Reza,
Others have commented on your hose stream demand selection, combining deluge
and sprinkler demands, etc. I'll just assume your trying to meet x demand
with parallel pumps. I'm thinking out loud, so I might not have everything
covered, but here's goes.

If you are going to parallel pump (e.g. both pumps are required to meet
demand, not simply parallel redundant pumps), I think you have two main
issues - pump starting and the combined water supply vs. demand. With regard
to pump starting, I see a few options. One, you could start both pumps using
the deluge start feature of the controllers. When the deluge valve(s) trip,
both pumps start regardless of how they are sized. You could add sequential
start to one of the controllers if you want to provide some minimal time
delay to avoid simultaneous starting of both pumps. Another option would be
to target simultaneous starting by attempting to duplicate low pressure
starting configurations - sensing line taps at same location, the same
starting pressure, etc. And finally, if the desire is to stagger pump
starting pressures (more typical in redundant pump scenarios) and you want
to ensure the 2nd pump will start, I would do a supply calculation on the
system with the only the lead pump running. See where the pump settles out
on its curve (likely pretty far out, but a big lead pump with a very flat
curve could hold a more significant system pressure) and what pressure you
have at the sensing line tap for the 2nd pump. The starting pressure for the
2nd pump has to be higher than the pressure with the 1st pump running. I
don't think this delay or a short delay you add via a deluge
start/sequential start combo in the controller is that significant.
Theoretically, I think all of these are viable options, but as I said, I'm
thinking out loud, so I might not have it all covered. If you would consider
utilizing the deluge start, sequential start features, etc. I would always
speak with the controller manufacturer or rep to ensure you understand the
feature and interaction of such options.

On the issue of the two pumps meeting the demand, I see two scenarios. If
the pumps are identical, supply to the discharge flanges and piping to a
common point of the system are the same, each pump will supply essentially
50% of the demand. You could do some hand calcs to ballpark your pump
sizing, etc. However, if you are going to use different pumps (different
gpm, pressure, or the same size from  different manufacturers - different
curves) or the supply/discharge arrangement is different for identical
pumps, you would need to develop a combined water supply curve. It would
difficult to determine exactly where each pump will settle out on its curve
and how much each will contribute to the supply without creating the
combined curve (supply) and running a supply calc on the deluge system. Once
you know where on the combined supply curve you are operating, you can back
out how much each pump is contributing. Any combination where each pump is
operating within the 150% of rated max is OK.

Well, I hope that helps and if I missed something or I'm off in some way,
someone will probably jump in.

Rich

Richard Malek
[EMAIL PROTECTED]


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Reza
Esmaeili
Sent: Wednesday, September 05, 2007 12:43 PM
To: [email protected]
Subject: RE: Fire Pump Selection - Another Question


According to NFPA answer, you were right Richard, howeever NFPA answer was
short for item 3.
  What I want to ask is simulating a real project like below:
  Imagine in a factory I want to select fire pump for my below demand:
  1- Total demand of deluge system: 1500 GPM
  2- Total demand of wet pipe sprinkler system: 700 GPM
  3- Total demand of hose streams: 300 GPM.

  Total water demand: 2500 Gpm, Total pressure: 100 psi
  For this project as my source of power is reliable, I want select TWO
parallel electric pumps with below specifications:

  Scenario 1: Two pumps( First: 1250Gpm ,100 Psi - Second: 1250 Gpm
,100Psi )
  Scenario 2: Two pumps( First: 1500Gpm ,100 Psi - Second: 1000Gpm ,100Psi )
  Scenario 3: Two pumps( First: 1500Gpm ,100 Psi - Second: 1500Gpm ,100Psi )

  As my deluge demand is 1500 GPM, so which scenario is the best for my
project?
  Note that I want to select one of the above scenarios and don't have any
other options.
  Would you also please analyze each item.
  Thanks,
  Reza


---------------------------------
Be a better Heartthrob. Get better relationship answers from someone who
knows.
Yahoo! Answers - Check it out.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to