20/2007
5:44 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to